AHJ is requesting the design curve for the fire pump to be 5% lower than the pressure limiting driver (PLD) set pressure to account for the tolerance allowed NFPA 20-2019 Section 6.2.2.2 "When operating below the rated speed in a self-regulating mode, a self-regulating variable speed fire pump unit shall maintain the discharge pressure within 5 percent of the set pressure."
Is this an appropriate application for this requirement in NFPA 20? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments
Pete H
4/25/2024 06:48:31 am
Not sure, my reading of it would have it be anything from 0-5% to be "within 5%" rather than just requesting only 5%.
Reply
Jack G
4/25/2024 08:31:13 am
It doesn’t look like an unreasonable requirement.
Reply
Mike Russell
4/25/2024 11:25:42 am
I guess there's an argument to be had for applying a 5% Safety to the pump curve IF your system demand places you in a point along the supply curve that is above the set-point of the PLD, but that's not typically where the demands fall... Keep in mind, once your demand pressure at the pump discharge drops below the set-point, the PLD is no longer "regulating" the pump. The pump will simply deliver it's rated capacity.
Reply
Colin Lusher
4/25/2024 12:02:05 pm
"When operating below the rated speed in a self-regulating mode, a self-regulating variable speed fire pump unit shall maintain the discharge pressure within 5 percent of the set pressure."
Reply