Is there any code that sets a specified elevation for the the Fire Pump Test Header above outside grade?
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments
Glenn Berger
10/3/2023 08:37:12 am
NFPA 20 would be the document that I would reference for this information. I did not find a min/max dimension in a quick review of the standard.
Reply
Casey Milhorn
10/3/2023 11:08:05 am
I think I looked many years ago and never found anything. I find it helpful to always ask an inspector when I'm presented with a choice on where or how to install a test header. They have a very practical approach and will think about it differently than an installer or designer.
Reply
NFPA 20 does not contain a specific code reference that sets a minimum elevation requirement for the fire pump test header above grade. The height at which the test header should be positioned above grade is influenced by local building codes and AHJ requirements.
Reply
Anthony
10/4/2023 09:25:02 am
The test header just needs to be accessible. I've seen them in all kinds of odd places but always able to be accessed by an average person standing on the ground i.e no ladder required.
Reply