Is Building Fire Pump Size Affected by Firetrucks?

3/29/2024

11 Comments

 
For multi family buildings, I am being told that for a 4-story building, normally the fire pumps are only 15HP because the standpipes are pressurized by the fire trucks.

My understanding of NFPA 20 is that it would still be required to have a correctly sized fire pump without considering the size of the pump on the local fire trucks.

Is this an industry norm that is allowed by certain AHJ’s or is there code related to multi family that I am missing?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments
Joe Burtell
3/29/2024 08:13:25 am

If the standpipes are a manual standpipe per NFPA 14, city water pressure is all you need, no fire pump. The FD is responsible to provide the flow and pressure needed, pumper truck. You still need to calculate the manual standpipe. If the standpipes are required to be fully automatic, you will need a fire pump sized to provide the full pressure and flow.

Reply
Dan (WSFP) Wilder
3/29/2024 08:33:39 am

I've not done a design that changed that because of it being specifically Multi-Family UNLESS if fell outside of the scope of NFPA 13R (above 60' or more than 4 stories) as the hydraulic requirements change.

It doesn't state how to provide the needed flows and pressures based on the applicable codes & standards (with any adoptions), just that those requirements need to be met. Height, locations, pipe sizing, pipe material, fittings, sprinkler all play into the final requirements then it's up to the MFG for equipment needs.

The smaller pump sizing is typically due to not needing a large fire pump to accommodate what is typically a small deficiency to get the sprinkler design to work and the lesser available incoming power and space requirements (for electric pumps) in lieu of a diesel pump but again, not limited to a specific HP.

Reply
Dan Wilder
3/29/2024 08:38:01 am

and since I've read this a couple different ways

The sprinkler system calculation can have a different supply than the standpipe calculation. It is not uncommon to have a city water supply (with or without a booster pump) for the sprinkler calculation, and another standpipe calculation based on the location of the FDC and AHJ fire pump apparatus providing the water supply (typically dictated by NFPA 1901). This applies to both residential and commercial buildings types.

Reply
Jesse
3/29/2024 08:40:13 am

If the standpipe is a manual standpipe as defined in NFPA 14, then the fire pump (technically a booster pump unless being supplied by a static source) is only serving the automatic sprinkler system. Most of the stand-pipes my company designs are manual standpipes. Effectively we use the fire department apparatus as the water supply node.

Reply
Anthony
3/29/2024 08:40:40 am

THe building's fire pump won't be affected by the city's fire truck.

The building STANDPIPE system may be. See A.7.10.1.2 from NFPA14-16 for reasonable Fire pump design curves when you don't know the pumper trucks information.

Reply
Jack G
3/29/2024 06:27:46 pm

Far from towns , buildings protected with sprinklers, would need its own tank, ( hose streams not required to be included- unless building has hoses) fire pump and standpipe hydrant with fdc.
The fire department usually has a pumper truck ( capable of flowing 750- 2500 gpm) with a tank, usually around 6000 gallons.
Other than that- if a building is protected by sprinkler system, and needs standpipes, in some cases the standpipe can be manual, where the fire truck connects to a city hydrant, and pumps the required pressure and flow to the building.( including sprinklers)
The installed sprinklers could work/ calculated off city pressure ( no fire pump in building) or a fire pump added to reduce pipe sizes ( buildings now a days are pretty tight above the ceiling)
So not much correlation between pumper trucks and building pumps)
Opinion.

Reply
RUSSELL BYRD
3/30/2024 12:15:03 am



The FDC piping for sprinklers and/or standpipe would be on the system side of the fire pump and be isolated by a check valve, which would close and cause the fire dept pumper to bypass the building fire pump...

Reply
Casey Milhorn
4/1/2024 09:27:15 am

As Russell stated, the FDC piping will be AFTER the fire pump discharge and it's not unnormal to have a 4" (or smaller) city water supply feeding a small 13R type pump setup but then have a 4" or 6" FDC piping system from FDC to standpipes. Think about it as the city is suppling your automatic sprinkler systems (with a booster pump when necessary) and the FDC system is supplying your standpipes/hose valves by way of pumper truck. They just happen to be partially a shared system.

Reply
Joe Burtell
4/1/2024 09:52:09 am

The problem I see here is the 2021 IBC does not allow 13R for buildings more than 30 above FDC access. If the building was not that tall we would not be talking about a standpipe system in the first place. See section 903.3.1.2 of the 2021 IBC. Maybe this jurisdiction has a different building code.

Glenn Berger
3/30/2024 07:14:03 pm

The fire pump provided for a building is not affected by the size of the pump on the truck.

The size of the fire pump is only affected by the requirements of fire protection systems provided for the facility.

The size of the fire pump may also be affected by the water supply system characteristics.

Reply
Robert bennett
4/3/2024 01:08:53 pm

Additional comment to Joe Burtell, I agree with your comment with one additional observation and that is that the standpipe must still be flow tested and provide the required VOLUME prior to occupancy. Over the past 5 years we have required flow testing as indicated in NFPA 14-19 and found that 30% of standpipes, hydraulically designed failed to flow the required volume at the designers specified pressure. I would strongly recommend that you work with your local FD to test the standpipes under operational conditions to insure they will function when needed.

We are a large department with 30 stations and the testing process provides good training for new pump operators and also forces the first due companies to visit and become familiar with the building layout.

RJB

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Oct '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 88A
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    November 2026
    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT