I have a project with Miscellaneous Storage of Class I commodities up to 12'-0" and Group A plastics up to 5'-0".
The water supply is a tank fed from a well. Based on NFPA 13-2016 Table 13.2.1, I designed to Ordinary Hazard Group 2 with a 90 minute duration of available water. My original demand was 57 psi at 385 gpm. Our pump supplier provided a vertical in-line pump rated to 80 psi 400 gpm. The client is now unhappy about the volume of water being required so they are removing the Group A plastics from their building so we can calculate to OH I with the new demand being 41.5 psi at 304 gpm. We have already installed most of the system and the pump is ready to be delivered soon. Is it okay to have an oversized pump? Can it be limited to a smaller flow to accommodate the new demand? My worry is that it will flow at the rated capacity and if we are sizing our tanks 10,000 gallons less than originally planned we would run out of water. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
J Golden
2/26/2024 08:09:05 am
Side note;
Reply
sean
2/26/2024 01:16:11 pm
The code does not require that a tank include hose allowance as the system is not designed to support line personnel pulling off the same water supply (tank).
Reply
Jack G
2/26/2024 02:53:16 pm
I believe it’s only hose , or if a hose rack system the hose demand.
Reply
Dan Wilder
2/26/2024 08:15:18 am
Some thoughts
Reply
Glenn Berger
2/26/2024 08:19:43 am
A 400 gpm fire pump for a water demand of 385 gpm is not considered oversized. The pressure rating of 80 psi v. 57 psi could be a manufacturer available size.
Reply
Jack G
2/26/2024 08:55:01 am
Assuming the problem is 150% for 90 minutes and not having a large enough tank,
Reply
Jesse
2/26/2024 10:03:55 am
There used to be a day when we'd just throw a monster pump in a building and call it good.
Reply
Casey Milhorn
2/26/2024 03:17:01 pm
I think others have covered it fairly well.
Reply
Rodney
2/29/2024 04:48:00 am
An oversized pump is fine, but the tank should be sized according to the duty point, plus dead water and freeboard. There control valves can likewise be sized accordingly with pump delivery being restricted by using equivalent lengths of pipe, similar to an orifice plate but with a more linear flow impact. Essentially replacing a pre calculated length of distribution mains above the alarm valve with a smaller diameter pipe over the calculated length then reverting to the designed diameter. This solution provides for a quick correction of a system’s flow delivery characteristics where you have a fixed water supply and or need to adjust an existing system’s delivery curve.