Eccentric Reducer Position when Fed from Above?

7/9/2024

10 Comments

 
NFPA 20 is pretty clear on the orientation of the eccentric reducer on the suction (upstream) side of a fire pump.

But the diagrams seem to suggest that the diagonal slope (not the flat side) of the eccentric reducer is always on the bottom.

Is this true even when the supply is being fed from above?

For instance, we often have a stub into a fire pump room from the floor, then a vertical backflow preventer, then the feed comes vertically-down and to the fire pump.

Which way is correct for the eccentric reducer when the feed is from above?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments
Pete H
7/9/2024 07:07:33 am

Pretty sure even if the feed is from above, you're still under guidance to put the flat side of the eccentric reducer. I think just being eccentric might be enough to reduce air pocket development. It still has to go 10 pipe diameters before the suction elbow which should get it to a horizontal feed.

Basing this on:
NFPA 20 (2016 ed.):
Figure A.4.15.6 - the top part of the image on the "right" side, doesn't show whether the feed is from above or below, because it still has to go horizontally into the suction of the pump.

Plus that detail also establishes you might have an elbow or tee at your point of suction before, for example if you used vertical piping to accomplish your 10 pipe diameters due to a smaller pump room, you'll still be coming in from above, you'll still have your eccentric reducer (if required) in the normal orientation (flat on top, diagonal on bottom).

Take with grain of salt, but this is where I'm landing.

Reply
Pete H
7/9/2024 07:15:23 am

"under guidance to put the flat side of the eccentric reducer on top" is what I meant to type in that first sentence.

Reply
Anthony
7/9/2024 07:35:13 am

If the feed is vertical it drops to a 90 then goes into the eccentric reducer. Don't put the eccentric reducer on the vertical drop with a 90 straight into the pump. Confirm with your pump rep if you need further guidance.

Reply
OP
7/9/2024 07:40:06 am

No the eccentric reducer wouldn't be on the vertical; it'd still be horizontal going into the pump.

Basically comes from above, 90-degree elbow, OS&Y suction, eccentric reducer, then suction flange of pump.

All of it is still in the 'plane' of the pump, but wanting to know the proper way to orient the eccentric reducer.

Reply
Dan Wilder
7/9/2024 07:58:14 am

I've seen and done this before with the pump MFG & Rep approval....while not specifically called out in NFPA 20, this is allowable.

Here is one of the articles on it by the US Fire Administration....

https://www.hsdl.org/c/abstract/?docid=720893

I'll see if I can find the MFG sheet on it as well.

Reply
Glenn Berger
7/9/2024 08:15:42 am

With the eccentric reducer being placed in the horizontal piping supply to a fire pump, it is always flat on top.

I too was confused by the comment on the proposed orientation of the reducer to the fire pump.

Reply
Franck Orset
7/9/2024 08:37:20 am

For a very long time, I was pretty sure that the flat bottom was always on top (as it is the only drawing indicated in NFPA 20). And I discovered recently that I might have been wrong for several decades, as I found several other technical documentations stating that it was true only if the water was coming from the side or from below.
If coming from top, it is normally to be installed with flat on bottom) (or with a concentric reduction), as indicated in the document from Dan :

When the pump is fed from below or the side from
an underground water main, the eccentric reducer must
be installed with the ”flat side” on the top, parallel to
the floor. This arrangement prevents air being trapped
in the upper portion of the fitting.

In those configurations where the fire pump supply comes from above, such as is the lower elevations
of a basement or from an elevated tank, the eccentric reducer may be installed with the “flat side” down,
parallel to the floor. When the water supply is delivered from above, any trapped air can be bled off at the
top of the pump casing while the system is filled with water.

In the document, there is a picture with the correct installation (flat at bottom) as water is top fed...

Other technical informations (samples) on this issue:

https://www.theprocesspiping.com/pumps-suction-piping-eccentric-reducers-straight-lengths/

When the source of supply is above the pump, then the eccentric reducers must be placed with the flat side down. When the source of supply is below the pump, then the eccentric reducers must be placed with the flat side up.
In case of long horizontal pipe runs, air pockets are avoided by installing the eccentric reducer with the flat side up.

https://www.pumpsandsystems.com/reducer-fittings-decrease-pipe-size-avoid-failure-first-two-parts

Eccentric convergent reducers are normally used for horizontal installations where there is potential for air vapor accumulation. The flat side shall be located on top, unless the inlet (suction) line approach from above, in which case either a concentric reducer or eccentric convergent reducer (with the flat side on the bottom) should be used.

Reply
Franck
7/9/2024 08:39:51 am

https://www.linkedin.com/posts/danvolsky_check-your-pumps-eccentric-reducers-installation-activity-7084434651687075840--DVV/

Reply
Jack G
7/9/2024 10:33:03 am

This was discussed on the Meyer website 11/18/2020. 13 comments I believe.
NFPA 20 is clear when the supply is horizontal or from below.
The pump handbook is vague.
The hydraulic institute recommends the flat part be on the bottom, with the reduced outlet on the top of the fitting/ elbow.
Mechanical pumps when supplied from above have the flat spot on the bottom( vertically)

Reply
Jack G
7/9/2024 04:49:34 pm

Another thing to consider are automatic air releases at the top of standpipes, and on individual floors of wet systems in addition to what’s required.
I ve even added them to my pump rooms with flow meters and bypasses. Trapped air can bring a world of hurt to your new sprinkler systems !

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT