MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Calc Backflow Retrofit for Pipe Schedule System?

7/18/2024

9 Comments

 
When retroactively adding a Double Check Valve Assembly (DCVA) to an existing system, we need to verify that the new DCVA does not adversely affect the system's performance.

If no significant adjustments are required, I usually use the hydraulic placard information and compare it to a new hydrant test to determine the system's available pressure. I then subtract the pressure loss from the DCVA at the flow rate indicated on the placard.

How do people deal with adding a DCVA to a pipe schedule system with no existing documentation?

Thanks in advance!


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Pete H
7/18/2024 06:35:41 am

With no existing documentation?

I rerun the calc for the system. I get a new flow test, I draw the system to the most remote area, and I calculate said remote area, now with backflow.

If you got the placard (and the placard still has all the information legible), the method proposed in the OP sounds good, imo. But I could see an AHJ requesting that it's at least directly stated with a note dating the hydraulic placard you're using, the available pressure/demand, the cut for the backflow you're installing with a reference to the pressure loss graph and the number you got from it to reach your current safety factor. Heck even a photo of that somewhere in your submission wouldn't hurt. Just to keep everything on the up and up.

Reply
Dan Wilder
7/18/2024 07:36:55 am

As most of my AHJ's require a letter submittal when adding in backflows retroactively, we perform a new flow test, calc the existing system via survey or as-builts (it is rare that the hydraulic placard is still on the valve), and provide those results in a writeup to the AHJ...inspector comes out to verify the calc plate being installed.

What typically happens is the owner gets caught for other work completed without permits, or some poor tenant that was sold on a suite that was not up to current requirements (racking, remodels, change in storage criteria from originally approved plans)....then we get to have that conversation.

Reply
Anthony
7/18/2024 07:53:13 am

A pipe schedule system "calc" must be completed which is just a the elevation loss of the highest sprinkler and the loss through the backflow subtracted from the curve at 850 gpm (For OH). if you have 20 psi left you're compliant.

see 11.2.2 through 11.2.2.5 in NFPA 13-2016

Reply
Anthony
7/18/2024 08:07:17 am

I miss typed I mean though 11.2.2.7 * in NFPA 13-16ed

Also see NFAP 13-19 ed:
Section 19.3.2 though 19.3.2.7

Reply
NK
7/18/2024 08:07:30 am

Pete and Dan hit the nail on the head. The system needs to be recalculated with a current flow test to ensure the hydraulic calculations aren't compromised by adding a new backflow preventer (either based on field verified as-built fire sprinkler drawings or by resurveying the existing system).

Reply
Jesse
7/18/2024 10:20:32 am

I'd definitely calc the system. An insurance company I did a lot of work for in the past never would accept placard data (the VP of engineering was on 13), so we calc'd EVERYTHING.

Reply
Glenn Berger
7/18/2024 12:25:04 pm

Like others have said - Get new hydrant flow test and then hydraulic calculate the system. There used to be assumption information in some of the old FM Design Guides.

Reply
Jack G
7/18/2024 05:03:10 pm

The AHJ usually wants you do survey , new flow test and calculate.
What I d like them to accept is a method I use to determine if the water supply will accept a density upgrade, etc.
First determine the systems k factor from the hydraulic plate.
Say 500 gpm = K x sq root of p. Use 36 psi. K = 500/6,
System k = 83.33
Substitute— here we are keeping density same and adding the psi for the bfp and valves. Say 8 psi. So
GPM= 83.33 x sq root of 44 psi
Gpm = 83.33 x 6.63 = 552.47 gpm.
Check the water curve to see if it’s under, flow increased and pressure increased o the water supply curve. In hydraulic calcs we do the same thing for paths, etc.
It’s pretty accurate, and I use it to first estimate the need for a pump on a water supply or an increased density say a whouse goes from palletised storage to rack storage etc. try it here.

Reply
Kyle R
7/18/2024 08:03:50 pm

I agree w/Anthony above. For an existing Pipe Scheduled system, NFPA 13 is pretty descriptive of how to retroactively add a BFP and the 'Calc' that is required.

For an existing hydraulically calculated system, I agree with Pete/Dan, the system would need to be as-built and hydraulic calcs performed to ensure the system can support the addition PSI loss of the BFP.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT