I am designing the sprinklers for a building with unusual seismic criteria (it's designed to be seismically resilient and "floats" on seismic isolators).
The structural drawings note that design should be in accordance with ASCE 7-16 equation 13.3-4: Fp = ai ap Wp Ax / (Rp / Ip) I see from NFPA 13 (2022) appendix E that the simplified method is based on ASCE 7-16 equation 13.3-1. Do you think the NFPA 13 simplified bracing method can still be applied/adapted to this alternate equation (without hiring a structural engineer)? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
3 Comments
Dan Wilder
7/12/2024 08:43:44 am
I see a lot of our community taking on roles that should be by others (for various reasons good or bad)....seismic is one. While definitely not a seismic guy, my opinion would be:
Reply
Brian Gerdwagen FPE
7/12/2024 09:09:23 am
ASCE 7 allows seismic design complying with NFPA 13 as an alternate to presciptive compliance.
Reply
Jack G
7/12/2024 09:28:07 am
First of all, it would depend on your projects engineer that specified that.