What is a "Revamp" Under NFPA Standards?

6/21/2024

10 Comments

 
How does NFPA define a "Revamp"?

In NFPA 13 2019, Section 29.5.2 states that "Calculations shall be provided to verify that the system design flow rate will be achieved" when revamping a hydraulically designed system.

The problem me and my coworkers are having is that we cant agree on a definition of "Revamp" and NFPA does not seem to define it either.

One opinion is that any "modification" constitutes revamping, and so any sort of modification will require calculations.

Another opinion is that any sort of new addition to a system or hazard change requires calculations. We have almost always defaulted to just calc it and leave it be, but would love a more defined definition on when calcs are needed.

Thanks in advance.

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments
Pete H
6/21/2024 06:40:32 am

No actual authority behind this, not even double checking books to see if I can verify, just taking a shot in the dark:

Any change that would effect whether the original design parameters.

Did a hazard classification change? Did walls change the spacing of the heads in the design area? Were heads added to the system at a greater than 1:1 ratio? Did the system go from steel pipe armovers to sprinkler heads to flexible connections? Was an extension that would change the remote area added? Did walls change the spacing in other areas that they now cover enough square footage that they're the remote area? Was the main/bulk run altered to add additional fittings or piping? Were valves added?

If yes to any or more.... run a calc.

Reply
Scott McBride
6/21/2024 08:19:34 am

When it comes to NFPA or ICC if the definition is not within the document itself then the definition is to be common meaning from the dictionary, such as webster's.

https://www.merriam-webster.com/dictionary/revamp, which states to "Revise, Remake, Renovate or Reconstruct."

Reply
JI
6/21/2024 09:26:02 am

I agree to all of those points. The addition of a backflow preventer of some sort is another item that comes to mind.

Reply
Dan Wilder
6/21/2024 08:15:23 am

Well, Chapter 3 has definitions and also states where a term is not defined "...they shall be defined using their ordinarily accepted meanings within the context in which they are used. Merriam-Webster's Collegiate Dictionary 11th Edition, shall be the source for the ordinarily accepted meaning."

https://www.merriam-webster.com/dictionary/revamp
https://www.merriam-webster.com/thesaurus/revamp

I also checked the NFPA Glossary of Terms with no luck.

https://www.nfpa.org/downloadable-resources/definitions/nfpa-glossary-of-terms-2021

So, the dictionary definition is very broad but "to remake revise, renovate, reconstrut"...so just about anything done to the system would trigger this. Yes, this would lead to requiring a calculation for anything performed on a system but there can be good arguments against the requirement like adding pendents to a light hazard occupancy with ceilings from an ordinary hazard shell space, like for like modifications of sprinklers with the same K-factors (relocations without adding additional sprinklers), change outs from SR to QR, even use of the Eq. K-Factor flex hoses coming onto the market (without adding sprinklers), possibly scope of work compared to the remote area/distance to the riser.....but that is purely an allowance provided by the AHJ.

We have two AHJ's that are currently requiring calcs on any submittal regardless of scope or quantity, exception being removal of sprinklers...owners are not the most excited to realize keeping all those closeout documents was in their best interest vs. the cost of system surveys and new flow tests.

Reply
Glenn Berger
6/21/2024 08:26:55 am

Sounds like judicial (lawyer) speak to me because of a previous definition interpretation.

Reply
RayJ link
6/21/2024 08:45:19 am

From NFPA 13, 2019 Edition: 29.7.1.1 Where modification is made to an existing system affecting more than 20 sprinklers, the new portion shall be isolated and tested at not less than 200 psi (14 bar) for 2 hours.

Reply
Jesse
6/21/2024 10:02:26 am

I want to reiterate a couple comments related to definitions and a dictionary.

In my experience, there are some things technical committees intentionally don't define. And like Dan said, the intent is to have the user go to a dictionary.

One of my technical committees had a lively discussion for 2 hours about a dictionary definition this revision cycle. I can not begin to describe how super-exciting that was......

Reply
Troy N
6/21/2024 10:33:21 am

Great question,
We have a plan reviewer that uses this to have almost any tenant improvement calculated and I haven't found anything in NFPA to make a case the other way.

Reply
Chris Heyer
6/21/2024 10:58:01 am

I would take it on a case by case basis, but definitely if changes were made beyond the most hydraulically demanding area

Reply
Jack G
6/21/2024 12:17:09 pm

Good points and I agree.
Most AHJ s require a calculation if the revamp/ modification is more than 1 to 1, and the area is 40 sprinklers or less.
So many nightmares in a recalculation—- how old is the pipe—- has an internal been done in the last 5 years to check for corrosion around the inside of the piping to affect flow. ( especially dry sys)
Things that are not considered when the architect asks the area to be recalculated after modifications.
I go for asking for the 5 year internal. Usually not done so I get a change order to perform. Then I can put my mind to ease. Also if there are areas that need to be replaced, another change order.
The corrosion definitely will impact the calc however most recalcs are performed with a c factor of 120, wet systems, and not ask for the 5 year internal. ( liability) you can ask the architect for the c factor to be used and see if you get an answer. Then I ll bet he grants the internal.
When performing the mods, the fitters can evaluate the piping also.
For adding flex sprinklers, bfp, a new calculation should be done because of the k factor alteration.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT