Column Sprinklers in Remote Area in NFPA 409?

6/7/2024

7 Comments

 
I would like to get your thoughts on the intent of NFPA 409 7.7.3.5 which states "Discharge devices for the protection of columns within the remote area of the overhead sprinkler systems shall be included in the calculations for the overhead system."

When determining the remote area, should it be assumed that the column protection sprinklers are activated?

In the specific case that I am referring to, if column sprinklers are not activated, the remote area of the overhead system does not fall around the columns being protected.

If the column sprinklers are activated, the remote area of the overhead system shifts to fall around the columns being protected.

My thought is that column protection sprinklers should be assumed to be activated when determining the remote area of the overhead system since a fire condition near the column has the potential to activate the column protection sprinklers and the remote area of the overhead system.

If the column protection sprinklers is not included in determination of remote area, this fire condition could cause the system demand to exceed the available supply.

​What are your thoughts? Thanks!


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Dan Wilder
6/7/2024 08:12:59 am

My approach has been to do the hydraulically most demanding area for the overhead, based on the overhead only. Any column sprinkler protection that falls inside that area then is added to the overhead area.

There is a GPM requirement for the wetted surface, but no requirement to keep the same sprinkler type for the columns (7.7.3.2) so change the column protection to not be driving factor.

If your demand calculation is that close to the water supply, does the system still work when a supply calc is performed to verify foam usage (if the system is foam)?

Reply
Glenn Berger
6/7/2024 08:53:52 am

Agree with Dan. I am assuming, in this case, that the column sprinklers are on the same system as the overhead and thus they are not activating by remote means.

Reply
Jesse
6/7/2024 09:15:07 am

Agree with Dan. I generally calc the most remote area and then add the column sprinklers if needed. I'm presuming this isn't a foam-deluge

Reply
Todd E Wyatt
6/7/2024 09:36:06 am

Per the scoping Code (e.g. IBC-2021), the fire-resistance rating (FRR) for the primary structural columns is to be provided by “individual encasement protection by protecting it on all sides for the full column height” or “provided by the membrane protection provided for the wall” or by “Sprayed Fire-Resistant Materials (SFRM).”

There are (3) methods for determining the fire-resistance rating (FRR) of building elements (including FRR for primary structure (e.g. columns)), components or assemblies:

1. 703.2.1 Tested Assemblies
2. 703.2.2 Analytical Methods
3. 703.2.3 Approved Alternate Method

Based on the 703.2, the “703.2.2 Analytical Methods” is to be used “WITHOUT the use of automatic sprinklers or any other fire suppression system being incorporated” so this option is out.

That leaves “703.2.1 Tested Assemblies” or “703.2.3 Approved Alternate Method”.

If the life safety engineer can provide a tested assembly that includes an automatic sprinkler system (ASPS) meeting the requirements of the required FRR assembly for the column, the AHJ may permit it.

However, many AHJs will NOT approve the substitution of a required passive FRR assembly (e.g. encasement, FRR membrane protection of a wall, or SFRM) with an “active system” such as an ASPS. ASPS are not always 100% effective and some AHJs may use the intent of “WITHOUT the use of automatic sprinklers or any other fire suppression system being incorporated” per “703.2.2 Analytical Methods” against the requirements of “703.2.1 Tested Assemblies.”

Reply
Todd E Wyatt
6/7/2024 09:36:48 am

REFERENCES
IBC-2021
Chapter 7 Fire and Smoke Protection Features

Section 703 Fire-Resistance Ratings and Fire Tests
703.2 Fire Resistance
The fire-resistance rating of building elements, components or assemblies shall be determined in accordance with Section 703.2.1 or 703.2.2 without the use of automatic sprinklers or any other fire suppression system being incorporated, or in accordance with Section 703.2.3.
703.2.1 Tested Assemblies
A fire-resistance rating of building elements, components or assemblies shall be determined by the test procedures set forth in ASTM E119 or UL 263. The fire-resistance rating of penetrations and fire-resistant joint systems shall be determined in accordance with Sections 714 and 715, respectively.
703.2.3 Approved Alternate Method
The fire resistance of building elements, components or assemblies not complying with Section 703.2.1 or 703.2.2 shall be permitted to be established by an alternative protection method in accordance with Section 104.11.

Section 704 Fire-Resistance Rating of Structural Members
704.1 Requirements
The fire-resistance ratings of structural members and assemblies shall comply with this section and the requirements for the type of construction as specified in Table 601. The fire-resistance ratings shall be not less than the ratings required for the fire-resistance-rated assemblies supported by the structural members.
Exception: Fire barriers, fire partitions, smoke barriers and horizontal assemblies as provided in Sections 707.5, 708.4, 709.4 and 711.2, respectively.

704.2 Column Protection
Where columns are required to have protection to achieve a fire-resistance rating, the entire column shall be provided individual encasement protection by protecting it on all sides for the full column height, including connections to other structural members, with materials having the required fire-resistance rating. Where the column extends through a ceiling, the encasement protection shall be continuous from the top of the foundation or floor/ceiling assembly below through the ceiling space to the top of the column.
Exception: Columns that meet the limitations of Section 704.4.1.

704.4 Protection of Secondary Structural Members
Secondary structural members that are required to have protection to achieve a fire-resistance rating shall be protected by individual encasement protection.
704.4.1 Light-Frame Construction
Studs, columns and boundary elements that are integral elements in walls of light-frame construction and are located entirely between the top and bottom plates or tracks shall be permitted to have required fire-resistance ratings provided by the membrane protection provided for the wall.

704.13 Sprayed Fire-Resistant Materials (SFRM)

Reply
Jack G
6/8/2024 10:59:41 am

I agree that all columns be encased with proper protection. Much better for protection.
If AHJ allows sprinkler protection of the columns ( included in FRR) then the flow should be included in the calculations.
Please see Myers’s Fire July of 2022.

Reply
DJT
6/17/2024 09:30:45 am

In my experience, if you are using sprinklers, your design area will include your most remote column sprinklers. The additional flow, fed from the collector main for instance, and pressure demand overcomes a more traditional design area located higher up a roof slope and in between the gridded mains. Your hazard area should dictate at least two columns are required to flow. A taller hangar would be more demanding than one for shorter aircraft on the basis that column protection is a function of column size and height.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT