|
I have an old existing 3 story building with a basement that is being converted into an apartment building. It used to be a small paint factory.
The architect is calling for a NFPA 13R system, which is understandable since it has all the qualifications for 13R. However, about 90% of the building is exposed 2x12 construction sitting on 10x14 wood beams. The only areas designated to get ceilings are the bathrooms and some kitchen soffits. That leaves most of the building having obstructed combustible construction, which creates a whole series of problems. First, I cannot find any residential sprinklers listed for installation below this type of construction. A smooth, flat or sloped ceiling is required for all of them. The AHJ is using the 2019 version of 13R, and Section 6.2.1.3 allows the use of QR sprinklers in dwelling units, but only if there are no more than four sprinklers in the dwelling unit. All of the dwelling units require more than four sprinklers, so it seems to be that I cannot use 13R at all? Could someone please tell me if I am interpreting and applying these code sections correctly? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
13 Comments
Pete H
7/8/2024 07:07:35 am
https://www.vikinggroupinc.com/vk467-residential-upright-sprinkler-k49
Reply
Keith T. (original poster)
7/8/2024 11:03:36 am
Thank you for your reply. I had looked at the Viking Residential Upright sprinkler since I have used it on many other projects, but the listing still refers back to NFPA 13 for ceiling types, and that of course calls for smooth, flat or sloped ceilings. The listing showing the uprights installed below 14" beams was a good call, but the maximum allowed distance between primary beams is 16'-0", and on this project most of the primary beams are 17'-8" apart.
Reply
Pete H
7/8/2024 12:52:47 pm
I see what you're reading on the listing:
Pete H
7/8/2024 01:01:03 pm
Looking more at the cut... there is no figure 3C on the cut, I think Viking may have forgotten to update part of their listing. I still see no reason, given figures 4A and 4B, you cannot have your lines slightly off underneath the beams 17'-8" (as shown in figure 2 on the cut) apart and then a center line of heads spaced 9'-0" (the minimum the cut calls for) away from those lines at the same elevation.
Pete H
7/8/2024 01:14:11 pm
Aaaaand now I see you're on 2019 edition which does call out:
Anthony
7/8/2024 07:15:04 am
You can still use 13R and do a light hazard calculation. 13R has other benefits to cost reduction other than the number of heads in a calculation.
Reply
Keith T. (original poster)
7/8/2024 11:14:53 am
I have to disagree with this comment. Section 6.2.1.1 in the 2019 NFPA 13R states "Listed residential sprinklers SHALL be used unless another type is permitted by 6.2.1.3 or 6.2.1.4 (6.2.1.4 is about allowing quick-response sprinklers in mechanical closets, so it does not apply) Since we cannot use residential sprinklers due to the obstructed construction, and Section 6.2.1.3 only allows the use of QR sprinklers up to a maximum of four heads per dwelling unit, I don't believe a 13R design is possible.
Reply
Todd E Wyatt
7/8/2024 08:41:21 am
The scoping Code (e.g. IBC-2021) identifies WHERE an automatic sprinkler system (ASPS) is required based on the Occupancy Classification(s) (OC) assigned to the building (Group R-2) and/or “Specific Building Areas and Hazards”, not the Type of Construction (TC) of the building.
Reply
Todd E Wyatt
7/8/2024 10:39:59 am
"I have an old existing 3 story building with a basement that is being converted into an apartment building. It used to be a small paint factory."
Reply
Jack G
7/8/2024 10:08:40 am
Hmmmm. I m not sure that I agree.
Reply
Todd E Wyatt
7/8/2024 12:12:20 pm
"In roughly 2013, or so, A bunch of apartment buildings 5 I think burned to the ground from a fire in one of the buildings ( were occupied) unsprinklered attics, down to the ground, in the King of Prussia/ conshehawkin area of pa. (. A hotweld the culprit)."
Reply
Jack G
7/8/2024 10:31:47 am
I ve replied above and would like to add that is beneficial to buy the straight code book, AND the commentary version as it provides explanations and examples. The same holds true with NFPA phamplets—- IE NFPA 13 , 14, 20, and the automatic sprinkler,standpipe and pump handbooks.
Reply
Jack G
7/8/2024 01:32:26 pm
Exactly. Arch, Eng, AHJ, put out a set of documents that were not correct. Major fire.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop Aug '26 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
October 2026
PE PREP SERIES |
RSS Feed
