Are sprinklers required for an H-3 Occupancy, retail fireworks (1.4g class) if less than 125lb?
IBC Section 415.1 states only need a automatic sprinkler if in excess of 125lb (25% of net weight of package fireworks). But, in Chapter 10 Table 1006.2.1, regarding means of egress, it says Not Permitted regarding H-3 units with no sprinkler system. Any help here is appreciated. Thank you! Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Brett
6/19/2024 06:52:36 am
All new group H occupancies require automatic sprinkler systems. See 415.4 and 903.2.5 of the 2024 IBC.
Reply
Pete H
6/19/2024 07:04:27 am
NYS Building Code (Adapted from IBC) 2020 reads:
Reply
Glenn Berger
6/19/2024 08:10:13 am
Agree with above comments; however -
Reply
Jesse
6/19/2024 09:53:35 am
Glenn makes an important point about the maximum allowable quantities. MAQ is a very important consideration.
Reply
Todd E Wyatt
6/19/2024 08:44:14 am
The scoping Code (e.g. IBC-2021) identifies where an automatic sprinkler system (ASPS) is required based on the Occupancy Classification(s) (OC) assigned to the building.
Reply
Warren M
6/19/2024 10:40:48 am
Everyone has addressed the IBC requirements but NFPA 13 does not address fireworks. So what Hazard Classification are you going to assign to this?
Reply
Jack G
6/19/2024 11:18:10 am
If it’s classified an H-3 there has to be other chemicals, gasses etc that pose a health risk. H occupancies require sprinklers.
Reply
Todd E Wyatt
6/19/2024 05:01:17 pm
The scoping Code (e.g. IBC-2021) defines the following applicable terms in Chapter 2:
Reply
Todd E Wyatt
6/19/2024 05:02:06 pm
REFERENCES
Reply