|
Can ESFR K-Factors be different within the same area, just at different roof elevations? The roof elevations here are dictating different design requirements. We have multiple ESFR sprinkler systems throughout a new building. The building has two different roof elevations, 38'-4" for the majority of the building, 43'-4" on remainder. We're under NFPA 13-2019 Edition.
The Contractor is wanting to use K-16.8 pendents at 52 psi at the low roof. K-25.2 at 40 psi at the high roof. One sprinkler system will cover the area where the roof steps, with two design areas (high/low roof). The outer thirds of the building separating the roof elevations will have full height concrete tilt-up walls. The center third only has a large open girder truss, with nothing stopping heat from traveling between the low and high roof. Section 7.2.2.6 says ESFR K-factor shall be selected for appropriate hazard. Sections 20.6.2.6 & 23.6.2 indicate ESFR shall be based on building height (amongst other things). Section 23.1.2 for Draft curtains, only reference the adjacent system with standard response sprinklers, not ESFR with different K factors. Section 27.2.4.9.2 says K-factors can't be mixed "for the purpose of minimizing sprinkler over discharge" (consolidated), which is not the case in this scenario. The Roof elevations are dictating the different design requirements. The K-25.2 sprinklers could be used throughout, but the low roof would only require 25 psi and the high roof 40 psi. However, there is a large cost savings going with the K-16.8 sprinkler for the majority of the building, along with additional storage allowance of exposed nonexpanded plastics. My thinking says that there should be some kind of draft stop at the girder truss/roof step to collect the heat, separating the two K-factor/roof elevations, but I am not finding a code reference that dictates it. Any input will help. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments
Anthony
7/10/2024 07:42:20 am
See: NFPA 13-2019: 20.10 (1) , (2) and (3).
Reply
Casey Milhorn
7/10/2024 08:13:42 am
I would agree with Anthony on not needing a draft stop. From a practical perspective I think it's fine. You have a 3/4 outlet for one and 1 inch outlet on the other. That all but alleviates the chance of putting the wrong head in. It doesn't clarify if these are on two different systems, but assuming they are, if a fire were to occur at the elevation change, discharge should be way overkill if heads activate on both systems, effectively splitting up the waterflow and reducing friction loss. I wouldn't lose any sleep over this one. Overall I'm of the opinion bigger isn't always better in fire sprinkler hydraulics.
Reply
Glenn Berger
7/10/2024 08:19:08 am
The 2022 edition of NFPA 13 had significant changes to the storage protection chapters (again).
Reply
Dan Wilder
7/10/2024 08:19:50 am
Also check out 19.2.2 for Adjacent Design Methods, Section 3 - "The requirements of 19.2.2(1) (The extension of the higher hazard 15' into the lower hazard area) shall not apply to the extension of more demanding criteria from an upper ceiling level to beneath a lower ceiling level where the difference in height between the ceiling levels is at least 2 ft, located above an aisle, where the aisle has a minimum 2ft horizontal separation form the adjacent hazard on each side. April 2019 #9 NFSA Tech Notes
Reply
Jesse
7/10/2024 08:25:22 am
Agree that you can use different K-factor ESFR sprinklers and a draft stop won't be needed. I'd also reiterate Dan's comment about the higher hazard.
Reply
Pete H
7/10/2024 10:06:04 am
Agree with the consensus as Anthony initially outlined: K25 throughout is the better practice and overall install, especially where maintenance is concerned.
Reply
Jack G
7/10/2024 10:46:38 am
I would design using 1 - k factor. I also agree that a draft stop is not required for the 1– or 2 k factor sprinklers.
Reply
Jack G
7/10/2024 11:26:08 am
In addition, if the 16.8 k factor solves the problem with higher benefits, then that’s the route.
Reply
Dwight Havens
7/10/2024 12:46:24 pm
The topic of safety factors was introduced in this discussion. This is a topic for another discussion, but I would add here that safety factors are often required by an AHJ, to offset the lack of information on the variability of the available water supply. Designs are often based on a single water test, despite the code requiring that the variability of the water supply be taken into account in the design.
Reply
OP
7/11/2024 11:56:27 am
All, Thanks for your input. I've done more research on this since this question was sent in.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop Sept '26 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
October 2026
PE PREP SERIES |
RSS Feed
