Reduce Pressure to Site Loop when FD Arrives?

6/9/2023

10 Comments

 
My community has a number of fire pump pressurized fire loop systems that include private fire hydrants.

These facilities are large industrial structures and require pressures in excess of 200 psi for their sprinkler systems. The hydrants are needed to provide water access within code required distances.

To avoid injury to fire personnel and damage to our pumper trucks, is it possible to decrease the fire pump pressure to a manageable pressure once we have arrived on site and assessed the situation?

This would allow us to operate normally while the existing sprinklers, though not at full discharge, are still adding water to the situation.

I am looking for solutions that don't involve millions of dollars or running hose for a quarter mile or more.

Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments
Pete H
6/9/2023 06:37:11 am

It seems difficult if this has to be a means of controlling the pressure only temporarily for when the fire department is on site.

If you can just deal with overall pressure control, fire pump mains are often equipped with pressure relief valves (pretty standard on diesel pumps) or discharge relief valves, which would probably help.

If it needs to be temporary... there are manual pressure regulating/relief valves, but I don't know if any are listed for fire protection piping.

Reply
Glenn Berger
6/9/2023 08:12:42 am

I recommend that you talk to the responding fire department. They may bring their own PRV's to handle the delivered pressures.

Reply
SCHULMAN
6/9/2023 08:20:13 am

can you slap one of these on the back of the truck? https://www.akronbrass.com/intake-pressure-relief-valve-53

Reply
Danial Bartle
6/9/2023 09:47:52 am

While this is a much nicer and newer version than when I was working on a truck, this is most likely the type that is on the intake of the pump. It has a relief valve and most are field adjustable. Definitely need a pre-planned SOP for your facility
https://www.akronbrass.com/valves/revolution-intake-valve-swivel-elbow-5-in-storz.

Reply
Alex
6/9/2023 08:43:08 am

I don't have a specific code reference, but I don't believe you would be able to decrease your pressure. During a fire, your sprinkler system's demand is likely to increase as more sprinklers activate and additional hose streams start to flow.

As others have mentioned, it could be worthwhile to discuss this with the responding fire departments and explore the option of them providing their own PRVs

Reply
Dan Wilder
6/9/2023 09:29:25 am

This sounds like some additional equipment will be needed for the responding crews (not millions of dollars but still a cost), a site SOP be created and implemented, the site flagged with that SOP, notification to the sister/companion responding departments, and signage be provided by the owner due to the site specific conditions.

Reply
Casey Milhorn
6/9/2023 10:13:39 am

I agree mostly with the comments. If the sprinkler systems are designed to operate in excess of 200 psi, I would be afraid of someone on site making the call on pressure reduction for them. I'm assuming ESFR Systems, and they need a lot of water, in a short amount of time, so as to control the fire spread early. Any monkeying with that recipe could be bad. I also suggest some type of PRV on the hydrant itself. If the fire sprinkler system is properly designed, installed, and maintained, the responding fire department should be limited to mostly clean up efforts. Definitely need site specific SOP for these locations and I wouldn't be afraid of asking for some $ for some PRV's for the trucks. Split between a few facilities, it should be pocket change for them.

Reply
Mark Harris
6/9/2023 06:00:19 pm

Agree with the comments that don't mess with the automatic fire sprinkler design including the fire pump. There are distribution centers that have burned down because system or pump were shut off before fire was totally extinguished. Could be addressed in design with fire hydrants off a hydrant loop and only the sprinklers downstream of the fire pump but if large building with multiple riser lead ins that would result in a high pressure underground loop for sprinklers and city pressure underground for the hydrants which could be costly. The pressure reducing device for truck pump protection and training and operation plans sound like the best answer.

Reply
James M.
6/14/2023 11:31:48 am

If the system pressure requires 200psi, I think you would need to supplement the system through the FDC at that as well.
The hydrant intake on most trucks have a screw to change the pressure setpoint, and then anything over that pressure autmatically dumps.

Reply
Scott McCormick
6/15/2023 11:35:58 am

What is the reason for this? I've had several warehouse projects and this was brought up. I immediately put the stops to this for several reasons. 1 the Fire Dept uses fire engines to connect to the private fire hydrant. These are "fire pumps", if the FD connects a pumper to a hydrant and then the pump turns on and now 90% of the water will be dumped on the ground. 2 the landscaper or street sweeper operator will get killed when the pump kicks on and 2,000 GPM is coming out of the end of the hose.

I do have 2 large warehouses 800,000 sq ft and 400,000 sq ft that share a 127,000 gal water tank with 2 pressurized loops and a few hydrants off of this loop. The reason for this is there is 27 systems in the larger building so each system riser is connected to this loop. Other than this reason I do not see the purpose for this. Each hydrant has a sign and ring on it to signify that this is part of a pressurized system, and the FD will respond.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT