If a stair structure is supporting the fire barriers that enclose the exit enclosure, does the stair structure have to be fire rated as well?
Looking specifically at IBC 2018 Section 707.5.1 and NFPA 101 (2018) Section 7.1.3.2. If there is a fire inside a stair, the means of egress is no longer usable and at that point are you protecting the interior of the building from the fire inside the exit enclosure? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Glenn Berger
6/8/2023 08:14:51 am
You always want the exit stair to be a safe, protected enclosure. If the event happens within one of the enclosures, then the other exit is used.
Reply
SCHULMAN
6/8/2023 08:22:43 am
any structure supporting rated construction also has to be constructed of materials rated to the same (fire resisting) duration as the enclosure ... any steel stair should do the job if I understand the question correctly. If someone is trying to build a rated egress stair out of wood I would question the method ...
Reply
Todd E Wyatt
6/8/2023 08:52:30 am
SUMMARYIf the "stairway" is an Interior Exit Stairway (IES) or an Exit Access Stairway (EAS), it is required to be protected by fire-resistance rated (FRR) Fire Barriers (FB) and the supporting construction (floor construction & primary structure) is also required to have the same FRR as the FBs.
Reply
Todd E Wyatt
6/8/2023 08:54:12 am
REFERENCES
Reply
Capone
6/19/2024 12:34:16 pm
What if the exit access stairway complies with an exception to omit enclosing the stair in a shaft? Would an exit access stair frame, treads and landing need to be rated in an atrium? Is it as simple as the elements must comply with Table 601 for structural frame and floor assembly rating? Todd I believe nailed it. Overall the intention of the code is for the entire means of egress to meet the minimum required fire resistance rating (i.e. 1 or two hours usually). The code typically assumes that a fire will not be located in the exit enclosure especially with other requirements limiting combustibles and non essential penetrations into the stair enclosure. A fire in the exit enclosure leans toward arson. The requirements are not typically meant to deal with intentional fires.
Reply
T
6/6/2024 02:55:36 pm
Tom,
Reply