MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Use 4-ft Obstruction Rules for 2-ft Obstruction?

6/30/2023

8 Comments

 
I’m designing a wet system protecting storage utilizing 25.2K ESFR pendents.

I have some continuous obstructions greater than 2-ft wide (less than 4-ft wide) that require protection below the obstructions. It's under the 2018 IBC, and NFPA 13 2019 edition. The obstructions are mostly closely-spaced conduit groups.

I would like to place the ESFR pendents within 3-inches to the side of the group with the deflector 6-inches below and have listed water shields installed for intermediate level rack type protection.

Chapter 9 in NFPA 13 seems to allow this, but it is in a subsequent section dealing with obstructions greater than 4-ft wide. The verbiage and the annex figure do not clearly state the width of the obstruction.

This protection scheme will be clearly denoted and submitted to the AHJ, but I want to get input if there are any potential issues with this design.

​Any questions, comments, or concerns will be greatly appreciated!

​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Dan Wilder
6/30/2023 08:03:29 am

Section 9.5.1.3 says that the Sections 9.5.2 through 9.5.5 apply to all sprinkler types unless modified to be more restrictive.

9.5.5.3.1 says obstructions over 4' wide.

9.5.5.3.1.2(2) through 9.5.5.3.1.5 are the sections you reference for the adjacent vs under.

9.5.5.3.3 says all sprinklers shall be the same type and specifically mentions ESFR

14.2.11.3 MODIFIES 9.5.5.3.1 for ESFR for width and location requirements, but protection beneath (other than spacing requirements) are not changed.

There is no other location beneath obstruction requirements that are modified within Chapter 14, only the more restrictive width and location of the obstruction requirements for when so I would say you've got a strong case.

It would be more beneficial to either have the conduit moved to be centered between branch lines/sprinklers or possible move the overhead BL/sprinklers to be centered over the obstruction purely out of a cost benefit but I know that is not always possible.

Reply
Jesse
6/30/2023 08:10:39 am

Dan is spot-on, but I'd really emphasize trying to get the MEP to move those cable trays.

Reply
Glenn Berger
6/30/2023 08:20:04 am

To me the obstruction rules were clear before I started going into the field to view obstructions. With field experience, I have questioned the minimum requirements of NFPA 13 as it relates to obstructions (and other items).

You are the DOR, if you feel that additional sprinklers are required below obstructions then add that requirement to the contract plans and specifications.

I use a basic rule, if I cannot see the sprinkler above an obstruction, then additional sprinklers are required below the obstruction, regardless of size of the obstruction.

Reply
Colin Lusher, PE
6/30/2023 08:50:10 am

No offense intended, but this is the reason people dislike AHJ's.... why make up your own rules?

"if I cannot see the sprinkler above an obstruction, then additional sprinklers are required below the obstruction, regardless of size of the obstruction"

This doesn't make much sense; if there is a 3-ft obstruction 6-ft below the sprinkler (standard spray), then you're not going to see the sprinkler, but the sprinkler will spray around the obstruction due to the fully developed spray pattern. Have you ever seen a sprinkler actually discharge? The floor under that duct will get plenty of water on it. The rules of NFPA 13 are fairly conservative and have been developed by extensive testing. No need to make up your own rules in my opinion.

Reply
Patrick Drumm
7/9/2023 12:37:54 pm

I agree with Colin. Also, it is very important to understand the legistlation regarding state building codes, fire codes, and their adoption of NFPA standards in your area. In a few states I am familiar with, the State Fire Marshall's Office is identified specifically as the AHJ and only their office can modify code requirements. There are other formal processes for interpretation including reviews by the state fire boards. City and town officials are directed to enforce the codes as they are written. That does not mean that I do not do my best to reach agreements with local officials, but if they were blatantly disregarding codes and making up their own rules it would be an issue that would need to be addressed with the state fire board.

Casey Milhorn
6/30/2023 09:20:42 am

I would also add that there was some fairly extensive recent testing done on obstructions to ESFR sprinklers and there were some very favorable results. I think they had another phase or two planned, and this was 1 or 2 years ago. Hopefully there should be some results coming out soon on this, if they haven't already. It will take some time for NFPA to review and adopt any changes of course.

Reply
Franck
7/3/2023 02:35:37 pm

Wasn’t it for obstruction at ceiling level from construction elements (beams, joists…) and position of sprinklers underneath (with possible greater distances than initially allowed), rather than obstruction below sprinklers ?

There was some research results on that topic at the last NFPA conference in Las Vegas (presented by FM global with modelization - later confirmed by actual testing).

Reply
Chad
8/15/2023 11:21:29 am

May I add a small twist to this discussion? What if we are talking about elevated conveyors, such as in a large distribution center, where the dimension of the conveyor exceeds 4'?

Does the requirement for a sprinkler(s) to be located under the conveyor apply only if there is or will be storage or some other combustible under the conveyor?

What if the owner says that there will be no storage so no sprinkler is required? NFPA 13 doesn't specify this exception though some believe it is implied.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT