Construction Type of Air-Supported Structure?

6/16/2023

8 Comments

 
We have a project with an air supported dome structure. It's serving around 430,000+ sqft of indoor sports.

However, I am a bit confused with the type of construction this would be clasified as.

As per NFPA 5000 and IBC, an air-supported structure can be Type II-B (000), but wouldn't we be limited on allowable floor area restrictions for the site of the building?

Are there any exceptions to sprinkler protection for a building like this?

I would really appreciate your point of view, thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Pete H
6/16/2023 07:03:05 am

I don't know of an exception personally. Because I agree with you, by IBC standards (2020 edition), this is an A-4 occupancy (indoor sporting arena). It's assumedly to be sprinklered (you're asking this question on a fire protection forum), so I'd look at Table 506.2 in the IBC. Based on what I'm seeing: The allowable area for a sprinklered A-4 occupancy built out of type II-B construction is 38,000 sq. ft. Type I would be unlimited.

Take with a grain of salt, I didn't check NFPA 5000 or look into air supported structures specifically, just type II-B construction for the occupancy.

Reply
Dan Wilder
6/16/2023 08:09:05 am

NFPA 102 Section 9.5 would likely be helpful to allow some omission of sprinklers when over the field area (pending roof height) and over seating areas.

Reply
Glenn Berger
6/16/2023 08:16:02 am

The area over the stadium itself cannot be physically sprinklered. Most indoor (or covered) sports stadiums do not contain fire sprinkler systems in the arena area.

Sprinklers are provided all areas where physically possible.

With that said - Automatic smoke exhaust (or smoke management) systems are provided to ensure safe egress. Extra egress paths are provided.

You need to work with the AHJs and other safety professionals to ensure that an adequate level of fire safety is provided. You may want to research major sports arenas to obtain back-up information.

Reply
Jesse
6/16/2023 08:24:19 am

I'm going to reiterate what Glenn is saying. Its not feasible to protect over the playing field, and most sports facilities are like this.As an insurance guy I did assessments on several NBA arenas and they are, but more to protect the cat-walks and scoreboard / jumbo-tron things

Reply
Todd E Wyatt
6/16/2023 08:58:31 am

SUMMARY
This “membrane structure” (e.g. air-supported, air-inflated, membrane-covered cable, membrane-covered frame and tensile membrane structures) would be classified as a A-3/A-4 Occupancy Classification and requires to be protected by an automatic sprinkler system (ASPS). Based on the anticipated Building Area (BA) of +430,000 SF, only Type IA and Type IB (both “Unlimited” UL) would be compliant.

This “membrane structure” is required to also meet the applicable Code (e.g. 2021 IBC Chapter 31 Special Construction, Section 3102 Membrane Structures) which states in 3102.3 Type of Construction
That “Noncombustible membrane structures shall be classified as Type IIB construction. Noncombustible frame or cable-supported structures covered by an approved membrane in accordance with Section 3102.3.1 shall be classified as Type IIB construction. Heavy timber frame-supported structures covered by an approved membrane in accordance with Section 3102.3.1 shall be classified as Type IV-HT construction. Other membrane structures shall be classified as Type V construction.” Because the Building Area (BA) surpasses Type IIB’s allowable BA of 62,000 SF, this Type of Construction is not compliant.

EXPLANATION
The requirement for a building to be protected by an automatic sprinkler system (ASPS) is based on the scoping Code (e.g. 2021 IBC). Chapter 9 Fire Protection and Life Safety Systems, Section 903 Automatic Sprinkler Systems, 903.2 Where Required identifies the ASPS requirements based on the building’s Occupancy Classification (OC). Based on your description, this building would be classified as Group A Assembly (see 303.1), either as an A-3 (gymnasiums w/o spectator seating) and/or A-4 (indoor sporting events and activities with spectator seating). It does not meet the intent of A-5 (assembly uses intended for participation in or viewing outdoor activities).

Assuming it is A-3 and/or A-4, we review 903.2.1 Group A and find that an ASPS is required for A-3 and/or A-4 if any one of the following parameters are met :
1. The fire area exceeds 12,000 square feet (1115 m2).
2. The fire area has an occupant load of 300 or more.
3. The fire area is located on a floor other than a level of exit discharge serving such occupancies.

Since this building meets all parameters, an ASPS is required.

Once we know the OCs and if an ASPS is required, we can then evaluate the “allowables” (Building Area, Number of Stories, and Building Height) per Chapter 5 General Building Heights and Areas to determine the compliant Types of Construction (TC) per Chapter 6 Types of Construction. The Building Area (BA) of +430,000 SF will be the deciding factor. Based on TABLE 506.2 ALLOWABLE AREA FACTOR, only Type IA and Type IB, both “Unlimited” (UL) would be compliant :

A-3 & A-4 (S1 : Single Story)
Type IA UL
Type IB UL
Type IIA 62,000
Type IIB 38,000
Type VA 46,000
Type VB 24,000

Per 2021 IBC, “Sections 3102.1 through 3102.8 shall apply to air-supported, air-inflated, membrane-covered cable, membrane-covered frame and tensile membrane structures, collectively known as membrane structures, erected for a period of 180 days or longer.”
Per 2021 IBC, a “NONCOMBUSTIBLE MEMBRANE STRUCTURE” is defined as “A membrane structure in which the membrane and all component parts of the structure are noncombustible.” A “TENSILE MEMBRANE STRUCTURE” is defined as “A membrane structure having a shape that is determined by tension in the membrane and the geometry of the support structure. Typically, the structure consists of both flexible elements (e.g., membrane and cables), nonflexible elements (e.g., struts, masts, beams and arches) and the anchorage (e.g., supports and foundations). This includes frame-supported tensile membrane structures.”

Reply
Todd E Wyatt
6/16/2023 08:59:15 am

REFERENCES
2021 IBC
303.4 Assembly Group A-3
Group A-3 occupancy includes assembly uses intended for worship, recreation or amusement and other assembly uses not classified elsewhere in Group A including, but not limited to:
Gymnasiums (without spectator seating)
Indoor swimming pools (without spectator seating)
Indoor tennis courts (without spectator seating)
303.5 Assembly Group A-4
Group A-4 occupancy includes assembly uses intended for viewing of indoor sporting events and activities with spectator seating including, but not limited to:
Arenas
Skating rinks
Swimming pools
Tennis courts
303.6 Assembly Group A-5
Group A-5 occupancy includes assembly uses intended for participation in or viewing outdoor activities including, but not limited to:
Amusement park structures
Bleachers
Grandstands
Stadiums

Chapter 4 Special Detailed Requirements Based on Occupancy and Use

Chapter 5 General Building Heights and Areas
Section 503 General Building Height and Area Limitations
503.1 General
Unless otherwise specifically modified in Chapter 4 and this chapter, building height, number of stories and building area shall not exceed the limits specified in Sections 504 and 506 based on the type of construction as determined by Section 602 and the occupancies as determined by Section 302 except as modified hereafter. Building height, number of stories and building area provisions shall be applied independently. For the purposes of determining area limitations, height limitations and type of construction, each portion of a building separated by one or more fire walls complying with Section 706 shall be considered to be a separate building.
Section 503 General Building Height and Area Limitations
503.1 General
Unless otherwise specifically modified in Chapter 4 and this chapter, building height, number of stories and building area shall not exceed the limits specified in Sections 504 and 506 based on the type of construction as determined by Section 602 and the occupancies as determined by Section 302 except as modified hereafter. Building height, number of stories and building area provisions shall be applied independently. For the purposes of determining area limitations, height limitations and type of construction, each portion of a building separated by one or more fire walls complying with Section 706 shall be considered to be a separate building.
506.1 General
The floor area of a building shall be determined based on the type of construction, occupancy classification, whether there is an automatic sprinkler system installed throughout the building and the amount of building frontage on public way or open space.

A-3 & A-4 (S1 : Single Story)
Type IA UL
Type IB UL
Type IIA 62,000
Type IIB 38,000
Type VA 46,000
Type VB 24,000

Chapter 6 Types of Construction
602.2 Types I and II
Types I and II construction are those types of construction in which the building elements specified in Table 601 are of noncombustible materials, except as permitted in Section 603 and elsewhere in this code.
602.3 Type III
Type III construction is that type of construction in which the exterior walls are of noncombustible materials and the interior building elements are of any material permitted by this code. Fire-retardant-treated wood framing and sheathing complying with Section 2303.2 shall be permitted within exterior wall assemblies of a 2-hour rating or less.
602.4 Type IV
Type IV construction is that type of construction in which the building elements are mass timber or noncombustible materials and have fire-resistance ratings in accordance with Table 601.
602.5 Type V
Type V construction is that type of construction in which the structural elements, exterior walls and interior walls are of any materials permitted by this code.

Chapter 9 Fire Protection and Life Safety Systems
Section 903 Automatic Sprinkler Systems
903.1 General
Automatic sprinkler systems shall comply with this section.
903.2 Where Required
Approved automatic sprinkler systems in new buildings and structures shall be provided in the locations described in Sections 903.2.1 through 903.2.12.
903.2.1 Group A
An automatic sprinkler system shall be provided throughout buildings and portions thereof used as Group A occupancies as provided in this section.
903.2.1.3 Group A-3
An automatic sprinkler system shall be provided throughout stories containing Group A-3 occupancies and throughout all stories from the Group A-3 occupancy to and including the levels of exit discharge serving that occupancy where one of the following conditions exists:
1. The fire area exceeds 12,000 square feet (1115 m2).
2. The fire area has an occupant load of 300 or more.
3. The fire area is located on a floor other than a level of exit discharge serving such occupancies.
903.2.1.4 Group A-4
An automatic sprinkler system shall be provided throughout stories containing Group A-4 occupancies and throughout all stories from the Group A-4 occupancy to and including the levels of exit discharge servin

Reply
Todd E Wyatt
6/16/2023 09:00:15 am

REFERENCES continued ...
2021 IBC

903.2.1.4 Group A-4
An automatic sprinkler system shall be provided throughout stories containing Group A-4 occupancies and throughout all stories from the Group A-4 occupancy to and including the levels of exit discharge serving that occupancy where one of the following conditions exists:
1. The fire area exceeds 12,000 square feet (1115 m2).
2. The fire area has an occupant load of 300 or more.
3. The fire area is located on a floor other than a level of exit discharge serving such occupancies.

Chapter 31 Special Construction
Section 3102 Membrane Structures
3102.1 General
The provisions of Sections 3102.1 through 3102.8 shall apply to air-supported, air-inflated, membrane-covered cable, membrane-covered frame and tensile membrane structures, collectively known as membrane structures, erected for a period of 180 days or longer. Those erected for a shorter period of time shall comply with the International Fire Code. Membrane structures covering water storage facilities, water clarifiers, water treatment plants, sewage treatment plants, greenhouses and similar facilities not used for human occupancy are required to meet only the requirements of Sections 3102.3.1 and 3102.7. Membrane structures erected on a building, balcony, deck or other structure for any period of time shall comply with this section.
3102.2 Tensile Membrane Structures and Air-Supported Structures
Tensile membrane structures and air-supported structures, including permanent and temporary structures, shall be designed and constructed in accordance with ASCE 55. The provisions in Sections 3102.3 through 3102.6 shall apply.
3102.3 Type of Construction
Noncombustible membrane structures shall be classified as Type IIB construction. Noncombustible frame or cable-supported structures covered by an approved membrane in accordance with Section 3102.3.1 shall be classified as Type IIB construction. Heavy timber frame-supported structures covered by an approved membrane in accordance with Section 3102.3.1 shall be classified as Type IV-HT construction. Other membrane structures shall be classified as Type V construction.
Exception: Plastic less than 30 feet (9144 mm) above any floor used in greenhouses, where occupancy by the general public is not authorized, and for aquaculture pond covers is not required to meet the fire propagation performance criteria of Test Method 1 or Test Method 2, as appropriate, of NFPA 701.
3102.3.1 Membrane and Interior Liner Material
Membranes and interior liners shall be either noncombustible as set forth in Section 703.3 or meet the fire propagation performance criteria of Test Method 1 or Test Method 2, as appropriate, of NFPA 701 and the manufacturer's test protocol.
Exception: Plastic less than 20 mil (0.5 mm) in thickness used in greenhouses, where occupancy by the general public is not authorized, and for aquaculture pond covers is not required to meet the fire propagation performance criteria of Test Method 1 or Test Method 2, as appropriate, of NFPA 701.
3102.4 Allowable Floor Areas
The area of a membrane structure shall not exceed the limitations specified in Section 506.
3102.5 Maximum Height
Membrane structures shall not exceed one story nor shall such structures exceed the height limitations in feet specified in Section 504.3.
Exception: Noncombustible membrane structures serving as roofs only.
3102.6 Mixed Construction
Membrane structures shall be permitted to be utilized as specified in this section as a portion of buildings of other types of construction. Height and area limits shall be as specified for the type of construction and occupancy of the building.
3102.6.1 Noncombustible Membrane
A noncombustible membrane shall be permitted for use as the roof or as a skylight of any building or atrium of a building of any type of construction provided that the membrane is not less than 20 feet (6096 mm) above any floor, balcony or gallery.
3102.6.1.1 Membrane
A membrane meeting the fire propagation performance criteria of Test Method 1 or Test Method 2, as appropriate, of NFPA 701 shall be permitted to be used as the roof or as a skylight on buildings of Type IIB, III, IV-HT and V construction, provided that the membrane is not less than 20 feet (6096 mm) above any floor, balcony or gallery.
3102.7 Engineering Design
The structure shall be designed and constructed to sustain dead loads; loads due to tension or inflation; live loads including wind, snow or flood and seismic loads and in accordance with Chapter 16.
3102.7.1 Lateral Restraint
For membrane-covered frame structures, the membrane shall not be considered to provide lateral restraint in the calculation of the capacities of the frame members.
3102.8 Inflation Systems
Air-supported and air-inflated structures shall be provided with primary and auxiliary inflation systems to meet the minimum requirements of Sections 3102.8.1 through 3102.8.3.
3102.8.1 Equipment Requirements
The inflation system shall consist of one o

Reply
Ben Hoffmann
1/9/2024 03:44:28 pm

Check IBC Section 507 Unlimited Area Buildings, specifically Section 507.4, Sprinklered, one-story buildings, Exception 2 where automatic sprinkler system shall not be required in areas occupied for indoor participant sports provided you have direct egress to the outside, have a fire alarm system, and have sprinklers in the ancillary / non-sport areas (storage, locker rooms, etc.)

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Aug '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT