MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Does EIFS Trigger Sprinklers on Exterior Corridor?

6/14/2023

8 Comments

 
We have a multistory hotel building with the rooms opening to an exterior corridor. There is Exterior Insulation Finish System (EIFS) along the walls of the exterior corridor.

NFPA 13 (2022), Section 9.2.3.3 allows omission of sprinklers from exterior exit corridors where the exterior wall of the corridor is at least 50% open and where the corridor is entirely of noncombustible construction.

It seems from research that EIFS is considered combustible and would require sprinkler protection along the exterior corridor.

Has anyone done more research on this or has this come up before for other projects with EIFS in the exterior corridors and ultimately required sprinkler protection?

​Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Jesse
6/14/2023 08:11:07 am

Oh the stories I could tell about EIFS...

Yes, EIFS is absolutely combustible. And yes, it should trigger exterior protection.

Reply
Todd E Wyatt
6/14/2023 08:47:31 am

If the EIFS substrate is of “noncombustible, limited-combustible, or fire-retardant materials”, an automatic sprinkler system is permitted to be omitted per 2022 NFPA 13.
2022 NFPA 13 defines “noncombustible and limited-combustible” in Chapter 4.

The Means of Egress component you describe (“exterior corridor”) is an “Egress Balcony” per 2021 IBC Section 1021. Balconies used for egress purposes shall “conform to the same requirements as corridors for minimum width, required capacity, headroom, dead ends and projections.” This includes the fire-resistance rating (FRR) of the “Egress Balcony’s” walls. Per 2021 IBC TABLE 1020.2 CORRIDOR FIRE-RESISTANCE RATING, Group R occupancies (Hotels are R-1) require an automatic sprinkler system (ASPS) in the “corridors” and the corridors are required to have a 0.5-Hour or a 1-Hour FRR. This FRR corridor separation is not required “where the exterior egress balcony is served by not less than two stairways and a dead-end travel condition does not require travel past an unprotected opening to reach a stairway.”

Reply
Todd E Wyatt
6/14/2023 08:48:12 am

REFERENCES
2022 NFPA 13
A.3.3.120 Limited-Combustible Material.
Material subject to increase in combustibility or flame spread index beyond the limits herein established through the effects of age, moisture, or other atmospheric condition is considered combustible. See NFPA 259 and NFPA 220.

Chapter 4 General Requirements
4.9 Noncombustible Materials and Limited-Combustible Materials.
4.9.1* Noncombustible Material.
4.9.1.1
A material that complies with any of the following shall be considered a noncombustible material:
(1) *The material, in the form in which it is used, and under the conditions anticipated, will not ignite, burn, support combustion, or release flammable vapors when subjected to fire or heat.
(2) The material is reported as passing ASTM E136, Standard Test Method for Assessing Combustibility of Materials Using a Vertical Tube Furnace at 750°C.
(3) The material is reported as complying with the pass/fail criteria of ASTM E136 when tested in accordance with the test method and procedure in ASTM E2652, Standard Test Method for Assessing Combustibility of Materials Using a Tube Furnace with a Cone-shaped Airflow Stabilizer, at 750°C.
4.9.1.2
Where the term limited-combustible is used in this standard, it shall also include the term noncombustible. [5000:7.1.4.1.2]
4.9.2* Limited-Combustible Material.
A material shall be considered a limited-combustible material where both of the following conditions of 4.9.2(1) and 4.9.2(2), and the conditions of either 4.9.2.1 or 4.9.2.2, are met:
(1) The material does not comply with the requirements for a noncombustible material in accordance with 4.9.1.
(2) The material, in the form in which it is used, exhibits a potential heat value not exceeding 3500 Btu/lb (8150 kJ/kg), when tested in accordance with NFPA 259.
4.9.2.1
The material shall have a structural base of noncombustible material with a surfacing not exceeding a thickness of 1⁄8 in. (3.2 mm) where the surfacing exhibits a flame spread index not greater than 50 when tested in accordance with ASTM E84, Standard Test Method for Surface Burning Characteristics of Building Materials, or UL 723, Standard for Test for Surface Burning Characteristics of Building Materials. [5000:7.1.4.2.1]
4.9.2.2
The material shall be composed of materials that in the form and thickness used, neither exhibit a flame spread index greater than 25 nor evidence of continued progressive combustion when tested in accordance with ASTM E84 or UL 723 and are of such composition that all surfaces that would be exposed by cutting through the material on any plane would neither exhibit a flame spread index greater than 25 nor exhibit evidence of continued progressive combustion when tested in accordance with ASTM E84 or UL 723. [5000:7.1.4.2.2]
4.9.2.3
Materials shall be considered limited-combustible materials where tested in accordance with ASTM E2965, Standard Test Method for Determination of Low Levels of Heat Release Rate for Materials and Products Using an Oxygen Consumption Calorimeter, at an incident flux of 75 kW/m2 for a 20-minute exposure, and both the following conditions are met:
(1) The peak heat release rate shall not exceed 150 kW/m2 for longer than 10 seconds.
(2) The total heat released shall not exceed 8 MJ/m2.
4.9.2.4
Where the term limited-combustible is used in this standard, it shall also include the term noncombustible. [5000:7.1.4.2.4]

9.2.3* Exterior Projections.
9.2.3.1*
Sprinklers shall be permitted to be omitted where the exterior canopies, roofs, porte-cocheres, balconies, decks, and similar projections are constructed with materials that are noncombustible, limited-combustible, or fire retardant–treated wood as defined in NFPA 703, or where the projections are constructed utilizing a noncombustible frame, limited-combustibles, or fire retardant–treated wood with an inherently flame-resistant fabric overlay as demonstrated by Test Method 2 in accordance with NFPA 701.

ENHANCED CONTENT
Sprinklers can be omitted if the canopy construction assembly is composed entirely of noncombustible, limited-combustible, or fire-retardant materials and the area underneath is essentially restricted to pedestrian use. The reference to noncombustible and limited-combustible construction applies to the entire canopy assembly and not just to the exposed surface. Cases in which the exterior roof or canopy is surfaced with noncombustible, limited-combustible, or fire-retardant-treated materials normally require sprinklers, but sprinklers can be omitted if the requirements of 9.2.3.1 are met.

The roof canopy typically found on strip shopping malls, where the area under the canopy is limited to pedestrians, is an example of this condition where pedestrian traffic is the primary use. Areas where automobiles stop briefly to pick up or drop off passengers are not considered storage areas. Areas located at drive-in bank windows or porte-cocheres at motels and hotels normally do not require spri

Reply
Todd E Wyatt
6/14/2023 08:49:00 am

REFERENCES continued ...
The roof canopy typically found on strip shopping malls, where the area under the canopy is limited to pedestrians, is an example of this condition where pedestrian traffic is the primary use. Areas where automobiles stop briefly to pick up or drop off passengers are not considered storage areas. Areas located at drive-in bank windows or porte-cocheres at motels and hotels normally do not require sprinklers. However, the area under the exterior ceiling shown in Exhibit 9.8 requires sprinkler protection. The space is used primarily for parking vehicles, and the remainder of the building is sprinklered.

9.2.3.2
Sprinklers shall be permitted to be omitted from below the exterior projections of combustible construction, provided the exposed finish material on the exterior projections are noncombustible, limited-combustible, or fire retardant–treated wood as defined in NFPA 703, and the exterior projections contain only sprinklered concealed spaces or any of the following unsprinklered combustible concealed spaces:
(1) Combustible concealed spaces filled entirely with noncombustible insulation
(2) Light or ordinary hazard occupancies where noncombustible or limited-combustible ceilings are directly attached to the bottom of solid wood joists so as to create enclosed joist spaces 160 ft3 (4.5 m3) or less in volume, including space below insulation that is laid directly on top or within the ceiling joists in an otherwise sprinklered attic [see 19.2.3.1.5.2(4)]
(3) Concealed spaces over isolated small exterior projections not exceeding 55 ft2 (5.1 m2) in area

2021 IBC
Chapter 10 Means of Egress

TABLE 1020.2 CORRIDOR FIRE-RESISTANCE RATING
OCCUPANCY : R
REQUIRED FIRE-RESISTANCE RATING (hours)
Without sprinkler system : Not Permitted
With sprinkler system : 0.5c/1d

Section 1021 Egress Balconies
1021.1 General
Balconies used for egress purposes shall conform to the same requirements as corridors for minimum width, required capacity, headroom, dead ends and projections.
1021.2 Wall Separation
Exterior egress balconies shall be separated from the interior of the building by walls and opening protectives as required for corridors.
Exception: Separation is not required where the exterior egress balcony is served by not less than two stairways and a dead-end travel condition does not require travel past an unprotected opening to reach a stairway.
1021.3 Openness
The long side of an egress balcony shall be not less than 50 percent open, and the open area above the guards shall be so distributed as to minimize the accumulation of smoke or toxic gases.
1021.4 Location
Exterior egress balconies shall have a minimum fire separation distance of 10 feet (3048 mm) measured at right angles from the exterior edge of the egress balcony to the following:
Adjacent lot lines.
(1) Other portions of the building.
(2) Other buildings on the same lot unless the adjacent building exterior walls and openings are protected in accordance with Section 705 based on fire separation distance.
(3) For the purposes of this section, other portions of the building shall be treated as separate buildings.

Reply
SCHULMAN
6/14/2023 09:34:45 am

In Europe you might get arrested for suggesting to omit these sprinklers .. Im with Jesse ... EIFS IS COMBUSTIBLE.

Reply
Pete H
6/14/2023 01:26:35 pm

No personal experience, but if it's combustible, you provide sprinkler protection. And it sounds pretty combustible.

Insurers classify EIFS as combustible.

Yeah, it needs sprinklers.

Reply
Alex
6/14/2023 01:45:14 pm

My two favorite research projects back in school were both the Grenfell Tower and the Torch Tower (well.. fire 1 and 2!).

I would highly recommend exterior protection.

Reply
Kevin
6/28/2023 11:14:22 am

A question. Would EIFS system such as Dryvit EPS10 combustible foam with a flame spread rating of 25 or less per ASTM E84 would not require exterior/exposure protection? Regardless if an exterior corridor or just the entire wood frame exterior of 4 story apartment?

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT