MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Why Are Standby Fire Pumps Not Required?

2/2/2021

12 Comments

 
If a fire sprinkler systems is designed for "life safety" purposes, should not a primary and standby fire pump be provided? Why are standby pumps not required to improve reliability for these systems?

​​​​Sent in anonymously for discussion. Discuss This | Submit Your Question | Subscribe
12 Comments
James Phifer
2/2/2021 09:14:28 am

Just my opinion, but I think the Fire Department Connection serves at a secondary supply. The Fire Department will not rely on the pump, and will always hook up to the FDC anyway.

Reply
Matt
2/2/2021 09:15:15 am

NFPA guidance provides a minimum reasonable standard of protection. If the prescribed maintenance is followed, then historically there is a very low failure rate. Many owners do provide a backup pump if they feel that the cost is justified.

There is no way to protect against ALL risk (if 2 pumps are better... why not 3... or an on-site water supply, or 2 on-site supplies...)

If the codes are too cost prohibitive, they wont be followed.

Reply
Brian Gerdwagen FPE
2/2/2021 09:17:48 am

It is a long answer.

Firstly, this is why we evaluate the reliability as well as the capacity of the public water supply when testing it. Sometimes having to add a tank and a pump to deliver the proper water. We add a safety factor that is appropriate for the demand and the supply. For example, if I know that in Ontario, California there is a huge water demand during some months due to growing strawberries, my flow test in June is going to be high compared to February when the strawberries are almost ready. If there is a golf course nearby, a flow test in the late afternoon will be much higher than a flow test in the early morning.

Secondly, most fire sprinkler systems are not Life Safety systems. They are for property protection. Unless it is a residential system, or allowing occupants time to escape (e.g. multistory and hospital), the sprinklers are protecting the building and its contents. Occupants should have left long ago. My rule of thumb has been that if you're using quick response, it may be life safety. If you're using standard response, you're protecting the property for the insurance company. Incidentally, insurance companies love to add extra fire pumps when the value gets high enough. Even redundant pumps and tanks.

Reply
Casey Milhorn
2/2/2021 09:20:26 am

James nailed it. The FDC serves as the "backup". You will see two pumps provided in hi-rise buildings a lot of times, when the height of the building exceeds the pumping capacity of the responding fire department. For example, locally that height is 250'. We are required to provide two fire pumps in parallel when buildings are over 250'. One fire pump is the main, with the other being secondary.

Reply
Casey Milhorn
2/2/2021 09:28:53 am

And to add to that, in almost all scenarios a bypass is installed around the pump that will allow city pressure to be supplied to the system(s). In pretty much all scenarios, other than the higher floors of hi-rises, the city water does provide some benefit. I don't remember the exact stat, but I believe almost all activations of fire sprinkler systems during a fire event involve only 1 to 2 heads. We actually had a small wet system on test overnight one time, with the valve shut off, and 1 head activated at a fire created by construction debris and it extinguished the fire with only test pressure and water.

Reply
CJ Bonczyk
2/2/2021 09:47:49 am

The fire sprinkler system is a critical component in life safety of a building. IBC provides many exceptions to when a building is "fully sprinklered". Reductions in rated separations, reductions in fire hydrant flow demands, increased egress travel distances and increased building heights and areas are allowed due to this capability. These exceptions are allowed with the exception that, the sprinkler system will suppress the fire to a point in which that occupants can safely evacuate the building and the the fire will be controlled until the fire department arrives to fully extinguish it.

The only time a fire pump is needed to supply the flow and pressure demands for the fire suppression systems is when there is an inadequate water supply pressures based on the system demands. If the supply cannot meet the demand, a booster pump is required. Conversely, if the water supply can meet the pressure and flow requirements, a fire pump is not needed.

If the water supply can meet the building system or fire flow demands there is no need to provide additional costs of equipment, infrastructure, power, etc. On top of the initial cost of everything involved with a fire pump and its components are all of the residual costs. Fire pumps and their appurtenances must be maintained and tested regularly which is not done very well in some cases. Why would an owner want to pay large amounts of money for something that that is not required, and have to hire additional maintenance personnel to take care of it as well.

It is not the intent of NFPA to provide additional items within system that could fail or need repair placing the fire suppression systems out of service. That is why NFPA prefers that systems are designed as simple as possible to maintain reliability in the event of a fire.

Lastly remember when a fire department rolls trucks to a scene as the existing fire suppression system is operating to "control/suppress" the fire, they will connect the the local hydrants and to the fire department connection on the building. The FDC will be pressurized by the fire department's pumper truck to boost the sprinkler and or standpipe system until the fire department has fully extinguished the fire. If initial hydraulic calculations prove that the all system demands can be met without the use of a fire pump, then one is not required.

Reply
Jesse
2/2/2021 09:54:12 am

Lots of great answers here. The short answer is that the local fire department is effectively the backup to the stationary fire pump.

Having worn several hats in my fire career from professional firefighter, to loss control, to design engineer, its interesting that "some" very large insurers consider local fire departments as tertiary response, and instead require for a full secondary fire pump to achieve true high-protected risk status.

Reply
Graham link
2/2/2021 10:53:30 am

Jesse raises a good point. In some regions of the world two fire pumps are considered critical especially for high risk environments with significant values at risk to cover impairments.

In many cases the Fire Department will not enter without effective fire control and will adopt defensive firefighting tactics. They cannot be relied upon to fulfill the role of a back up.

Many insurers will not take the risk on a several hundred million dollar plant or more in Europe for example without two fire pumps. I usually see primary electric plus diesel as standby both rated to meet required demands.

Reply
Franck
2/2/2021 11:14:43 am

As indicated by Graham and others, some other countries have other requirements and some insurance companies ask for more (based on insured values, not life safety).
In the UK, for example, you have 3 fire pumps each capable to supply 50% of the demand (i.e. one out of service and you still have 2 x 50 % = 100%)
In France, you have one main fire pump (100%) and a smaller electric pump rated at 250 gpm @ 90 psi with a small dedicated water tank for 30 min supply. This is based on the fact that most fires are controlled with less than 5 sprinklers in operation during less than 30 min.
Many insurance companies require 2 separate fire pumps / tanks, based either on the TIV (Total Insured Values) or MFL/PML (Maximum Foreseeable Loss / Probable Maximum Loss).

FDC as a back up is fine, but only when you have adequate Fire Department with a reasonable response time and enough water to supply the fire trucks, which is not the case everywhere in Europe.

So yes, it would be a good practice to have 2 separate fire pumps for life safety, but could be cost prohibitive for a small office building or small retail center.
NFPA is for minimum requirements, thus one pump, but does not prevent you to install 2 (or more... for nuclear power plants, for example) if you think it makes sense

Reply
Loki
3/2/2021 10:33:16 am

referring nfpa 20; if I install a diesel engine driven fire pump then does it also requires an electric motor driven fire pump as primary?

Reply
Hak
8/30/2021 07:27:30 am

no, you install the fire pump that is most affordable and accessible. i.e an electric fire pump is the most affordable at small sizes but is no longer viable once it reaches above certain kilowatts because it will require medium voltage to run.

calculation of costs is the main factor for the decision to pick between electric of diesel pump.

Reply
Chris
1/28/2022 10:27:20 am

As I read NFPA 20 5.6.2 it is required in very tall building, a building where the fire protection water demand exceeds the pumping capacity of the fire department

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT