Sprinkler Zone Req'd for IT Rooms, Elevators?

2/5/2021

7 Comments

 
We have a project where the Authority Having Jurisdiction (AHJ) is requiring zone control valves and dedicated pipe from the standpipe to any IT rooms and sprinklers in elevator shafts.

As a result, we have three zone controls for each floor: (1) the floor sprinkler system, (2) IT rooms, and (3) any sprinklers in elevator shafts.

Is there a code or standard basis for this requirement, or would it be specific to the AHJ?

We're doing the work either way for this project since the AHJ is requiring it, but I would like to know for future projects. Thanks in advance.

​​​​​​Sent in anonymously for discussion. Discuss This | Submit Your Question | Subscribe
7 Comments
Brian Gerdwagen
2/5/2021 09:16:53 am

There is a standard requirement for a control valve on the sprinkler at the top of the elevator shaft, but no the bottom. Certainly not IT rooms.

Otherwise, it's just an AHJ requirement.

Reply
DS
2/5/2021 09:24:06 am

NFPA 13 2016 EDITION, 8.15.5.1
SIDEWALL SPRAY SPRINKLERS SHALL BE INSTALLED AT THE BOTTOM OF EACH ELEVATOR HOISTWAY NOT MORE THAN 2 FT ABOVE THE FOLLOR OF THE PIT

NFPA 13 2016 EDITION, 22.14.2.3
SPRINKLER SYSTEMS PROTECTING INFORMATION TECHNOOLGY EQUIPMENT AREAS SHALL BE VALVED SEPARATELY FROM OTHER SPRINKLER SYSTEMS.

Reply
Peter
2/5/2021 09:37:01 am

The requirement in chapter 22 comes directly from NFPA 75 "Standard for the Fire Protection of Information Technology Equipment"

NFPA 75 2020, 9.1.3: Sprinkler systems protecting ITE areas shall be valved separately from other sprinkler systems.

This is required, however, almost never (in my experience) enforced.

Kelsey
2/5/2021 11:04:40 am

NFPA 75 that is described in 22.14 references "high risk" ITE areas. If it is not deemed a high risk by the client, we don't add the extra valve - particularly for small closet scenarios.

Glenn Berger
2/5/2021 09:34:43 am

Previous comments addressed the elevator. NFPA 75 provides the requirements for the sprinkler system for Information Technology Equipment Rooms/Spaces (formerly called Data Centers).

Reply
CJ Bonczyk
2/5/2021 09:57:55 am

NFPA 13 Chapter 22 requires that IT/server areas to be zoned separately. This coincides with NFPA 75 9.1.3.4. I have seen instances if it is a single sprinkler, some AHJ's will be a bit lenient and allow the use of a single tampered butterball valve. However verify with the AHJ a means of testing is not required.

NFPA 13 8.15.5 - 8.15.5.7.2 and ASME 17.1 are guidelines and exceptions for your sprinklers in elevator shafts and machine rooms. See note below:

Many UFC/ETL/DOD projects however require variations of this depending on the type of facility and or branch of the government. One reason an AHJ or government agency requires the sprinkler for the elevator shaft or machine room to be zoned is that they can test the interoperability of the system piping with the alarms to ensure reliability during a fire. Be careful of the fact that if you have an elevator that has a control assembly with a Zero-Delay flow switch for the elevator itself, that there is not a control assembly required for the elevator machine room as well if the elevator is hydraulically operated.

If this is not a government/DOD project then the standard adopted local fire codes of that jurisdiction, NFPA, & ASME typically apply.

Reply
James Richardson
2/5/2021 10:24:09 am

Ask the AHJ for the code section that requires it. If he can't cite it, he can't write it or require it.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT