I am building out a space that has been vacant for multiple years. The space has a hydraulic elevator that travels 1 floor. There is a sub that is ushering the elevator contractor through the certificate milestone with all the adjacent trades.
He has proposed to change out the Class III-B hydraulic fluid with a Hydro-Safe or equivalent non-combustible fluid in order to work around the NFPA 13 requirement for a pit sprinkler and pit detection to be installed. My question is, does swapping the petrol-based fluid to a bio-equivalent have any long-term effects on the pump, pistol, seals, gaskets, etc.? Also, how do I make sure this is the fluid that remains in use for the life of the certificate? Sent in anonymously for discussion. Discuss This | Submit Your Question | Subscribe
10 Comments
Jesse
2/9/2021 09:19:23 am
Good question, but I'd have some concerns.
Reply
Michael M
2/9/2021 11:32:06 am
Agree with Jesse.
Reply
Rick Thompson
9/26/2023 07:13:36 am
I'm s firefighter, trying to learn more about elevator oil flash points and other hazards. Went to a call last night where the motor malfunctioned and heated the oil to close to 300 before the circuit tripped. It was smoking but didn't flash. What is the flash points and atomizing hazard you spoke of?
Reply
CJ Bonczyk
2/9/2021 09:54:49 am
Be advised that sprinklers shall be installed at the top and bottom of elevator hoistways where elevators utilize polyurethane-coated steel belts or other similar combustible belt material. Secondly the sprinkler in the pit can only be removed as well if the shaft is noncombustible, fully enclosed, and does not contain combustible fluids. I would proceed as follows.... First go straight to the manufacturer of the oil and obtain the SDS sheets of the exact type of oil being used. More than likely you will find out it is combustible to some degree requiring the need for sprinkler protection. Speak with the elevator installation contractor to provide cutsheet submittals for the equipment being installed for the elevator. The oil will have a specific set of specifications along with the SDS sheets. The elevator equipment submittals should state if the oil is compatible with the equipment or not. If it's compatible then you can always call the manufacturer of the oil and see if they can provide any testing data for the oil. Also, you can verify if swapping of these oils causes a warranty violation for the elevator. You probably won't get much test data on the oil from the elevator manufacturer. However, the elevator manufacturer could provided you with documentation about various service life of the components themselves. As to making sure the fluid remains in use for the life of the certificate....I would guess that would depend on how the protocol is set up for the elevator to be inspected & maintained with record documentation. By speaking with both manufacturers for the oil and elevator you should obtain a decent amount of information about your inquiries. Just my two pennies...
Reply
Franck
2/9/2021 10:28:23 am
You can check, if you have the information for the oil (name, brand...) on FM Global approval guide:
Reply
Brian Gerdwagen FPE
2/9/2021 01:29:19 pm
I always specify the pit sprinkler, regardless of elevator type, because of the potential for the accumulation of debris.
Reply
Thanks for helping me understand that there are non-combustible fluids that will be used to work around a certain requirement. I guess there are certain tools needed to use for different purposes. It would be important to use the right tools, such as the right hoses, to ensure that they will be able to take if there are chemicals that will be transported.
Reply
Jeffrey J Hanlon
10/10/2021 11:43:12 am
Do NOT use the veggie based hydraulic fluid in your elevator. It is a HUGE PITA to deal with in the elevator equipment end. Ruins the valve and makes car run like trash
Reply
Joseph Edward Morrissey
2/17/2022 02:51:23 pm
Veggie oil must be changed on a regular basis (depending on use). Hydraulic elevator oil can heat up to over 120 degrees which will cook the oil, create a problem with the valves, packing and seals.
Reply
Andrew
2/28/2025 07:19:56 am
Does anyone know of any truly noncombustible hydraulic elevator fluids?