Is there a method to use a main drain test to calculate the hydraulic curve at the riser itself?
I haven't done it myself, but using a static pressure at the riser, with a residual pressure at the riser, and then to gather the flow a pitot reading on the main drain discharge to measure how much flow? If the flow discharge outside was greater than the demand of the system, conceivably a hydraulic calculation could be made with the riser as the source point, and with more accuracy than a hydrant flow test somewhere near the site. Obviously if a backflow test header or hose valve were supplied, a higher flow could be obtained with a better curve. I heard this mentioned recently so it's just theory to me, but for small remodels having a setup like this could be far simpler (and potentially more accurate) to know the available water supply at the system. Sent in anonymously for discussion. Discuss This | Submit Your Question | Subscribe
16 Comments
Dan Wilder
2/25/2021 08:54:25 am
While technically accurate to create a "micro" water supply curve (assuming the discharge pipe can be routed into a known orifice & pitot readings are accurate), it does not create an accurate water supply for the building, just a baseline to compare future results to. Gauge placement becomes very important for the static/residual readings (think performing a hydrant static/residual/flow test from a single hydrant....it can be done but the numbers are skewed). Outside hose also is a question.
Reply
OP
2/25/2021 08:57:56 am
Dan - agreed on all points.
Reply
Dan Wilder
2/25/2021 09:28:17 am
I'll take the current static from the system (bleed off the pressure above the check valve or past the backflow so I don't get an artificially high static), then use the residual required flow & pressure. It is super conservative as those numbers are from a demand calc (not an actual supply test) but again, I've only used it for lesser hazard additions as I can prove the new area demand is less than the existing area demand requirements.
Jesse
2/25/2021 09:08:49 am
Agree with Dan's comments about it really just being a benchmark for future comparative analysis. We need to be accurate in our calculations, and that accuracy begins with the flow test we use as the basis of design. I mandate all of our field staff to strictly adhere to NFPA 291 Ch. 4 when obtaining flow values for our design calcs.
Reply
Dennis R.
2/25/2021 10:44:01 am
Agreed! Accuracy is of the utmost importance when performing a flow test. The results form the basis of the whole calculation process!
Reply
Dennis R.
2/25/2021 09:21:16 am
I was interested to see the replies to this comment. I read the old GAPS Guideline on this very thing. Although I can't find it online, I did save a copy to my computer. It makes a lot of sense, but obviously isn't within the intent of NFPA13.
Reply
Matt
2/25/2021 10:20:08 am
Typically I would use the Residual flow and pressure from the base of riser placard, and use the reading of the city pressure gauge for my static pressure. As mentioned before, this is NOT an accurate model of the water supply, but depending on the age of the system (keeping in mind that water supplies can change drastically over time) this can provide reasonable constraints to use when modeling changes/modifications in an existing system.
Reply
jay richardson
2/25/2021 10:48:48 am
Yes you can do this to get a relatively accurate available water supply at the BOR, but you don't know the coefficient of discharge to use for the main drain. I would connect a hose to the main drain pipe and use a hose monster nozzle (known Cd) to determine the flow.
Reply
Franck
2/25/2021 11:13:24 am
I like the conservative approach of Dan to have a rough idea on the possible available water supply on a system.
Reply
Franck
2/25/2021 11:19:03 am
To come back to the initial question, this is not something I would do for a new system.
Reply
Dennis Randolph
2/25/2021 11:32:54 am
Here is the paper I was referring to earlier, if anybody is interested. I couldn't find it online again, so I stuck it in Dropbox.
Reply
Jonathan Sullivan
2/26/2021 09:13:56 am
Thanks Dennis. Why do you think the recommendation is that the gauge must be tapped into the riser rather than the hose?
Reply
Dennis Randolph
2/26/2021 09:40:17 am
I would think it is the same principal as NFPA13 (213 Ed.) A.8.16.2.4 in that you would not record a true residual reading if the gauge is on the drain.
James Richardson
2/26/2021 11:44:47 am
Thanks for that paper.
Reply
James Richardson
2/26/2021 10:49:43 am
I would consider this method to be primarily a starting point used when questioning if the incoming water can meet the numbers on the placard.