Does Deluge System Use Supply or Demand Calc?

2/11/2021

10 Comments

 
This question pertains to hydraulic calculations at the supply and sprinkler sides of a deluge system:

Our example using rough numbers; the deluge system requires 4,000 gpm based on density requirements through the building. This is the system demand.

Now suppose you have a strong water supply. The water supply actually provides 8,000 gpm based on main capacity testing. This is the system supply.

Now my question is, the pipe is wet up to the deluge valve. There is about 50-feet between the deluge valve and the hazard. It is understood that the system demand is 4,000 gpm, but within the pipe network, is it necessary to size the pipe for a deluge system based on 8,000 gpm on the supply side?

Until the water begins discharging through the deluge nozzles, the 8,000 gpm will be surging through the pipe network to reach the nozzles, correct?

​​​​​​Sent in anonymously for discussion. Discuss This | Submit Your Question | Subscribe
10 Comments
Glenn Berger
2/11/2021 09:19:30 am

Pipe sizes are based upon the demand requirements. Some may alter the pipe sizes to allow for greater pressure usage, if available.

Reply
Dan Wilder
2/11/2021 09:23:47 am

Supply capacity of the system is not a consideration (for this specific question, if you are working towards a containment, foam usage result, tank/break tank sizing, or a balancing requirement then a supply calc is needed). A demand calculation provides the minimum required pipe/valve sizes to make the system work. The fact the supply can provide 8000GPM (surging water has to have an outlet) and still keep the adequate pressure is just an additional safety factor to the system.

Think of it this way, assuming a light hazard calc requires 5.6K-7PSI-14.8GPM at the "hydraulically most demanding sprinkler". From that sprinkler using known calculation methods (Hazen-Williams), the riser GPM/PSI can be determined via pipe sizing and lengths based on however many sprinklers are within the calculated area - Lets call it a system demand of 247GPM @ 32PSI. Now, if that one sprinkler every does get activated, it will not see just that 7PSI, it's going to see (for example) 80PSI (50 GPM - thats 1/5 of the system demand already). As additional sprinklers activate, the GPM/PSI equalizes and it is fairly easy to have the demand calc requirements be exceeded by only a few activated sprinklers. If the entire calculated area sees the available water supply, it may actually discharge 431GPM @ 80 PSI (weirdly accurate since I ran a quick test calc..). The demand calc also takes into account a safety margin (PSI or % of PSI depending on AHJ) which the supply calc does not account for.

I'm not sizing valves or worried about velocities (if that is still a thing were you are) based on the 431 GPM running through the system, only the 247 GPM just as I am not sizing the system for the actual supply.

I hope that made sense....?

Reply
Justin Milne
2/11/2021 11:48:36 am

It makes sense, yes, I just know that there Unified Facilities Criteria codes required 10 ft/s for underground lines if you want to use ductile iron pipe. Otherwise you'd have to use PVC for the underground. Therefore, the velocity in the pipe might dictate thrust block requirements for underground depending on velocity and GPM, right?

Reply
CJ Bonczyk
2/11/2021 09:49:22 am

If its open nozzle/sprinkler style your deluge valve and piping network only needs to be sized based on the simultaneous flow of all devices downstream of the valve which as you state is the 4,000 gpm demand/the entire area protected by the deluge system. Hydraulic calculations and sizing of the pipe for system demand will show how much water is being used based off of system demand and what is still available via the supply. You don't need to account for the additional leftover available water unless its a water storage tank design with refill rates or hangar supplying a foam systems.

If you have high pressures in the water supply and are worried about the pressure surges in the deluge system piping then you have a different issue. High pressure surges causing heavy water hammer in deluge systems can be corrected with the use of items such as surge tanks (Amtrol or Young Engineering).

Reply
Justin Milne
2/11/2021 11:52:18 am

At what pressure are is water hammer going to start to be an issue? Only have 70 psi currently and normally don't have issues with water hammer. Pump startup would jump that 70 psi to 184 psi.

Reply
Franck
2/12/2021 02:48:55 am

Just one comment on waterhammer.

Waterhammer is an effect of the pressure rise (surge) that accompanies a sudden change in the velocity of water flowing in a pipe.

Pressure surges may be initiated by:
• The sudden closure of a valve
• The quick increase of pressure inside a given system
• The sudden stopping of a pump
• The sudden development of abnormal water demand when a water main breaks

It happens, for example, upon a pump start (sudden pressure variation in the system) when you have a closed volume that can not really compress to compensate.
So a pipe full of water will have water hammer if you have a sudden high pressure.


Discharge lines from pumps are subjected to waterhammer caused by water column separation. This may occur when a pump suddenly stops (due to power failure, manual shutdown…) or if the discharge valve is closed too quickly with the pump operating. This is one of the main reason for not having ¼ turn valves on fire mains.

The principal factors contributing to water column separation are:
• The rate of flow stoppage, either by rapid closing of a valve or the fast deceleration of a pump
• The length of pipe system (this factor determine the time that pressure continues to fall before positive-pressure waves returning from the far end of the line counteract the initial pressure drop)
• The normal operating pressure at critical points, such as the crest of hills
• The velocity of the water just before pump stoppage or valve closure occurs: the greater the velocity, the larger the size of the void, reverse flow velocity, and the final pressure rise.

Normally, as deluge systems have many open nozzles downstream the deluge valve and the fire pump starts only once the valve has activated, there is limited water hammer effect has the water compression is less a problem (until all pipes are full of water with nozzles discharging, but in that case, because of friction losses to bring the water, the residual pressure in the system is lower than the one out of the fire pump at no flow.

Note that to avoid having water hammer in sprinkler systems, NFPA indicates the following for the start/stop setting of fire pumps (in the annex section of NFPA 20) :
a) Cut-out Jockey Pump : Pressure of the fire pump at churn (= pressure when the pump is running and there is no flow delivered)
b) Cut-in Jockey Pump : Cut-out Pressure of Jockey pump – 10 psi
c) Cut-in Pump #1 : Cut-in Jockey Pump – 10 psi
d) Cut-in Pump #2 : Cut-in Pump #1 – 10 psi
e) Etc.

+ it is also sometimes advisable, if water requirements call for more than one pumping unit to operate, that the units should start at intervals of 5 to 10 seconds.

This sequential starting is absolutely necessary, otherwise in case of a sudden sharp drop in pressure, all the switches would trip at the same time.
Where this rule is not adhered to, pump houses have been destroyed when the surge of tons of water breaks the headers or elbows in the underground piping.

Reply
Franck
2/12/2021 02:58:04 am

Another additional comment to emphasize the excellent explanations by Dan.
The flow requirement from the system and the available flow from the water supply are not the only parameters.
The required pressure and available pressure are also key factors, whether it is a deluge system of a sprinkler system.

If your demand is 4000 gpm (need to be hydraulically calculated to add additional flow from friction losses from one nozzle to another) at 65 psi, and your 8000 gpm water supply can only deliver 4000 gpm @ 45 psi (you can have this value on the flow curve from your water supply - Good guess with Static pressure, residual pressure @ flow and use of a Q1.85 graph for city water supplies)), then you have a problem.
Your 8000 gpm water supply will not be able to deliver 4000 gpm inside your system because of the too low pressure available.
In other words, the friction losses in your system will prevent 4000 gpm to run into your pipes...

And the demand point of a system is not obtained by multiplying the density by the area of coverage (this will give the theoretical minimum flow, not a demand for the system), but by calculating the demand flow AND pressure from all the sprinkler/nozzles operating at the same time. And if you need 7 psi for the most remote nozzle/sprinkler, you may need 8 psi fore the next one... and so on, because of friction losses to bring water from one nozzle to the next one through the piping.

Reply
Wajeeh Abbas link
10/18/2021 01:59:17 am

Hi,

I need to verify the existing fire water system installaed in an upstream oil processing facility for 6000bbl of crude oil storage. I need guidance on which NFPA Standard to follow for the calculation of Fire Water Demand? FYI this is not a sprinkler based system.

Reply
social media management services philippines link
6/15/2022 05:03:29 am

Thank you so much for this article! This was exactly what I needed.

Reply
Jack G
1/7/2026 08:56:13 am

I agree basically with the above, however, when designing to a safety factor of 10 psi, as example, does one drop the water supply by 10 psi , or calculate to 10 psi under the curve. ? Or are they the same.
I ve demand calculated systems, burning up pressure to 10 psi under the curve, and if you supply calc the same area with the higher pressure ( velocities and friction loss increase ) your system ends up deficient .
Which is true! The system has not the ability but to allow the extra 10 psi thru it ultimately making your system deficient.
So I perform a supply calc, to balance the flows ( ultimate goal is to achieve not much overflow but that never happens) and use those sizes in my demand calc. I then tweek my sizes ( slightly) to allow the 10 psi safety. ( mains usually. So that the lines can flow the system demand of the supply calc. And controls the amount of overflow.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Oct '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 88A
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    November 2026
    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT