Sprinkler Criteria for Compact Mobile Shelves?

2/18/2021

8 Comments

 
Having trouble getting a good feel for fire sprinkler design criteria for compact, mobile storage shelves. These contain Class I-IV commodities. As I understand it, NFPA 13 only covers light hazard for compact shelving.

The metal shelves have a height of 8-feet, the ceiling height is 26-feet. The room is 3,000 sqft, and the shelves have a footprint within that space of 21 x 30 feet. Any help is appreciated. 

​​​​​​​​Sent in anonymously for discussion. Discuss This | Submit Your Question | Subscribe
8 Comments
Dan Wilder
2/18/2021 08:32:55 am

Depending on what your current adopted standard is...

13-16' Table 13.2.1 if the storage is less than 10' (unlimited ceiling height) design criteria is only OH2 (.2/1500) is one approach (but not specific to "compact mobile" storage)

I do see Section 20.6 and that allows light hazard protection schemes specific to the conditions in that section. You could go with the OH2 approach as an alternate option with approval from your AHJ.

If your situation does not fall into those two categories, the design falls outside of 13 and will require a FPE provide options/review. Possibly utilize FM standards for moveable racks (they don't have anything specific to this last I checked)

You can request the download the archived NFPA report from 2008 or google "Compact Mobile Shelving System Fire Testing Project Final Report" to read. Summary was that fires were contained, but only to the extent of the metal encasements but the fire continued to burn within the array so not considered suppressed which is understandable with how these are built.

https://www.nfpa.org/News-and-Research/Data-research-and-tools/Suppression/Archived-reports---Suppression

Reply
Brian Gerdwagen FPE
2/18/2021 09:10:17 am

I'm getting hung-up on the "mobile" part. Do you mean this type of shelving?

https://info.kardex-remstar.com/us/vertical-carousel-module

FMDS 8-34. Protection criteria for automated storage and retrieval systems.

Reply
Dan Wilder
2/18/2021 09:29:02 am

More this setup is what I'm thinking...

https://bradfordsystems.com/high-density-mobile-storage/

Reply
Franck
2/18/2021 11:04:40 am

As indicated by Dan, by considering this as an OH Gr 2 based on NFPA 13 13.2.1 (!4.3.1.7.1 in 2019 Edition ), you are fine with cl IV and all classes of storage, from pile to shelves, from single to multiple row racks.
Your configuration is less than the worst in the list because the metallic shelves will prevent the fire from spreading from one row to another, eventhough, if no manual firefighting is implemented, you may burn everythin within one row.
Note that §20.5.2 (NFPA 19) define movable racks as multiple row racks for sprinkler protection.

Reply
Franck
2/18/2021 11:20:41 am

Otherwise, you are right, if you consider the same storage arrangement with a class III commodity, this is covered under §20.6 in NFPA 13 2016 (21.12 in NFPA 2019) and is considered as a Light hazard occupancy.
It is indicated in the annex that other storage (class IV or plastic, for example) are out of the scope of NFPA 13 and not covered by the standard. A case by case approach is then to be made and the one proposed by Dan seems the most resonable one in that case.
In NFPA handbook, it is indicated that if the same storage of class III products were stored in fixed racks (library stacks) then the required density would be OH Gr 2.
In other words, the movable rack storage arrangement is less problematic than fixed record storage racks or library stacks.

Reply
Jesse
2/18/2021 11:37:09 am

A Class-IV Commodity stored to 8-ft is protected as OH-2 in any arrangement

Reply
Arnold Wilkins
2/18/2021 12:50:15 pm

The compact storage shelving I have been seeing lately is similar to this link.

https://www.youtube.com/watch?v=cbs_7jhcEa4

Here is my thought process. Please let me know if I am missing something. The following is from 2016 ed. of NFPA 13.
Section 13.1.1(5) - Storage Class I-IV.... as directed by 14.2.3.1 and 16.2.1.2.

Section 14.2.3.1 does not cover multiple-row racks.
Section 16.2.1.2 kicks you back to 13.2.1.

Section 16.2.1.2.3 is for 12 ft or less that does NOT meet definition of Miscellaneous storage. States it shall be protected with in-rack sprinklers.

If in-racks are the only option then maybe look at something like a Metraflex seismic joint.







Reply
Todd M Delisle
7/14/2021 10:59:10 am

I'm interested in opinions/guidance for Horizontal Carousels and the potential hazard or overloading existing protection systems.

These units when placed side by side (and) on top of one another do exactly what they say they will do - increase the density of storage in any given area. To date I have not been able to locate a clear path to protection requirements proposed by NFPA 13, though I have found FM Data Sheet 8-33 CAROUSEL STORAGE AND RETRIEVAL SYSTEMS.

Does anyone have experience with these types of systems?
https://info.kardex-remstar.com/us/horizontal-carousels?utm_source=adwords&utm_medium=ppc&utm_term=kardex%20horizontal%20carousel&utm_campaign=3V%20-%20Brand%20-%20Product%20Terms%20-%20Desktop&hsa_cam=8868506348&hsa_mt=p&hsa_ver=3&hsa_src=g&hsa_ad=496148272236&hsa_net=adwords&hsa_tgt=kwd-1065690396908&hsa_acc=2692017079&hsa_grp=121772849024&hsa_kw=kardex%20horizontal%20carousel&gclid=EAIaIQobChMIg4GelOTi8QIVEmyGCh20QQ-8EAAYASAAEgJyofD_BwE

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT