Does Remote Ansul System Need Monitoring?

11/14/2022

7 Comments

 
We have a stand alone open-air pool pavilion with no attached building.

There is a gas grill under the roof with a very elaborate hood/exhaust/Ansul system. There is no fire alarm system in this pool pavilion.

The Fire Inspector wants the Ansul system monitored by the clubhouse fire alarm system that is 100-ft away.

Is he correct by code?

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Glenn Berger
11/14/2022 08:13:10 am

You have a very unique case with a fire system provided for an outdoor exhaust system.

NFPA 17A does not have a provisions to required connection to fire alarm system.

If the pavilion is connected to the building, then I would say it would be required. If the pavillion is somewhat separated from the building then you may be able to omit it.

Reply
Jesse
11/14/2022 08:17:56 am

I agree with Glenn - this is a very unique situation. I think you can make the case to omit connection to the FA system, but as always it comes down to local AHJ requirements. Did the inspector provide a code reference?

Reply
Derek Crumley
11/15/2022 07:43:27 am

The inspector did not reference a code. After further conversation with AHJ they deem the pavilion to be attached to the clubhouse building because it is encompassed with in the pool fence that is attached to the clubhouse and wraps around pool and pool pavilion structure.

Thanks for everyone's reply very informational by all.

Reply
Alex
11/14/2022 08:18:36 am

Hi,

There was a previous discussion on this topic as well a while back. Looks like you had posted your question here originally but wanted to bring light to the previous feed:

In addition, NFPA 96 10.6.2 states "where a fire alarm signaling system is serving the occupancy where the extinguishing system is located, the activation of the automatic fire-extinguishing system shall activate the fire alarm signaling system."

Since you note that there is no fire alarm system serving the location of the gas grill, I do not believe it is required by code. Although, always smart to have them monitored!

Thanks,
Alex

Reply
Todd Wyatt
11/14/2022 08:36:50 am

The adopted Fire Code (e.g. 2021 IBC) is the scoping document as to WHERE an “alternative” automatic fire-extinguishing system is permitted or required. The referenced standard (e.g. NFPA 96 Standard for Ventilation Control and Fire Protection of Commercial Cooking Operations) identifies HOW the an “alternative” automatic fire-extinguishing system is to be designed, installed, inspected, and maintained.

The open-air pool pavilion would be classified as a Group U Utility and Miscellaneous Occupancy Classification (OC). Per 2021 IBC Ch 9 Fire Protection and Life Safety Systems, a Group U building does NOT require an automatic sprinkler system (ASPS) to be installed in the commercial kitchen exhaust hood and duct system per 903.2.11.5. “Domestic cooking facilities” require a hood with an automatic fire-extinguishing system for OCs including Groups I-1, I-2 and R-2 college dormitories but NOT for Group U buildings/structures.

Regardless if the hood and associated automatic fire-extinguishing system is required or not, its design & installation shall meet the scoping Code (e.g. 2021 IBC) and the associated referenced standard (e.g. 2021 NFPA 96 Standard for Ventilation Control and Fire Protection of Commercial Cooking Operations).

NFPA 96 states the following :

Chapter 10 — Fire-Extinguishing Equipment for Cooking Operations in Buildings
10.6 System Annunciation.
10.6.2
Where a fire alarm signaling system is serving the occupancy where the extinguishing system is located, the actuation of the automatic fire-extinguishing system shall actuate the fire alarm signaling system in accordance with the requirements of NFPA 72.

ENHANCED CONTENT
When the fire alarm signal is activated, all people in the building should respond according to the fire emergency plan developed by the owner or tenant. Most people will evacuate using the nearest exit, while others might be assigned other duties such as actuating the fire-extinguishing system or using portable fire extinguishers if it is safe to do so. To improve correlation between NFPA 17A, Standard for Wet Chemical Extinguishing Systems, and NFPA 96, the requirements in Section 10.7, which addressed system supervision requirements and are more appropriate in an installation standard, were moved to NFPA 17A.

One could argue that since the Group U pavilion is NOT being served by a fire alarm signaling system, the activation of the automatic fire-extinguishing system in the hood would NOT be required to actuate the fire alarm signaling system in the building.

Reply
Wes
11/15/2022 07:49:11 am

Just as a fallback, Potter just came out with a new wireless supervisory switch. If you had to connect it back to the main fire alarm system, at least you wouldn't have to dig and bury conduit to do so:
https://www.pottersignal.com/fire-sprinkler/supervisory-switches/signalink-bridge

(note: I don't represent Potter, just thought it interesting)

Reply
Frank J. Herrick
11/16/2022 11:24:29 am

In that situation I'd be happy with a 10" exterior bell and rated outdoor strobe.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT