Any Experience with Oxygen-Reduction Systems?

1/23/2024

18 Comments

 
I had a client ask about Oxygen-Reduced Systems (ORS), aka Hypoxic air technology (displacing ambient oxygen in an enclosed environment such as in warehouses). I did a quick read with what's available on Wiki, FM and NFPA. But even my go-to suppression people have hardly encountered these. Testing has been very specific.

Just to increase my knowledge, does anyone here have an practical experience in these?

Are these systems really being installed?

Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
18 Comments
Sean
1/23/2024 08:08:39 am

I would recommend drawing in a vendor like Wagner (there may be others). They have started creating a presence here in the US and we are aware of several projects that have deployed ORS systems in warehouses.

WAGNER Fire Safety, Inc.
1670 Barclay Blvd,
Buffalo Grove,
Chicago, IL 60089
United States of America
Phone +1. 847. 243-4034
[email protected]

Reply
Glenn Berger
1/23/2024 08:12:03 am

My experience has been vendors telling me that these systems are being installed all over the place without proof.

Recommend avoiding these systems in all occupied spaces and any limited occupiable spaces.

Reply
Eddie
1/23/2024 08:26:15 am

How does one escape from the center of a warehouse if this system is activated?
NFPA has an article from 2018. The executive summary is interesting. Review of Oxygen Reduction Systems for Warehouse Storage Applications
By Patrick van Hees, and John Barton, Lund University; Martin Nilsson, Zurich Insurance plc; and Brian Meacham, Meacham Associates

Reply
Franck
1/23/2024 11:28:37 am

Eddie

The issue is not "when the system is activated" as this system is activated all the time !
The aim of this protection is to keep at all time the atmosphere of O2 below 16% to limit the possibility of a fire to occur.

I know, this seems crazy...

And it does not work for some fires such as the one generated by thermal runaway (lithium-ion batteries) or metal fire (to prevent/extinguish metal fires you need inerted atmosphere, generally of argon or helium).

Franck
1/23/2024 11:30:58 am

Fully agree.

I would even say... "Recommend avoiding these systems".

Reply
Greg
1/23/2024 08:50:56 am

I did review the oxygen reduced environment as a consideration within an AutoStore system. I'll put a link below as to what an AutoStore system is. My thought as to where an oxygen reduced environment could be considered was in a location that is not normally habitable. No one would normally be inside of the robotic type of storage systems. However, there a numerous safety tradeoffs that must be considered with a hypoxic technology system.

I felt that even though the reduced oxygen systems seem to advertise safety, the operational % O2 is on the fringe of impairment, and may have more debilitating effects on some than others. Reference NIH article, below.

As such, the addition of an engineered protective system for fire suppression considerations would require administrative controls and PPE ensure worker safety. It's somewhat of a difficult climb to balance both to a net positive, holistically. With any new technology, independent testing may improve hard data regarding these questions and be more emphatically positive around occupational safety. However, I didn't find conclusive evidence to this point and felt that these are early days for hypoxic technology to be introduce occupiable spaces, especially large spaces such as warehouses.

My recommendation as an alternative consideration would include (what I like to say as)...belt & suspenders thinking. If you're concerned about fire, be very very early in detection with air-sampling. Improve loss control with 2 hour fire wall separations that are above code minimum. Use fire wall enclosure with consideration for aerosolized systems as a supplemental fire suppression system tactic, and in addition to your sprinkler installation. Follow the guidance of FM Data Sheets for conservative sprinkler design and densities. If possible, change packaging to non-combustible or try to incorporate fire retardant packaging on the exterior of the product. Improve separation of stored products, or other segregation tactics.

My conclusion. It's very early days for hypoxic air technology and the capacity for systems to demonstrate remarkable fire suppression capabilities in all conditions. Not all occupational safety considerations appear to be fully investigated.

In the history of oxygen displacing fire suppression systems, the Idaho National Lab CO2 accident was the most influential in providing evidence that oxygen displacement must have engineering rigor to ensure physical lockout is available, and administrative controls to communicate the inherent hazard of oxygen deprivation. In the INL event, spurious equipment performance was a part of root cause, and these learnings should be considered as a real possibility within similar technologies where the breathable environment could be negatively impacted. Equipment can fail badly, and/or incorrectly provide false or misleading information that people believe to be true. Link to the INL event below.

AutoStore System Example
https://www.fortna.com/autostore/?_vsrefdom=ppcgoogle&msclkid=7e9d2db8e5171dbff9b3481728ae108b&utm_source=bing&utm_medium=cpc&utm_campaign=Autostore%20-%20GTP&utm_term=%2BAutostore%20%2BSystem&utm_content=Autostore%20Systems

Article, NIH Respiratory Protection for Oxygen Deficient Atmospheres
https://www.ncbi.nlm.nih.gov/pmc/articles/PMC7183576/

INL CO2 Accident Investigation
https://www.energy.gov/ehss/articles/type-accident-investigation-july-28-1998-fatality-and-multiple-injuries-resulting

Reply
Greg M
2/3/2026 06:46:02 pm

Btw - the CO2 accident was a release of huge quantities of CO2 suddenly - that's nothing like the Wagner etc. reduced O2 systems on the market. Those involve small controlled releases of nitrogen to keep the O2 level down CONSTANTLY in the space. There's sensors to monitor O2 levels and in case of failure the system shuts down and stops supplying N2 and the O2 levels slowly increase. The engineers who design these things clever - and the design is such that it is totally impossible to release enough N2 at once to flood the space and suffocate the workers.

Reply
Jesse
1/23/2024 09:05:02 am

Like Glenn, I've been told they're being installed "all over the place", but have yet to actually see any evidence of it.

Reply
Franck
1/23/2024 11:15:32 am

I yhave seen one of these systems in Sweden, in an electrical room (switchgear).
Theu have apparently been installed in Germany at some locations (including warehouses).
But the installations are hopefully very limited.
I don't like these systems for many reasons.

I will first speak about Health issues.

First, you have to consider the health effect of having a reduced level of oxygen.
Contractors say that this is similar as being in the mountains at very high altitude. This is not true. If the number of molecules of oxygen is reduced on a given volume at high altitude, the O2 concentration is still 20.9%...

OSHA (Occupational Safety & Health Administration) states in Paragraph (d)(2)(iii) of the Respiratory Protection Standard that any atmosphere with an oxygen level below 19.5 percent to be oxygen-deficient and immediately dangerous to life or health.
To ensure that employees have a reliable source of air with an oxygen content of at least 19.5 percent, paragraphs (d)(2)(i)(A) and (d)(2)(i)(B) of the Respiratory Protection Standard require employers working under oxygen-deficient conditions to provide their employees with a self-contained breathing apparatus or a combination full-face piece pressure-demand supplied-air respirator with auxiliary self-contained air supply.
In the preamble to the final Respiratory Protection Standard, OSHA discussed extensively its rationale for requiring that employees breathe air consisting of at least 19.5 percent oxygen.

People at greatest risk would be older employees and those with health conditions such as pulmonary disease, cardiovascular disease, or anemia.
Also, employees with lung disease and exertional demands greater than the resting level might experience greater hypoxemia.
In addition to potential adverse health effects, hypoxemia might also affect neuropsychiatric function, resulting in safety issues such as increased risk for injuries.

When I entered the room with low level of oxygen (it was around 16%), I had to sign a document saying that I have no lung or heart disease (do I really know) and that I have not smoke any cigarette over the last 24 h (would the people working in warehouse do that every day ?).

• At concentrations of 16 to 19.5 percent, workers engaged in any form of exertion can rapidly become symptomatic as their tissues fail to obtain the oxygen necessary to function properly. Increased breathing rates, accelerated heartbeat, and impaired thinking or coordination occur more quickly in an oxygen-deficient environment. Even a momentary loss of coordination may be devastating to a worker if it occurs while the worker is performing a potentially dangerous activity, such as climbing a ladder.
• Concentrations of 12 to 16 percent oxygen cause tachypnea (increased breathing rates), tachycardia (accelerated heartbeat), and impaired attention, thinking, and coordination, even in people who are resting.
• At oxygen levels of 10 to 14 percent, faulty judgment, intermittent respiration, and exhaustion can be expected even with minimal exertion.



Reply
Greg
1/24/2024 07:39:54 am

Franck provides very practical and first hand experience about concerns with oxygen deficiency and elevation (higher altitudes). The NIH article cited above in Greg's comment speaks to that in some depth and provides for a calculation - styled consideration. While the article was written from the perspective of wearing respirators, the physiological response to oxygen deprivation is the key - takeaway.

As Franck is describing, people can have different reactions based on physiological response. The NIH article describes people responding to oxygen deficiency (in the concentrations of ORS systems) to become euphoric and actually want to remain in that condition. Basically, it creates a feeling of being high and works against the normal response of evacuation.

Reply
Greg M
2/3/2026 06:38:27 pm

I feel compelled to respond here, as there is a common misunderstanding being shared here as a reason these systems are dangerous, when it is in fact the opposite!

Franckk you are 100% correct that the percent oxygen at altitude is 20.95%, the same as at sea level. However, percent oxygen does not actually matter for that exact reason! It is the partial pressure of oxygen that matters (=how much oxygen is available to be "pushed" into your arteries within the lungs and carried around the body). The partial pressure of oxygen is the barometric pressure * 20.95%. Now you can see why the amount of oxygen available to the body decreases with altitude (the barometric pressure decreases at altitude)

In an airplane or in the mountains the percent of oxygen is still 20.95%, but there's less of that 20.95% that's there that can get into the arteries based on that decreasing partial pressure. Otherwise, you would have no trouble breathing at the top of Everest.

You can establish the equivalent % oxygen at sea level. In an airplane or in the mountains the amount of oxygen available to the body is equivalent to 15-16% at sea level!

The 19.5% argument is pervasive, but relies really on heavy safety factors in occ. health and safety that were intended to be applied to uncontrolled atmospheres in confined spaces.

Europe has had these systems in place for 20 years with zero issues. And England and Australia also permit their use. We are the luddites in America.

Reply
Franck
1/23/2024 11:24:39 am

Now I will speak about the technical issues.

The main components of an oxygen reduction system are:
• Nitrogen generation system (to continuously generate nitrogen in order to keep the oxygen level under a certain %)
Note that automatic sprinkler protection should be provided for the gas generation room designed for the combustible load in the room.
• Electronic control device and alarms
• Oxygen sensors (within the room that is “protected” by the system, as well as in the gas generator room).
In the gas generator room, oxygen sensors should be provided and set to alarm if oxygen levels drop below 19.5% or increase above 23.5%.
These values are meant to define an environment that can be accessed by a person without any special considerations or equipment.

Nitrogen is produced as required and stored temporarily, if necessary.
This may involve central nitrogen supply facilities. The storage quantities may be either liquid or gaseous.

This means that you have a chemical plant to produce nitrogen close to your plant if the volume is not very limited.
Maintenance of such systems is not easy and any deficiency can lead to a too low level of oxygen that could be a threat to people working in such an environment.
Not to mention the cost on the long term operation (as you will be producing nitrogen all the time !).
Better to install a sprinkler protection system.

Note also that a fire can still occur, under some circumstances. • Reduced oxygen environment results in higher production rates of soot and smoke, which is also not a desirable thing...

I would normally suggest such systems only for limited volumes and areas where nobody is supposed to work inside. It would be more a "controled atmosphere" such as filled with nitrogen, than an oxyden reduction atmosphere.

FM Global data sheet 4.13 (Oxygen Reduction Systems) provides some guodance and should be strictly followed dor such installations.

But my best advice: chose an alternative protection system (sprinklers, total flooding gas protection system for a small volume...) !

Reply
Mark Harris
1/23/2024 01:17:22 pm

My understanding Wagner did a system in an automated warehouse in the Northwest a couple years ago. Probably have done more in the states since that. As I recall intent is forr automated storage not for normally occupied. Support areas (docks, offices, etc. would need different protection - sprinklers). The suppression design of taking oxygen below 15 percent would be similar to suppression with clean agent inert gas system. For inert clean agent systems NFPA 2001 states exposure should be limited to 5 minutes for up to 43% design - 12% oxygen and 3 minutes for up to 52% design - 10% oxygen.
Wagner did some presentations to SFPE Chapters a couple years ago. Can't remember what was said about redundancy or what if nitrogen supply had issues.

Reply
Anonymous
1/23/2024 06:12:58 pm

As the person who posted the question, I thank you all for your insightful and informative comments!

Reply
Pete
1/24/2024 06:14:16 am

My feeling is that there are a lot of technologies that will put the fire out. As an engineer/design pro, we kind of need to do our best to "do no harm " to people, except our mandate takes the form, "hold paramount the safety and welfare..." My mind jumps to the case studies of mishaps, and I try to consider them in the context that nobody set out to intentionally, say, level a school and kill 100 kids. When I have the need to think outside the box to protect some commodity, only as a last resort do I consider CO2 flooding, Halon 1301, high expansion foam, or any other method that could potentially kill someone in the process of protecting the property. Can it be safe? Sure. But, I would only consider after exhausting every other option, and not without a detailed risk analysis and system reliabilty calculation. I'd also consider ongoing maintenance cost and depreciation before choosing a hypoxic system.

Reply
James Art, FPE
1/24/2024 01:16:18 pm

The reduced O2 can be all the time.
Some whole warehouses for fruit or vegetable storage have reduced O2, to preserve the fruit longer.

They can have Sally Ports, 2 doors, and try to limit the number of times they enter. Fork lift drivers may use SCUBA gear.

But then they want to avoid sprinklers, the argument being fire is less likely!

Reply
Vijai Kumar
12/12/2024 03:19:05 am

This is a great topic being discussed here. I have been working at HBW for the past 8 years and we use the OXY reduct system supplied by Wagner. However, this system is not suitable for non-automated warehouses or enclosed spaces where staff are present inside, as it reduces oxygen levels up to 13-14%, compared to the normal level of around 21% inside the atmosphere. While the lower oxygen levels help prevent product damage from fire accident but same time maintaining the nitrogen level at approximately 85% incurs ongoing costs to the company. According to FM Global data sheet 4.13 (Oxygen Reduction Systems), there are protocol to work inside not more than 1.5 to 2 hours continuously and staff must be out side for 30 to 45 minutes in fresh atmosphere to re start his work again and this has been verified through specific medical tests (G28) for employees on regular basis.

Reply
Greg M
2/3/2026 06:40:18 pm

Precisely - it's very safe if the time spent inside is controlled.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT