MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Kitchen Hood Required to Activate Fire Alarm?

10/26/2021

9 Comments

 
NFPA 101 has commentary that states that kitchen hood suppression systems are not required to activate public mode alarm for fire alarm systems.

Our Authority Having Jurisdiction stated that since the kitchen hood systems are provided in lieu of required sprinkler systems, then they are required to activate public mode alarm.

What is the generally accepted practice for kitchen hood suppression monitoring?

​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Glenn Berger
10/26/2021 08:08:11 am

It depends on the application. Large kitchens with large seating areas with the kitchen NOT OPENED to the diners, I typically do not activate the notification appliances. Kitchen Hoods in other applications, I have activated the notification appliances. Always activate the transmission circuit to notify the responding fire department.

Reply
Mark
10/26/2021 08:13:59 am

Section 5.2.1.9 of NFPA 17A - Standard for Wet Chemical Extinguishing Systems, 2017 Edition requires that if a fire alarm is provided in the building, activation of the kitchen hood suppression system shall activate the fire alarm system.

5.2.1.9 The extinguishing system shall be connected to the
fire alarm system, if provided, in accordance with the requirements
of NFPA 72 so that the actuation of the extinguishing
system will sound the fire alarm.

Reply
Fred WALKER
10/26/2021 08:55:01 am

101 allows either connection or no connection for life safety purposes.
72 allows either connection for alarm systems.
17A requires connection if alarm system is present.
None of these address substitution of hood system for sprinkler system which if approved by AHJ would simply make it condition of the substitution approval.
In our case we are both the owner and the AHJ and we do normally require connection of a hood system to the alarm system.

Reply
Robert Bambino
10/26/2021 10:18:55 am

The IFC requires that alternative extinguishing systems installed where there is a fire alarm system are required to activate the fire alarm system. And why wouldn't you want that? Regardless is the kitchen is open to seating or not, if there is a fire (thus activating the suppression system) get people out of the building, which is the most important thing.

Reply
Alex
10/26/2021 12:17:16 pm

Agreed. Our industry strives for life safety, therefore the most important thing is to evacuate the building. I can see if the system is prone to false alarms but a complete hood activation in my opinion calls for a building evaluation.

Reply
PETE D
10/26/2021 06:38:56 pm

Plus, if the hood drops on the cook's line in the middle of dinner service, it's not like they're going to get their beef Wellington 20 minutes later. Typically the equipment will have the gas shut off and get wheeled outside for cleaning / decontamination then reinstalled. Add to that recharge the wet chem cylinder and replace the activation elements. Close the restaurant and apologize to the guests.

Chad
10/26/2021 11:54:37 am

If there is no FA we require a local horn/strobe on the exterior of the building. They usually just use a120V version so it’s simple to power off the hood branch circuit.

The thought is two fold:

1-if it goes off when no one is there, hopefully someone will hear it and call (this has happened, fire from food left on stove with burners on, system tripped randomly, this also lets us notify Health dept, they need to be aware of any discharge)

2- same thing if occupied, if it goes off and they don’t bother to call us, (Happens) someone will hear/see it and call 911(happens, makes us aware of fires they don’t want us to know about)

Reply
Jason Lupa, PE
12/3/2021 09:37:01 am

The IBC provides requirements WHEN to install life safety equipment. IBC [2015 & 2018] requires automatic fire suppression system to be connected to the building’s fire alarm system.

IBC 904.3.5 Monitoring
Where a building fire alarm system is installed, automatic fire-extinguishing systems shall be monitored by the building fire alarm system in accordance with NFPA 72.

This section only requires monitoring; it doesn't say if it should be by supervisory signal or alarm signal.

NFPA 72 provides guidance for HOW to install the IBC’s referenced life safety equipment. NFPA 72 [2013 & 2016] requires operation of any fire extinguishing or suppression system to initiate an alarm.

NFPA 72 17.13 Detection of Operation of Other Automatic Extinguishing Systems.

The operation of fire extinguishing systems or suppression systems shall initiate an alarm signal by alarm-initiating devices installed in accordance with their individual listings.

Typically, if a kitchen hood fire suppression system is installed in a building that is also served by a fire alarm system, the two systems are connected so that any activation of your fire suppression system will also trigger a fire alarm. In rare situations the owner/engineer has asked for (and received) permission to treat the hood discharge as a supervisory signal rather than an alarm signal.

Reply
Derek Crumley
11/1/2022 11:32:03 am

I have less complex question that relates. We have a stand alone open air pool pavilion with no attached building. There is a gas grill under the roof with a very elaborate hood/exhaust/Ansul system. There is no fire alarm system in this pool pavilion. Fire inspector wants the Ansul system monitored by the clubhouse fire alarm system that is 100' away. Is he correct?

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Oct '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 88A
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    November 2026
    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT