MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

How to Calc "In-Use" System That Spans MAQs?

2/2/2023

12 Comments

 
We have a situation where we'll have a piece of equipment in one control area that has a closed-use pipe arrangement with oxidizing gases that goes through different control areas. I've gotten conflicting feedback on this.

How do you figure the amount of "in-use" for each control area? 

Here's a sketch of the concept:
Picture
The equipment that is using the oxygen is on the fourth floor Control Area 2. The tanks that feed it are (2) 200 CF oxygen tanks that are in the second floor Control Area 1.

Which of the following two scenarios is the proper way to tally up the "in-use" quantity for the fourth floor Control Area 2 when comparing against the Maximum Allowable Quantities (MAQs)?

  • Concept #1: The "in-use" amount is only the gas within the equipment itself, and only the gas within the piping to the extent of the control area wall.
  • Concept #2: The "in-use" amount is all of the gas within the equipment itself, and all of the gas within all of the piping, and all of the gas within the (2) oxygen tanks which are actively hooked up to it.
 
My initial gut reaction was that the second option is correct, but now I’m not sure. My reasoning being that if there is an event in 4th floor control area 2 that causes a leak or something like that, it’s not going to just leak out what is physically within the control area… it’s going to leak out everything in all of the piping, all of the equipment, and all of the hooked up tanks. This is all presuming there are no safety devices to stop this from happening.

Assuming my initial gut reaction was correct, is there a way to limit the amount so that it stops at the control area wall?

As in: is there a safety device such as an automatic shutoff valve we can put at the wall such that in the event of a leak or other event, the automatic valve will shut off and then we only have to count the amount of gas between the equipment and the shutoff valve?

I’ve looked in the IBC and its commentary for more info, but couldn’t find anything helpful. I’ve also reached out to a number of different people and there seems to be a variety of different opinions on it.

Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
12 Comments
Chad
2/2/2023 08:22:02 am

#2

In use is not in storage.

If its connected to utilization equipment, it is in use.

Reply
chad
2/2/2023 08:24:52 am

IMO, this applies and that fits in use.

2016 NFPA 400


3.3.86* Use. To place a material, including solids, liquids,
and gases, into action.

3.3.86.1* Closed System Use. Use of a solid or liquid hazardous material in a closed vessel or system that remains closed during normal operations where vapors emitted by the
product are not liberated outside of the vessel or system
and the product is not exposed to the atmosphere during
normal operations and all uses of compressed gases.
3.3.86.2* Open System Use. Use of a solid or liquid hazardous
material in a vessel or system that is continuously open
to the atmosphere during normal operations and where
vapors are liberated or the product is exposed to the atmosphere during normal operations.

Reply
Mike
2/2/2023 01:04:47 pm

This will only apply if NFPA 400 is the charging document within the project jurisdiction. In jurisdictions that use IBC, NFPA 400 is not a referenced standard and is therefore not enforceable. IFC does reference NFPA 400, but not for defining in-use systems. It does reference it for quantities of oxidizing liquids and solids, but not gases.

In a case where IBC/IFC is the charging document, we would need to turn to those documents for the definitions of various in-use systems (both open and closed use), as well as the MAQ of these types of oxidizing gases.

Mike
2/2/2023 01:00:46 pm

According to IBC/IFC, though... in-use DOES count towards storage. Sub-Note B applies:

"The aggregate quantity in use and storage shall not exceed the quantity specified for storage."

Also, the commentary for Closed in-use piping systems note that all equipment within the continuous system is to be accounted for, including the equipment, the piping, and the storage vessels. Typically, all of the above is included within a single control area, so it's easy to figure out... but in this case it traverses multiple control areas. So which control area to apply it to?

The most conservative approach would be that the full quantity of the in-use system applies to each/every control area that the system passes through.

The least conservative approach would be that each control area only needs to consider the piping/equipment/vessels which are physically contained within that control area.

Reply
Mike
2/2/2023 01:10:10 pm

Apologies, I just re-read your original comment and see that you are saying the same thing: the whole thing is considered in-use.. everything hooked up to the system is in-use.

I agree. Sorry for the confusion.

Glenn Berger
2/2/2023 09:01:35 am

This question would be best answered by someone specializing in health care / hospital design.

I would add that y0our situation all the O2 would be considered in-use. Depending on the equipment would determine the it would be open or closed-use.

Reply
Mike
2/2/2023 12:45:47 pm

Glenn,
It's important to note that the ICC characterizes all gas usage as "closed", since it is not possible to have an open-use gas arrangement as it would dissipate into the air.

I agree that all O2 would be considered in-use... but which control area does it apply to? You could make the same argument for literally any control area that it passes through: if there is a leak, all of the O2 is going to come out at the point of the leak, not just what is bounded by the control area walls.

Reply
Todd E Wyatt
2/2/2023 09:02:23 am

Oxygen is a “Class 2 Oxidizer.”

Per 2021 IBC Table 307.1(1), in a gas form, the MAQ for Oxidizers for Storage and for Use-Closed Systems is “NA”.
In a liquid state, an “Oxidizer Class 2” is limited to MAQ of 250 lbs for Storage and for Use-Closed Systems. If the building is sprinklered, MAQs are increased by 100%.
Per 2021 IBC Table 414.2.5(1), “oxidizers” are limited to MAQs according to their “Class” ... 1, 2, 3, or 4 ... in Group M and S occupancies.

2021 IFC Chapter 63 Oxidizers, Oxidizing Gases and Oxidizing Cryogenic Fluids includes the following “shutoff” requirements :

Section 6303 General Requirements
6303.1 Quantities Not Exceeding the Maximum Allowable Quantity Per Control Area
The storage and use of oxidizing materials in amounts not exceeding the maximum allowable quantity per control area indicated in Section 5003.1 shall be in accordance with Sections 5001, 5003, 6301 and 6303. Oxidizing gases shall also comply with Chapter 53.
6303.1.1 Special Limitations for Indoor Storage and Use by Occupancy
The indoor storage and use of oxidizing materials shall be in accordance with Sections 6303.1.1.1 through 6303.1.1.2.
6303.1.2 Emergency Shutoff
Compressed gas systems conveying oxidizing gases shall be provided with approved manual or automatic emergency shutoff valves that can be activated at each point of use and at each source.
6303.1.2.1 Shutoff at Source
A manual or automatic fail-safe emergency shutoff valve shall be installed on supply piping at the cylinder or bulk source. Manual or automatic cylinder valves are allowed to be used as the required emergency shutoff valve where the source of supply is limited to unmanifolded cylinder sources.
6303.1.2.2 Shutoff at Point of Use
A manual or automatic emergency shutoff valve shall be installed on the supply piping at the point of use or at a point where the equipment using the gas is connected to the supply system.

This would address your concern regarding an “... event in 4th floor control area 2 that causes a leak ...”.

Reply
Mike
2/2/2023 12:54:51 pm

Todd,
It's important to note that Oxygen in the context of this table is an "Oxidizing Gas" in gaseous form. That is why it is listed as "N/A" within the "Oxidizer" row. The "Oxidizer" row only applies to liquid and solid oxidizers. The separate "Oxidizing Gas" row applies to oxidizing gases (in gaseous and liquid forms) as its name implies. 1500 cubic feet, which can be doubled for a fully sprinklered building, and doubled again for a gas room/cabinets. However on the 4th floor of a building, control area MAQs are greatly reduced to only 12.5% of the full quantity. So in a fully sprinklered building without gas cabinets, on the 4th floor you'd be limited to 375 cubic feet of oxidizing gas:
(1500 CF * 2)*12.5%=375 CF.

The information regarding the emergency shutoffs is helpful, and reconciles the concept of only counting the in-use gas within the boundaries of the control area, since the safety devices will prevent an unmitigated event that involves all gas within the closed use system.

Reply
Alex
2/2/2023 11:45:43 am

Hi,

I've run into issues like this before in the past where compressed gas cylinders are stored outdoors and piped inside. For me, during my review, the gases have been inert with no limit regarding the MAQ.

For you, oxidizing gas is limited to 1,500 CF (in an unsprinklered building), 1st floor. Therefore your limits are:
Second Floor CA1: 750 CF
Fourth Floor CA2: 187.5 CF

Even with a sprinklered building, if you were to assume all 400 CF in use on the fourth floor, you would be over your MAQ (375CF).

I'm not aware of a device/solenoid that would allow you to only calculate the quantity of O2 that is truly in your 4th floor CA. I would research emergency solenoid valves and talk to a few reps to see if there is something out there for this case. Would love an update down the road on this!

Alex

Reply
chad
2/2/2023 11:48:13 am

Agreed, no device would alleviate. Most places limit themselves to the 375 CF to avoid CA's

Reply
Tom
2/15/2023 08:42:50 am

NFPA 99 covers this I believe. Sorry not in a place I can research/reference it

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Aug '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT