MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Dampers Required for Room with Clean Agent?

2/20/2023

8 Comments

 
We have a project where we're adding a sound (anechoic) chamber and and protecting it with clean agent.

A question came up as to whether or not dampers are required for the HVAC system that provide supply and return air to the pre-manufactured chamber.

Is an anechoic chamber required to have dampers for limiting the migration of the clean agent?

My thinking is that the clean agent will be activated by an air sampling system, so there should be no meaningful amount of smoke in the chamber.

That said, do the dampers have to be listed for fire/smoke? 

Any help with getting specifics from code or a clearer understanding is always appreciated from the community so thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Glenn Berger
2/20/2023 08:05:51 am

You want smoke dampers to contain the clean agent in the protected volume.

Reply
schulman
2/20/2023 08:07:27 am

to do the job for the clean agent system the dampers just need to stop the hole so you don't have pressure loss ... smoke/fire requirements would be for other code reasons such as wall rating or compartmentalization for egress ...

Reply
Jesse
2/20/2023 08:58:16 am

Determining the amount of agent needed requires a volume calc. So without the dampers, you would need to include the area beyond where the damper would be. Otherwise you agent concentration won't be correct.

Reply
Todd E Wyatt
2/20/2023 09:43:20 am

Per the scoping Code (2021 IBC), a “clean-agent system” (904.10) which is an “Alternative Automatic Fire-Extinguishing System” (904) is required to be “be designed, installed, inspected, tested and maintained” in accordance with 2018 NFPA 2001 Standard on Clean Agent Fire Extinguishing Systems.

NFPA 2001 references (10) instances of “DAMPER” (see REFERENCES below) ...
• Chapter 7 Approval of Installations, 7.2.3.7 When applicable for system operation, fan coastdown and DAMPER closure time shall be verified that they are in accordance with the system design criteria.
• Chapter 9 Marine Systems A.9.7.2 Automatic shutdowns are the preferred method for shutting down a ventilation system. Shutdowns requiring personnel to find and manually close DAMPERs far from the fire extinguishing system discharge station should not be permitted.
• Annex C — Enclosure Integrity Procedure ... (8) instances ... This annex is not a part of the requirements of this NFPA document but is included for informational purposes only.

These DAMPER references do not require the use of dampers in “Clean Agent Fire Extinguishing Systems” although DAMPERS can be a part of the system to achieve the “Enclosure Integrity Procedure” (Section 7.5)

REFERENCES
2021 IBC
Section 904 Alternative Automatic Fire-Extinguishing Systems
904.1 General
Automatic fire-extinguishing systems, other than automatic sprinkler systems, shall be designed, installed, inspected, tested and maintained in accordance with the provisions of this section and the applicable referenced standards.
904.2 Where Permitted
Automatic fire-extinguishing systems installed as an alternative to the required automatic sprinkler systems of Section 903 shall be approved by the fire code official.
904.10 Clean-Agent Systems
Clean-agent fire-extinguishing systems shall be installed, maintained, periodically inspected and tested in accordance with NFPA 2001 and their listing. Records of inspections and testing shall be maintained.

2018 NFPA 2001
Chapter 7 Approval of Installations
7.2* General.
7.2.3 System Acceptance Testing.
7.2.3.7
When applicable for system operation, fan coastdown and DAMPER closure time shall be verified that they are in accordance with the system design criteria.
7.5 Review of Enclosure Integrity.
7.5.1
It shall be determined that the protected enclosure is in general conformance with the construction documents.
7.5.2
All total flooding systems shall have the enclosure examined and tested to locate and then effectively seal any significant air leaks that could result in a failure of the enclosure to hold the specified agent concentration level for the specified holding period.
7.5.3*
Quantitative results shall be obtained and recorded to indicate that the specified agent concentration for the specified duration of protection is in compliance with Section 5.6, using an approved blower fan unit or other means as approved by the authority having jurisdiction. (For guidance, see Annex C.)

Chapter 9 Marine Systems
9.7 Enclosure.
9.7.1*
To prevent loss of agent through openings to adjacent hazards or work areas, openings shall be one of the following designs:
(1) Permanently sealed
(2) Equipped with automatic closures
(3) Equipped with manual closures outfitted with an alarm circuit to indicate when these closures are not sealed upon activation of the system
A.9.7.1
A well-sealed enclosure is vital to proper operation of the system and subsequent extinguishment of fires in the protected space. Gastight boundaries of the protected space, such as those constructed of welded steel, offer a highly effective means for holding the fire extinguishing gas concentration. Where the space is fitted with openings, avenues for escape of the gas exist. Automatic closure of openings is the preferred method of ensuring enclosure integrity prior to discharge. Manually closed openings introduce added delay and an added human element into the chain of proper operation of the system. Failure of personnel to properly close all openings has been a recurring cause of gaseous systems not performing as intended. It is recognized that some openings in the enclosures, such as maintenance hatches and watertight doors, cannot be fitted with automatically operated closers due to personnel hazards or other limitations. In those cases, an indicator is required to alert the system operator that an opening has not been closed as required and thus the system is not ready for operation.
9.7.1.1
Where confinement of agent is not practical, or if the fuel can drain from one compartment to another, such as via a bilge, protection shall be extended to include the adjacent connected compartment or work areas.
9.7.2*
Prior to agent discharge, all ventilating systems shall be closed and isolated to preclude passage of agent to other compartments or the vessel exterior. Automatic shutdowns or manual shutdowns c

Reply
Franck
2/20/2023 11:07:29 am

If you want to keep your gas concentration for at least 10 minutes, you will probably need dampers.
And you may also need “overpressure” dampers to eliminate the overpressure at the initial stage of the discharge.

This being said, are you sure that gas protection is the best solution to protect your anechoic chamber ?
It might depend on your configuration, but most anechoic chambers have cones made of some type of combustible foam material.
If the fire is inside this cones structure, you will have a quick spreading fire and deep seated, so probably difficult to extinguish with your gas.
The question is : what are you protecting ? The room from a fire coming from the equipment being tested, or the equipment itself ?
Most anechoic chambers I have seen were sprinkler protected, and only a few of them had a gas protection in addition (not instead).
Be careful if you provide sprinklers, they have to be installed upside down (water is to be delivered towards the cones, not inside the room). And when provided on telescopic branch lines (to limit perturbations inside the room), it may become problematic from a maintenance en operational point of view.

Another underestimated issue with gas protection : over the time, dust accumulate over the cone surface. When activating the gas protection, because of the pressure and release of gas, the dust will be spread all over the room. If you test equipment that are very sensitive to dust, such as mirrors for space industry, it could be a disaster.

Reply
Chad
2/21/2023 08:47:15 am

Be careful if you provide sprinklers, they have to be installed upside down (water is to be delivered towards the cones, not inside the room).

That is a darn good point! I can imagine someone arguing it but you are certainly right.

Reply
Franck
2/20/2023 11:16:10 am

For the “overpressure” dampers, I have a “funny” real story.
A very large anechoic chambers was protected by sprinklers and gas (nitrogen, or something similar). This large chamber was used to test satellites, so they wanted to be sure that the system was working.
Why sprinkler + gas ? Because they had a fire in this chambers that damaged a several hundred million dollars satellite.

Sprinkler arms operations were tested with air pressure.
For the gas protection system, they wanted to make an actual release with concentration measurements at several heights.
But when they discharged the gas (several dozens of cylinders… the test cost a fortune), the overpressure was such that it activated the anti-panic bars on the entrance door and opened them widely, releasing the gas out of the chamber immediately!

To a certain point, this failure was a good thing as they could remediate the issue… Imagine if that had happened during a fire !

Reply
Frank Savino link
12/26/2023 10:47:05 am

You need to imagine that your clean agent protected room is a large swimming pool that you are trying to fill up with water. Most clean agents like Novec 1230 (aka FK 5-1-12) or FM-200 (aka HFC227es) are heavier than air. The water and clean agent will leak out through all of the openings in the walls, doors, and floor. It will not leak out upward through openings in the ceiling. The HVAC supply and returns grills are at the ceiling and agent will leak upwards. If the HVAC is allowed to continue to run after agent discharge, you will dilute your extinguishing concentration. The best and easiest way to deal with that is to electrically interlock your clean agent to automatically shut down the HVAC upon agent discharge. You do not need dampers. Most of the time, HVAC shuts down instantaneously. If not, you can time delay the agent discharge to give time for the HVAC to shutdown. Keep in mind that if you have HVAC openings in walls or the floor, these will likely need to be dampered. Remember the swimming pool analogy.



Doing it this way will save a lot of money in damper installation, and wiring. One issue that you will need to address is passing the room integrity test because you have room openings through the open HVAC ducts at the ceiling. The test procedure allows you to temporarily close those duct openings at the ceiling with cardboard and duct tape for test purposes.

Inert gas agents like Inergen, ProInert, Nitrogen, or Naturara are very close to the same density as air. They very much stay suspended in the room and their hold time is far superior to the other clean agents. You will need to also be sure to shut down the HVAC electrically to prevent agent loss from dilution. Same rules apply as in the first example i gave.

The inert gas agents require that a lot of agent be discharged into the protected space compared to the other clean agents. You have to do a calc to make sure that you do not over pressure the room and cause a wall in the room to rupture. You might need a pressure operated pressure relief vent to prevent over pressurization. This is weighted damper that automatically opens upon pressure increase and closed when the pressure normalizes. You need to make sure that you don’t over pressurize an adjacent space. You might need to duct this to the outside of thr building. Doing this over pressure calc is very important. It is described in NFPA 2001 and the integrity test people can help you with this. Please note that NFPA 2001 requires all clean agent systems be calculated for over pressurization but it is especially important to do for inert gas agents.

If you do use dampers, they should be fail safe ( fail in the state you want them to be in a fire). Also, they must be at least 99% airtight. Many are very leaky and will cause agent dilution. In my opinion, they do not need to be fire listed but I am not sure about the listing question.

Bottom line is avoid dampers if you can. They usually are not needed.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT