The installation contractor and I have had an argument about how sprinklers should be spaced and calculated in a 13R system.
I have argued that per NFPA 13R Section 7.1.1.3.1, we should calculate 3 sprinklers in the greatest hydraulic demand area. This area is furthest from the riser and the calculation permits 16x16-ft spacing for the area that has the most sprinklers. Section 7.1.1.3.1: For each of the following situations, the number of sprinklers in the design area shall be all of the sprinklers within a compartment, up to a maximum of four sprinklers, that require the greatest hydraulic demand: The contractor wants to remove a sprinkler in a single room and move a sprinkler 10 feet off of the exterior wall, but in NFPA 13R makes no mention of a single sprinkler proof calculation that could justify such a move. There is no mention of a single sprinkler calculation in NFPA 13R permitting a spacing of 20x20, and so all sprinklers on the project can be only 16x16 if the greatest hydraulic demand is permitting it. In NFPA 13D, it makes no mention of a single sprinkler calculation either, but does refer to single sprinkler operations in A.10.1. I did not feel comfortable designing a sprinkler system that was not up to code standards and need an outside opinion on this matter. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments
Peter Howard
2/14/2023 06:35:55 am
Why can't a residential head that is listed for 20 x 20 spacing (at the correct pressures) be calculated for 20 x 20 spacing?
Reply
Anthony
2/14/2023 07:20:06 am
Yes you definitely can calculate only one sprinkler if there is only one sprinkler in the compartment.
Reply
danefre
2/14/2023 07:44:21 am
Contractor is correct. Yes, you can have a 1 sprinkler calculation in 13R if that's the compartment that produces the greatest demand. Also, very common to reduce number of heads and increase spacing for hydraulic purposes. Each compartment is calculated separately and you can either prove all of them or the ones that logically make the most sense.
Reply
Alex
2/14/2023 08:05:40 am
Yes, you can only calculate a single sprinkler head if only one head is protecting the entire compartment. Like others have mentioned, if you have a compartment on the same floor that is protected by (2) sprinklers, I would run both calcs (1 with 2, the other with the single head) to ensure both designs work.
Reply
Jesse
2/14/2023 08:15:24 am
Oh how I wish GCs would stick to GC things and let fire people do fire things.
Reply
Dan
2/14/2023 08:33:16 am
We provide this kind of proof calculation on a normal basis in our residential designs. It allows us to provide layouts for the couple different situations we find during install.
Reply
Casey Milhorn
2/14/2023 09:03:34 am
Everyone covered it really well, the only thing I would add is that MAKE SURE you are meeting the definition of a compartment per NFPA 13R. Then yes, a 1 head calc could prove 1 head at 20x20, with the rest being at 16x16.
Reply
Joshua Bush
2/14/2023 10:49:41 am
I had a similar issue just last week. I had a contractor place a ceiling fan in the main room of an apartment. Because of this change I had to adjust the head to be just over 9'-0" from the farthest wall. For calculation purposes that sprinkler would demand a higher pressure to work properly. I still had 2 other heads in that same room that were spaced at 16'x16'. So, I kept the pressures required for those heads at the 7.0 PSI. Now I have 1 head with a pressure requirement of 16.7 PSI and 2 heads at 7.0 PSI. My plans were rejected from the reviewer with the reasoning that if I increase the pressure of one head in a remote area calculation, all heads have to be calculated at that higher pressure, even if they are spaced in a way that does not require higher pressures to provide coverage. In the end I was told I had to increase the pressure requirements for all 3 heads to16.7 PSI for the calculation to be correct. I was told that I was not able to pick and choose pressures in a remote area calculation. So from my understanding, if I have a multi head room, I must calculate all sprinklers with the pressure requirements of that single head that requires increased pressure. Does this sound correct? I feel like I am either missing something or the plan reviewer is. I'm happy either way. I'd just like to know which is correct so that I do things the proper way.
Reply
Cliff Schulze
2/14/2023 12:50:59 pm
The reviewer is partially right. The 7 psi is a minimum but if another head in the same room has a higher pressure, it will drive up the pressure to the other heads. If one head in the room needs 16.7 psi, the other heads in the room are going to see the higher pressure as well. The only caveat is the pressure can be reduced by manipulating the pipe sizes; i.e. larger pipe size to the head requiring 16.7 psi, smaller pipe size to the heads requiring 7 psi.
Reply
danefre
2/14/2023 03:02:03 pm
What Cliff said is true. The 14x14 will flow more than the minimum due to the 20 x 20 causing it to overflow.
Reply