MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Use a Well in an NFPA 13D Fire Sprinkler System?

4/26/2022

6 Comments

 
We have a house (single family home) that will require an NFPA 13D system, but it is not going to be connected to city water.

There is a well onsite. The well completion report does not provide a pressure or flow output.

Can the well be used as part of the hydraulic calculations? What data would be necessary to incorporate it?

If not, I'm assuming that both a pump and tank would be needed here for the 13D system?

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
Alex
4/26/2022 06:45:08 am

Hi,

NPFA 13D (2013) 6.2 states that a "well with a pump of sufficient capacity and pressure to meet the sprinkler demand" shall be considered acceptable as an available water supply.

You will need to ensure that the well pump and holding tank can satisfy a 10 minute water demand rate (6.1.2) or 7 minutes if you fall under the provisions listed in 6.1.3.

You will need the following:
- holding tank size
- available pressure
- determine your demand duration
- determine your demand flow
- determine your required pressure

NPFA wrote about this back in 2019 as well: https://www.nfpa.org/news-and-research/publications-and-media/blogs-landing-page/fire-sprinkler-initiative/blog-posts/2010/02/19/nfpa-13d-fire-sprinkler-systems-on-well-water

Thanks,
Alex

Reply
Jesse
4/26/2022 08:10:37 am

We have done a handful of these with similar issues. Alex is correct.

The one that I did with best results had two pumps. A well pump pumping from the well into a storage tank with about 500-g capacity, and then a pump from the storage tank to the domestic system. The tank more or less functioned the same way a break-tank or surge tank would work in that the well pump was never considered in the calcs. In our case, with a 500-g tank clearly the 10 minute duration wasn't an issue even without considering refill rate. As I recall, our AS demand was in the area of 30-GPM.

Reply
Joe
4/26/2022 10:02:26 am

We have installed many 13D projects with private well pumps. A large majority of private well pumps will not produce the required flow unless the well pump is a variable speed pump.
We typically end up installing an independent 13D Pump & Tank System like the Talco Home Hydrant for example.
We design for a 16'x16' Spacing with a K4.9 requiring 13 GPM for two sprinklers, so 26 GPM would be required.
If you install the 13D pump & tank system, make sure the plumber provides a 3/4" auto fill water supply line with shut-off valve above the tank. The autofill will provide additional water for fire protection.

Reply
Susan McMahon
7/16/2024 07:22:50 pm

I am looking for someone certified to design a 13D system for a small house on well water. We need a system with a tank supply independent from the well. Are you able to design such a system or can you refer me to someone who does?

Thanks,
Susan

Reply
Dave
4/26/2022 10:25:53 am

Like Joe above, I've designed many 13D's supplied by a private well, if it could provide the supply and duration. Sometimes keeping sprinkler spacing at a minimum, once in a while get lucky and not have a compartment with more than one sprinkler. Often had to upgrade the well pump itself, or catch it early if a new well. But I prefer the pre-packaged 13D units if it's in the budget and there's space for it. As you know often the uninformed owner is already angry at having to install a system at all.
13D was not our bread and butter, that alone wouldn't keep our lights on, but we did them to provide a complete service.

Reply
Scott McBride
4/26/2022 10:59:12 am

As an AHJ, all of the others are on the mark. I also emplore you to have a discussion with your local AHJ and find out what specific requirements that they have regarding rural supplied 13D systems.

Does the well pump feed directly in to the tank or is it connected to the domestic water supply and the tank. If so you may be required to install a backflow preventer.

You can also reduce the size of the tank if you have limited space for the tank and the data for the well pump is known, but if not I would recommend sizing the tank for the required flow from the calcs times 7 or 10 minutes as required. As mentioned above though you must account for refill time if you are reducing tank size.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT