MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Can CPVC be Run Exposed?

3/31/2023

13 Comments

 
With the use of CPVC, what are the limits to how much can be exposed?

I had thought that we needed to have all of the pipe concealed, and I can't see in code how this is addressed.

We have a project with a temperature-controlled and insulated attic (the mechanical engineer has confirmed it will be kept above 40 degrees F year-round) in a warm climate. This is in an NFPA 13R apartment building.

Is CPVC allowed to be run exposed through the combustible attic space?

The attic is not sprinkler protected (NFPA 13R system, 3-story, apartments, smaller-sized project). Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
13 Comments
Chad
3/31/2023 07:32:35 am

Sadly/Ugly, it can be exposed in some cases as long as its in line with the installation manual. Viking/Blazemaster says:

Exposed Installations Listed hangers are required for all exposed installations. Viking Plastics BlazeMaster® CPVC fire sprinkler products are UL and C-UL Listed for installation by a qualified installer or contractor without protection (exposed) with the following restrictions: (I wont post it all here)

/https://www.vikinggroupinc.com/sites/default/files/documents/080712.pdf'

Each brand will have its own separate instructions.

Reply
Anthony
3/31/2023 08:20:24 am

CPVC 100% can be run in combustible concealed space (how else can you install it?)

Reply
Darin
3/31/2023 09:16:10 am

I’m with you. Nearly every single installation is “exposed” in an attic. Not sure if the original question means exposed as in an occupied space, e.g. along the underside of a smooth ceiling.

Reply
Randy Kimbro
3/31/2023 08:32:03 am

We just ran into this problem (we are an AHJ). Blazemaster, if exposed, must be run next to a smooth finish, horizontal surface. Otherwise it must be protected. Their reasoning is that the CPVC might fail prior to the sprinkler head activating or may fail during activation.

Call the BlazeMaster tech support number. (216-447-5330 [email protected]) They were extremely helpful in explaining and later validating what we were requiring. Since we are an AHJ, we did not have installation experience. We observed some things that did not appear correct and each time a call to BlazeMaster helped us understand and then explain the issue to the installation contractor.

Reply
Dan Wilder
3/31/2023 08:40:49 am

It depends...which MFG and what their specific listings are.

Spears allows exposed in attics and basements when other criteria are met (based on sprinkler used, spacing and distance below ceilings, and construction). Blazemaster allows exposed as well with similar requirements. Both have very specific conditions as to when its allowed to be run exposed.

As to specifically within an attic space, is the space considered a combustible concealed space or just an attic? This also changes criteria but many times the CPVC needs to be "tented" (insulation placed over the top of the CPVC).

Use your MFG recommendations, it's not in NFPA, this is a listing criteria allowance.

https://www.spears.com/flameguard.htm
https://www.blazemastertraining.com/

Reply
OP
3/31/2023 10:06:36 am

This is a warm-climate, insulated attic that's supposed to stay above 40-degrees.

We run CPVC in non-sprinklered combustible floor/ceiling spaces all the time, so I guess this isn't that far of a departure from that situation.

However, it's just a large open combustible attic. No storage, no occupancy. It just 'feels' a little different because we have the warm/insulated attic which is unusual for me. A fire up there in a large non-sprinklered space would compromise the pipe, but I guess that's not any different than a fire in a combustible concealed space also compromising the pipe.

NFPA 13R gets me in a twist sometimes on ideology, but I get that it's not trying to be an NFPA 13 system.

Reply
Jesse
3/31/2023 09:06:33 am

CPVC can indeed be exposed. We get that a lot, where someone heard it from someone, who heard it from someone, who heard it from someone that it can't, but no one knows where in the code it says that.

Each manufacturer handles it differently as far as how much is exposed, using what hangers, and under what circumstances.

Reply
Randy Kimbro
3/31/2023 09:35:02 am

Here is the exact wording from the Viking BlazeMaster installation manual:

Combustible Concealed Installations
Viking Plastics BlazeMaster® CPVC fire sprinkler products CANNOT be installed exposed in spaces defined by NFPA 13 as combustible concealed areas requiring sprinklers.

Exception: In accordance with the UL Listing, specially Listed sprinklers exist that have been tested and are Listed for use with Viking Plastics products in combustible concealed spaces requiring sprinklers.

Standard Coverage Sprinklers
These installations shall be below a smooth, flat, horizontal ceiling construction and require the use of Viking Plastics approved one-step cement. The use of listed hangers for thermoplastic sprinkler piping mounted directly to the ceiling (or wall) is permitted. The resulting clearance between the pipe and ceiling (or wall) resulting from the use of the listed hanger is acceptable.

Residential
These installations shall be below a smooth, flat, horizontal ceiling construction, are limited to the unobstructed construction, require the use of Schedule 80 fittings for sizes 1-1/2 inches and greater, and require the use of Viking Plastics approved one-step solvent cement.

There are a lot more details in the manual.

Reply
sean
3/31/2023 11:39:47 am

Yes follow mfg requirements

Reply
Todd E Wyatt
4/1/2023 07:15:27 pm

If the building meets the (3) requirements for use of NFPA 13R (versus NFPA 13) per the scoping Code ... “2021 IBC 903.3.1.2 NFPA 13R Sprinkler Systems” is shown below in REFERENCES ... then NFPA 13R is the applicable “referenced standard.”

If the attic meets the exceptions per “2021 IBC 903.3.1.2.3 Attics”, automatic sprinkler system (ASPS) protection of the attic is NOT required.

(Based on the building being an “apartment” and 3-stories, it would be classified as a Group R-2 Residential Occupancy Classification (OC) per 2021 IBC Chapter 3 Occupancy Classification and Use. The Type of Const is not known.)

If the Chlorinated polyvinyl chloride (CPVC) pipe meets the requirements of “2022 NFPA 13R Chapter 5 System Components, 5.2 Aboveground Piping and Equipment, 5.2.3” (see REFERENCES), then the intended installation is compliant.

Reply
Todd E Wyatt
4/1/2023 07:15:50 pm

REFERENCES
2021 IBC
Chapter 9 Fire Protection and Life Safety Systems
903.3 Installation Requirements
903.3.1.2 NFPA 13R Sprinkler Systems
Automatic sprinkler systems in Group R occupancies shall be permitted to be installed throughout in accordance with NFPA 13R where the Group R occupancy meets all of the following conditions:
1. Four stories or fewer above grade plane.
2. The floor level of the highest story is 30 feet (9144 mm) or less above the lowest level of fire department vehicle access.
3. The floor level of the lowest story is 30 feet (9144 mm) or less below the lowest level of fire department vehicle access.
The number of stories of Group R occupancies constructed in accordance with Sections 510.2 and 510.4 shall be measured from grade plane.

903.3.1.2.3 Attics
Attic protection shall be provided as follows:
1. Attics that are used or intended for living purposes or storage shall be protected by an automatic sprinkler system.
2. Where fuel-fired equipment is installed in an unsprinklered attic, not fewer than one quick-response intermediate temperature sprinkler shall be installed above the equipment.
3. Where located in a building of Type III, Type IV or Type V construction designed in accordance with Section 510.2 or 510.4, attics not required by Item 1 to have sprinklers shall comply with one of the following if the roof assembly is located more than 55 feet (16 764 mm) above the lowest level of fire department vehicle access needed to meet the provisions in Section 503.
4.1. Provide automatic sprinkler system protection.
4.2. Construct the attic using noncombustible materials.
4.3. Construct the attic using fire-retardant-treated wood complying with Section 2303.2.
4.4. Fill the attic with noncombustible insulation.
The height of the roof assembly shall be determined by measuring the distance from the lowest required fire vehicle access road surface adjacent to the building to the eave of the highest pitched roof, the intersection of the highest roof to the exterior wall, or the top of the highest parapet, whichever yields the greatest distance. For the purpose of this measurement, required fire vehicle access roads shall include only those roads that are necessary for compliance with Section 503 of the International Fire Code:
4. Group R-4, Condition 2 occupancy attics not required by Item 1 to have sprinklers shall comply with one of the following:
4.1. Provide automatic sprinkler system protection.
4.2. Provide a heat detection system throughout the attic that is arranged to activate the building fire alarm system.
4.3. Construct the attic using noncombustible materials.
4.4. Construct the attic using fire-retardant-treated wood complying with Section 2303.2.
4.5. Fill the attic with noncombustible insulation.

Reply
Todd E Wyatt
4/1/2023 07:16:28 pm

REFERENCES
2022 NFPA 13R
Chapter 5 System Components
5.2 Aboveground Piping and Equipment.
5.2.1
Pipe or tube used in sprinkler systems shall be of the materials specified in Table 5.2.1 or in accordance with 5.2.2.
Table 5.2.1 Pipe or Tube Materials and Dimensions
Materials and Dimensions / Standard
Chlorinated poly(vinyl chloride) (CPVC) plastic pipe (SDR–PR) / ASTM F442/F442M

5.2.3*
Chlorinated polyvinyl chloride (CPVC) pipe shall comply with the portions of the American Society for Testing and Materials (ASTM) standards specified in Table 5.2.1 that apply to fire protection service.
A.5.2.3
CPVC is a plastic material, and consideration is necessary when other materials or chemicals come in contact with CPVC that can cause degradation of performance of the pipe due to interaction of materials. Other construction materials include, but are not limited to, materials used in the fabrication of the sprinkler system, additives to water supplies, cable and wiring, and certain insecticides and fungicides. Compliance with 5.2.3 combined with following the manufacturer’s guidance on installation and compatible materials will help prevent premature performance degradation of nonmetallic piping. Mechanical stress caused by hanging methods or bending on nonmetallic piping beyond the manufacturer’s recommended limitations can cause stress failure over time and should be avoided.
5.2.3.1
Nonmetallic pipe in accordance with Table 5.2.1 shall be investigated for suitability in automatic sprinkler installations and listed for this service.
5.2.3.1.1
Listed nonmetallic pipe shall be installed in accordance with its listing limitations, including installation instructions.
5.2.3.1.2
Manufacturer’s installation instructions shall include its listing limitations.
5.2.3.2
When nonmetallic pipe is used in systems utilizing steel pipe internally coated with corrosion inhibitors, the steel pipe coating shall be listed for compatibility with the nonmetallic pipe materials.
5.2.3.3
When nonmetallic pipe is used in systems utilizing steel pipe that is not internally coated with corrosion inhibitors, no additional evaluations shall be required.
5.2.3.4*
When nonmetallic pipe is used in systems utilizing steel pipe, cutting oils and lubricants used for fabrication of the steel piping shall be compatible with the nonmetallic pipe materials in accordance with 5.1.2.2.
A.5.2.3.4
When fabricating steel pipe for a combination (CPVC–steel) system, the cutting oil and lubricants can cause performance degradation of the CPVC piping. Cutting oils and lubricants found to be compatible are available and should be used.
5.2.3.5
Fire-stopping materials intended for use on nonmetallic piping penetrations shall be compatible with the nonmetallic pipe materials in accordance with 5.1.2.2.
5.2.3.6
Nonmetallic pipe shall not be listed for portions of an occupancy classification.
5.2.3.7
Where pipe other than steel is run horizontally or vertically through wood or metal studs, the following provisions shall apply:
(1) Steel shield plates shall be provided where the face of the piping is less than 1.25 in. (32 mm) from the nearest edge of the member.
(2) Steel shield plates shall have a minimum thickness of 0.0575 in. (1.463 mm) (No. 16 gauge).
(3) Steel shield plates shall cover the area of the pipe where the member is notched or bored.

5.2.9
Fittings used in sprinkler systems shall meet or exceed the standards in Table 5.2.9 or be in accordance with 5.2.12.
Table 5.2.9 Fittings Materials and Dimensions
Materials and Dimensions / Standard
CPVC:
Threaded chlorinated poly(vinyl chloride) (CPVC) plastic pipe fittings, Schedule 80 / ASTM F437
Socket-type chlorinated poly(vinyl chloride) (CPVC) plastic pipe fittings, Schedule 40 / ASTM F438
Socket-type chlorinated poly(vinyl chloride) (CPVC) plastic pipe fittings, Schedule 80 / ASTM F439

Chapter 7 Design Criteria
7.1 Inside Dwelling Unit.
7.1.1 Residential Sprinklers.

7.4 Attics.
7.4.1 Occupied Attics and Attics Used for Storage.
Attics that are intended for occupancy or storage shall comply with Section 7.1, where the attic is part of the dwelling unit, or Section 7.2, where the attic is outside of the dwelling unit.
7.4.1.1
Sprinkler temperature ratings shall comply with 6.2.3.
7.4.2 Fuel-Fired Equipment.
Where fuel-fired equipment is installed in an attic that is not otherwise required to have sprinklers, the space containing the fuel-fired equipment shall comply with 6.6.6.1 through 6.6.6.4.
7.4.3* Other Attics.
Attics that are not required by 7.4.1 to have sprinklers shall be permitted to have protection in accordance with one of the following.
(1) Protection complying with NFPA 13
(2) Protection using sprinklers specifically listed to provide attic protection in residential occupancies using a discharge density of not less than 0.05 gpm/ft2 (2.04 mm/min) and a design area of not less than four sprinklers
A.7.4.3
NFPA 13R does not require installat

Reply
James Art, FPE
4/3/2023 09:37:08 pm

Many years ago, in the '70's,
before they came out with the "rated" CPVC,
that melts a bit higher than PVC,
the Palo Alto Fire Dept did some fire sprinkler experiments with Sch. 40 PVC, plain white, like heavy irrigation pipe.

The results were interesting:
If the fire was near a sprinkler, then the sprinkler activated, and the flowing water kept the pipe intact.

If the fire was away from a sprinkler, often the pipe "pinholed" putting some water on or near the fire, and also the flowing water cooled the pipe, but not as well.
After either fire some of the pipe would need to be replaced.
-------------------------------------------------------------------
When I worked for Lawrence Livermore Lab, I discovered they had sprinklered a few of what they called "Trailers" using white PVC pipe.
These buildings were built off site, in 10 foot wide 50 foot long sections, them put together up to 5000 sq. ft. max.
In 1980 a 5.5 magnitude earthquake occurred on the up to them unknown Greenville Fault. Cabinets fell, and the "Trailers" bounced up and down, and off their stands, and broke the supply piping.
Now bookcases are bolted and "Trailers" are secured there.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Aug '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT