MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

When is Standard Response Better Than Quick?

6/30/2021

10 Comments

 
When are standard response sprinkler heads a better choice than quick or fast response heads (5mm vs. 3mm bulb)?

Are there applications where it would be preferable to have a slower response time?

As far as I know, quick and standard response heads cost the same, come with the same k-factors, and the same temperature ratings.

Why would the slower one be chosen? When would you choose a Tyco TY-B instead of a TY-FRB?

​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments
Pete
6/30/2021 06:49:52 am

NFPA 13 Chapter 11 I believe says quick response sprinklers shall not be used for extra hazard occupancies or other occupancies with flammable liquids or combustible dusts.

There might also be a restriction to not being allowed quick response sprinklers in storage applications.

Reply
Chris Nelson
5/31/2022 06:03:57 pm

NFPA 13 2016 12.6.6 allows QR where the QR sprinklers are listed for storage applications.

Reply
MattC
6/30/2021 08:17:14 am

Any application where you may have many sprinklers activating simultaneously, or in quick succession typically warrants the use of standard response sprinklers.
The idea being that many sprinklers activating at the same time is more taxing on the system, and less effective at controlling the fire than a smaller number of sprinklers operating in the right places.

Seems counterintuitive until you see some live fire testing, but the difference is staggering.

Reply
franck
6/30/2021 08:30:59 am

As indicated by Pete, quick response sprinklers are normally recommended by NFPA for Light and Ordinary hazard occupancy, with a possible reduction of the desihn area (25 to 40%).
This is based on the fact that comparative fire tests with standard response and quick response spray sprinklers demonstrated that the earlier the water is applied, the smaller the size of the resulting fire. The smaller fire size, in turn, results in the operation of fewer sprinklers.

But this only applies for low combustible loads / slow heat release rates.
If you provide quick response with extra hazards or storage, as indicated by Matt, you may activate too many sprinklers at the ceiling in the early stage of the fire, and then have more operating sprinklers at the end.
This is why, it is also normally recommend to have high temperature sprinklers for storage occupancies and extra hazard occupancies.

As a summary : if your combustible load is quite low (slow heat release rate), and you want to activate the sprinklers quickly before the fire spread and develop, QR are a good idea. For example for offices, corridors...
If the combustible load is higher, then standard reponse are better (such as machine shop, miscelaneous storage areas...)

Only exception: ESFR.
ESFR are designed for storage and are quick response (Early Suppression Fast Response).
But the design of these sprinklers is different from standard spray. They are not designed to control the fire, but to extinguish it.
As soon as one head activate, it will have an effect to avoid the activation of the surrounding ones, if not needed.

Reply
Salvatore Izzo
6/30/2021 09:17:02 am

The use between standard response and sprinklers that contain fast response thermal elements (ESFR, residential, quick response, CMSA) is dictated by the standards, the type of design criteria chosen, as well as the listing of the sprinklers themselves. It is really not a subjective choice of installation. For example, as mentioned by others, where life safety is a concern, residential or quick response sprinklers will be required by the standards. Where design criteria is based on water quickly being applied to the fire in its early stages, design area adjustments by the standard are permitted. Extended coverage sprinklers require a fast response thermal element to be able to operate quickly to enable coverage and fire control over a larger area, etc.

Reply
Brad K
6/30/2021 09:45:44 am

An additional note to consider. Please check your local adopted building codes when considering QR vs SR sprinklers. For example, several instances in IBC require quick response sprinklers. Specifically one example is 2015 IBC 903.3.2 where sprinklers are required in light hazard occupancies (among others) as defined by NFPA 13. This is important when selecting sprinklers.

Reply
Daniel
6/30/2021 09:48:08 am

The maintenance requirement is also a big consideration. Standard response heads need to be tested every 50 years vs. 20 years for quick responses. For my work we had several work trailers that had quick-response heads which were replaced with standard response heads as quick response heads are not required for an office trailer.

Reply
DL
6/30/2021 11:51:08 am

Along with the excellent explanations above, generally, there IS a price difference that can quickly add up, and pricing is something designers also need to be aware of. For example, the TY-FRB you mention costs significantly more than the TY-B.

Reply
Mike
6/30/2021 12:49:59 pm

In Light hazard when you want to take an area reduction.

Reply
Jesse
7/1/2021 08:33:06 am

The advantage in standard response has to do with flash fire events such as combustible dust, flammable liquids, etc. The concern being that the flash heat from the ignition would open too many sprinklers, thus overwhelming the available water supply. With protection being overwhelmed, the resultant fire takes the building.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT