A high-rise is considered a building with an occupied floor located more than 75-ft above the lowest level of fire department vehicle access.
Would a rooftop access stair with floor level located at 76' warrant the requirements of a high-rise building? IBC 2015 Section 1011.12.2 states that where a stairway is provided for roof access shall be provided through a penthouse complying with 1510.2. Section 1510.2 states penthouse complying with 1510.2.1-5 shall be considered part of the story below. The roof is not occupied and is only provided for egress for equipment access for equipment located on the roof. Technically a portion of the occupied story is located above 75-ft. Do I need to meet highrise requirements? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Darin
11/10/2022 08:35:41 am
No
Reply
Jesse
11/10/2022 08:37:09 am
It would not be considered an occucpiable floor.
Reply
Todd E Wyatt
11/10/2022 09:30:00 am
Short Answer
Reply
Todd E Wyatt
11/10/2022 09:34:48 am
... per 2021 IBC ...
Reply
Danefre
11/10/2022 09:52:16 am
Agreed with the above but also check state amendments. For example Massachusetts is 70ft to top of occupiable floor.
Reply
Bill
11/10/2022 01:26:35 pm
Check the municipality, in Chicago a high-rise is 80' to the roof regardless of the number of floors. mechanical penthouse roofs may add to that height depending on their square footage.
Reply
Alex
11/10/2022 05:03:31 pm
Agree with all other comments above - this would not tip you over.
Reply