MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Requirements for Two-Way Door Swing?

12/21/2022

10 Comments

 
​In the corridors of an apartment building (wrap) there are fire doors that are double-egress pairs that are left-hand-reverse by left-hand reverse which follows the natural traffic pattern within the corridor.
Picture
However, there are also several right-hand-reverse by right-hand-reverse in the same corridor.

Is there a requirement one way or another on which direction these are supposed to be?

​I informed the project manager that the egress needs to follow the natural traffic pattern. I was curious about the different flow patterns of the doors so I researched the code but was unable to locate anything in the code regarding whether it was code or not, except for the AHJ. The county where I live also agreed with me but if someone out there knows if this is code please respond.

​​​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments
Corey Eppinghaus
12/21/2022 08:16:40 am

Just making comment to see what comes of this.

Reply
Glenn Berger
12/21/2022 08:25:37 am

Need a plan view to determine current requirements for door swings. Many of these older facilities have undergone several renovations, which have impacts on current egress requirements.

Reply
Todd E Wyatt
12/21/2022 08:34:26 am

SHORT ANSWER
The Codes do not designate which side of the Exit Access Corridor (EAC), left vs right, that Exit Access Doors (EAD) are required to swing in the direction of egress.
The AHJ can only interpret and/or enforce the adopted Codes. The AHJ cannot require design features that are not included in the Codes.

EXPLANATION
Door swing direction is determined by the Occupancy Classification (OC), by special “use”, and/or by the calculated Occupant Load (OL).

2021 IBC Ch 10 Means of Egress identifies the requirements for Exit Access Doors (EAD) including the cross-corridor, opposite swinging double doors in your question.

Per 2021 1010.1.2.1 Direction of Door Swing, the following OC require EAD to swing in the direction of egress travel :
1) Group H Hazardous

Per 2021 IBC, the following special “use” require EAD to swing in the direction of egress travel :
1) 1010.2.9.1 Refrigeration machinery doors >1000 SF.
2) 101.2.9.2. Rooms with electrical equipment … electrical equipment rated >800 amperes containing overcurrent/switching/control devices & EAD is <25 feet from the working space (see NFPA 70).

Per 2021 1010.1.2.1 Direction of Door Swing, the following OL requires EAD to swing in the direction of egress travel :
1) Room or Area of 50 or more occupants.

Based on this scenario presented (e.g. OC = Group R-2 Residential … Apartment), this cross-corridor, opposite swinging double doors are required because the calculated OL on BOTH sides of these doors are > 50 occupants.

Reply
Aviv
12/21/2022 10:54:56 am

How could a corridor be 50 occupants on each side of every one of those doors? is it really long? or must you account traversing through it from adjacent spaces?

Reply
Todd E Wyatt
12/22/2022 08:49:36 am

Yes, the calculated Occupant Load (OL) would include rooms, areas and spaces that access the (shared) Exit Access Corridors (EAC) that then lead to an Exit (e.g. Interior Exit Staiway). Any cross-corridor doors in an EAC that would be used by >50 occupants are required to swing in the direction of egresss.

When calculating the OL, all area of rooms/spaces within the interior face of the exterior walls are to be included and all are required to be assigned an Occupant Load Factor (OLF), even corridors.

Colin Triming
12/21/2022 10:33:57 am

I agree that the code doesn't answer this question as stated. Unless you happen to be from Australia (like me) you have been taught to keep right since you were knee high to a grasshopper. If the corridor is full of smoke and you come to the doors you might get confused and head back the way you came. It could also be confusing for firefighters. I think these doors should be turned around.

Reply
martin m
12/21/2022 09:41:29 pm

To the right in the states too growing up

Reply
Alex
12/27/2022 06:39:43 am

I agree with Colin. I am not aware of a code section that states cross doors have to swing in a certain direction per side but it is common to always keep right. I would recommend switching the entire assembly so the door on the right is opposite.

Thanks

mike bauer
12/21/2022 11:06:45 am

We have alot of these in our jurisdiction in apartment buildings with enclosed corridors. They are separating the building into different fire areas under section 707 (Fire Barriers) with a 2 hour rating for residential construction. Under normal conditions they are held open by magnetic devices connected to the fire alarm system. The only thing we would look at if the direction of travel were in question is the travel distance to an exit. If the doors were placed in one part of the building where the path was required to be through them, then they would have to open in the path of egress travel. We have not had this issue as on both sides of the Fire Barrier door, there have been two exits available within the required travel distance.
I will say in my opinion a more important concern and problem has been the contractor installing the correct rated gasket molding on the door and frame to meet the listing. The fact that the picture shows what appears to be a slide bolt at the top and you can see between the doors is concerning.

Reply
DS
12/21/2022 01:04:21 pm

This is usually a designer using the fire compartment allowance in the IBC to increase the floor size or square footage of the building. It basically is providing exit access in both directions and has an active door leaf in one direction from each side. This could also be because of an assembly occupancy with an occupant load greater than 49, but is not typically the case in the R-2 occupancies.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT