Does Every Occupant Need Access to All 3 Exits?

12/16/2022

7 Comments

 
A business occupancy we're working on has 550 occupants, and requires three means of egress per Section 7.4.1.2 (NFPA 101, 2018 Edition).

Section 7.5.1.1.1 indicates that egress shall be arranged such that each occupant has access to not less than two means of egress.

When the three means of egress are required per Section 7.4.1.2, does access to all three means of egress need to be provided to each occupant?

Or will providing access for each occupant to a minimum of two means of egress satisfy the code requirement?

​​​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Alex
12/16/2022 07:41:22 am

When determining number of exits, there are two main driving factors: occupant load and common path of travel.

Occupant Load:
For your case, since you are over 500 occupants (and under 1,000), you are required to provide three means of egress. Two of the means of egress need to be properly separated. This is to decrease the chance of congestion and ensure adequate time to egress. When you layout the exits, you need to indicate the number of occupants that will be utilizing each exit and show the egress width is in compliance.

Common Path of Travel:
Now, if you have a smaller space that will be loaded under 50 occupants, it is still possible to require two means of egress. You need to review the common path of travel, per occupancy classification, and ensure that in any one location the common path of travel is in compliance.

To answer your question, no, not every occupant needs three means of egress. BUT, any room loaded over 50 needs two and any room/space loaded over 500 will need 3. You then need to review that space individually to ensure common path of travel and maximum travel distance. Both of these are measured to your closest exit. Since most of the time you will exceed your common path of travel, those occupants will require (2) exits.

Hope this helps!
Alex

Reply
Glenn Berger
12/16/2022 08:12:51 am

In addition to Alex's response, if possible ensure that all egress components are sized for the same number of occupants. By this I mean, do not size 1 exit for 50% of the occupants, 1 exit for 40% of the occupants, and the last exit for 10% of the occupants.

Reply
Jesse
12/16/2022 08:30:22 am

Glenn beat me to the follow-up point on Alex's response. The reason for this of course is that it is expected occupants will evacuate by using the means of egress furthest away from the hazard. Obviously, this applies to just the two means of egress also,

Reply
Todd E Wyatt
12/16/2022 08:52:37 am

Determining the Occupancy Classification(s) (OC) and if the building is protected throughout by an automatic sprinkler system (ASPS) are additional requirements when evaluating the Means of Egress (MOE).

The Building’s OC & ASPS determines the (3) maximum Travel Distances :
1. Common Path (2018 NFPA 101 Table A.7.6 & 2021 IBC Table 1006.2)
2. Exit Access (2018 NFPA 101 Table A.7.6 & 2021 IBC Table 1017.2)
3. Dead End (Corridors) (2018 NFPA 101 Table A.7.6 & 2021 IBC 1020.5)

As some of the other commentors have stated, the “loss” of 1 of the 3 required MOE shall not reduce the remaining available MOE capacity/width by less than 50% of the required MOE capacity/width.

Assembly OC require that the “Main Exit … accommodate not less than one-half of the occupant load” per 2021 IBC 1030.2 Assembly Main Exit.

The Codes (NFPA 101 & IBC) do not have additional prescriptive requirements in how a Life Safety Plan may “assign” occupants to individual MOE … this determination relies on the Design Professional & AHJ agreeing to a complaint MOE plan.

Reply
Norbert Soliva link
12/16/2022 05:58:27 pm

In addition to the aboved clarification, We need to satisfied tha code about the number of means of egress to meet the time to evacuate all the occupants of the buiding as 100 person per unit of exit width. Also include in our design the formula in the remoteness of each means of egress.

Reply
Chuck
1/11/2023 03:52:19 pm

Q. When the three means of egress are required per Section 7.4.1.2, does access to all three means of egress need to be provided to each occupant?
A. No. Large facilities with high occupant loads are required to have more than 2 exits from each story so at least one exit will be available in emergency situations and to increase the likelihood that a large number of occupants can be accommodated by the remaining exits when one exit is not available.
The life safety code specifies that the loss of one exit must not reduce the available exit capacity by more than 50% coupled with the requirement to provide a minimum separation distance between exits based on the diagonal dimension of the story or floor area to reduce bottlenecks and maintain egress flow
Equal distribution of exit capacity among all exits is not a code requirement but proper design is based on occupant load and capacity distribution to avoid dependence on one exit and bottleneck situations.

Reply
Steven Reilly
3/2/2023 02:26:28 am

So only 2 of the exits need to meet the exit separation requirements of 7.5.1.3, and there is no code requirement for the 3rd exit to meet the same remotness criteria? As a rule of thumb I try to ensure the 3rd exit is more than 45 degrees away at the end of the common path employing the UK regulations

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT