|
We have a sprinkler protected facility where we have a corridor that exceeds 50-ft in length.
At the end of the corridor is a door that leads to the apparatus bay. It's not a means of egress leading to an exit (higher hazard on the other side). The required means of egress are at other locations in the facility. Is this considered a dead end corridor under NFPA 101? In all the examples I've found on the topic, the end is truly dead-end with no means of exiting. What's your take on this? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Glenn Berger
6/18/2024 08:17:23 am
This question has a lot of buzz words that can lead to a response of yes to the question of is this a dead-end corridor. A floor plan with a compliancy write-up is required to ensure if the correct answer is given.
Reply
Greg
6/18/2024 08:28:06 am
The mention of an apparatus bay would give the impression personnel in the building would be familiar with the hallway. Similar to a fire station, possibly. The door arrangement and ladder may require signage as a component of occupational safety, to caution or warn of what is on the other side. If signage were on the door, would that improve the awareness of the corridor, and provide readable information ahead of the 50 ft distance?
Reply
Todd E Wyatt
6/18/2024 08:34:41 am
NFPA 101-2024 restricts Exit Access (EA) passing through “any intervening rooms other than corridors, lobbies, and other spaces permitted to be open to the corridor” per Chapter 7 Means of Egress.
Reply
Todd E Wyatt
6/18/2024 08:35:09 am
REFERENCES
Reply
Rick Sellek
6/18/2024 10:06:51 am
Todd E Wyatt’s response where he provides the enhanced content tells you everything. The dead end is measured when you pass the exit and no other exit is available from that point on. Your condition could just as easily be a residential occupancy with unit entry doors located beyond the distance limits set forth in the code.
Reply
Todd E Wyatt
6/18/2024 11:13:31 am
While the "ENHANCED CONTENT" from NFPA LiNK and the NFPA 101 Commentary can both aid in understanding the intent of the Code, AHJs (Authority Having Jurisdictions ... Code Official) are not required to enforce it (nor consider it) so use it cautiously. Recommend always confirming your interpretations with the AHJ (in writing).
Reply
Jack G
6/18/2024 11:08:05 am
Todd is spot on.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop Sept '26 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
October 2026
PE PREP SERIES |
RSS Feed
