MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Pumper Truck Required for Standpipe Testing?

3/2/2021

20 Comments

 
Is a pumper truck from the fire department required to do standpipe flow testing?

​​​​​​​​​​Sent in anonymously for discussion. Discuss This | Submit Your Question | Subscribe
20 Comments
jay richardson
3/2/2021 09:10:23 am

Assume you are asking in regards to a manual standpipe.
See Annex A of the current edition of NFPA 14 for alternatives.
You can use only hydrant pressure and then mathematically adjust the FDC inlet and HVC outlet pressures to demonstrate compliance with the standard.

Reply
Matt
3/2/2021 09:14:13 am

one time we had to rent a large pump on a trailer because the FD required a test, but refused to provide a pumper truck.

another AHJ we have worked with simply did the test to confirm that the piping was connected and un-obstructed. We opened the hose valves and flowed water from the city connection, but there was no flow/pressure requirement for the test.

Reply
Mike
3/2/2021 09:15:55 am

NFPA 25 6.3.1.1:

A flow test shall be conducted every 5 years on all
automatic standpipe systems to verify that the required flow and pressure are available at the hydraulically most remote
hose valve outlet(s) while flowing the standpipe system
demand.

Keyword is automatic. These are already connected to a water supply.

I've seen pumper truck used but maybe they don't want to deplete onsite water.

If a pumper truck is used, they may be testing manual systems if required by the AHJ.

Reply
Peter
3/2/2021 09:35:09 am

It's important to note that connected to a water supply doesn't necessarily mean the standpipe is 'automatic'. Most of us understand that a standpipe fed from a 3/4" line is just a manual wet standpipe (obviously not automatic). However, it can be challenging to determine if the standpipe is automatic or not if you don't have the plans. For example, an unsprinklered building that is 6 stories (less than 75') and has a class III standpipe may be an automatic standpipe but have flow rates equivalent to a class II standpipe per NFPA 14. That same 6 story building with a fire pump and fully sprinklered may have a manual class I standpipe. Performing 5 year inspections without having plans or a calc plate that says it is a manual standpipe or shows the flow rate required can be tough.

On a separate note, I have never seen a fire department require a contractor to use a fire truck to flow test the standpipe on a manual standpipe. Some do it themselves regularly, but I've never seen it as a contractor requirement.

Reply
sean
3/2/2021 02:13:39 pm

per NFPA 14 all standpipe systems need acceptance testing to match the calculated flow.

Reply
CJ Bonczyk
3/2/2021 09:19:54 am

Assuming the system is not automatic. 11.5.1 of 14 Ed. states to verify system demand, this can be waived by the AHJ. 11.5.2 For a manual standpipe, a fire department pumper, portable pump of a capacity to provide the required flow and pressure, or other approved means shall be used to verify the system design by pumping into the fire department connection.

11.5.2.1 Where allowed by the authority having jurisdiction,
the test required by 11.5.2 shall be permitted to be waived.

A.11.5.2 It is not always necessary to use a pump to test a standpipe system. See Figure A.11.5.2(a), Figure A.11.5.2(b), and Figure A.11.5.2(c) for examples of possible test methods.
Where using the method shown in Figure A.11.5.2(c), it is
necessary to flow the system demand while observing the pressures at the FDC inlet and the hydraulically remote standpipe hose valve. While the standpipe test might indicate that a greater pressure is required at the FDC inlet than what was indicated in the hydraulic calculations, this is not necessarily a cause for failing the test. This greater pressure, if acceptable to the AHJ based on the ability of the fire apparatus to provide the additional pressure, should be incorporated into the standpipe sign required at the FDC by 6.4.5.2.2.

Reply
Keith A Heckler
3/2/2021 09:24:22 am

A FD vehicle is not necessary but somehow you need to create the flow and pressure. The flow and pressure at the discharge needs to be measured. I have seen portable pumps on trailers used at the FD connection and, if a building has a fire pump, it can also be used.

Reply
Jesse
3/2/2021 09:49:30 am

Thankfully the AHJs in our area that require the flow testing also provide a Engine Co. to conduct the test. Without that, I guess we'd have to figure something out.

Reply
Mike
3/2/2021 10:19:01 am

Reference NFPA 14 for the definition of an AUTOMATIC system:

3.3.17.2 Automatic Wet Standpipe System. A standpipe system
containing water at all times that is attached to a water
supply capable of supplying the system demand at all times
and that requires no action other than opening a hose valve
to provide water at hose connections.

Reply
Mike
3/2/2021 10:21:06 am

Also reference testing requirements per NFPa 14:

13.1 General. A standpipe system installed in accordance with
this standard shall be properly inspected, tested, and main‐
tained by the property owner or an authorized representative
in accordance with NFPA 25 to provide at least the same level
of performance and protection as originally designed.

I understand AHJ may be different.

OP didn't specify system type. Just saying.

Reply
Jay Richardson
3/2/2021 11:41:10 am

System type doesn't matter for acceptance testing

Reply
Robert Bennett
3/2/2021 01:15:58 pm

System type does matter because an automatic standpipe must provide the 100 PSI residual without FDC support. IE High rise

Jay Richardson
3/2/2021 11:17:08 pm

In regards to when flow testing is required...system type does not matter for acceptance testing, all types are required to be flow tested....system type does matter for 5 year testing of existing systems, automatic systems are required to be flow tested whereas manual systems are not

JOHN M ERCOLANO
3/2/2021 11:46:38 am

We have been performing MWSD tests for the AHJ's and othe SPK contractors in NY for the last 8 years. We purchased a used fire pumper truck, 4- 2.5" hose monsters and hoses. At the top of the furthest SD install two- 2.5" FHV connections and a gauge run hoses out of the building and connect to the 2- hose monsters they must provide 500gpm @100psi. Repeat the same at the top of each other SD with one FHV, run hoses out of building to 1- hose monster, each of them must provide 250gpm @100psi. Connect the 5" suction hose from hydrant to the fire truck and multiple 2.5"hoses as required from truck to the buildings FDC connection. Adjust the RPM on truck and throttle FHV on SD until proper GPM@PSI is reached. 3men @ $4750/test paid upfront if working for another sprinkler contractor LOL.

Reply
Dave Sornsin
3/2/2021 10:04:56 pm

John E:

Great info. How close are the hyd. calcs to predicting what is actually required at the FDC?

In 30+ years I'd never been required by an AHJ to do one. Then I moved. Now in the last two years, I've done 4 new system acceptance tests. The first 3 were within 5psi of what I expected. I got cocky. The last one was way short and took 2 tries - first try shut down early due to communication & potential flooding issues, and then fire crew had to leave. Between attempts, I mapped out actual installed elbows/footages, plugged it all in to calcs, and was convinced it would be easy to achieve. It was 15-20psi off. Fire Marshal boosted the pumper truck, got the pressure/flows and signed off on it and we had a sign made to that pressure. We didn't have the time or manpower to dig further. What have you been seeing?


Reply
JOHN M ERCOLANO
3/3/2021 11:48:18 am

99% of the MWSD tests are on 4story or less buildings and the limit of the test is 1000gpm at 100psi, we have never fell shoot meeting the requirement since I can just rev up the pumpers rpm's and make pressure and flow. So far so good, most of the fire marshals are happy seeing 100psi at the top gauge and 45psi on the hose monster pitot gauge using 1-1/8"orifice. Good luck out there!

Jason
3/24/2022 09:32:50 pm

We are dealing with an engineer that is claiming the additional pressure added by the pumper truck is providing a pressure in excess 175 psi. We tried to explain that there isnt actually that type of pressure on the system because the system is open and flowing water. Is there something in the code that “exempts” this testing from the 175 psi limit? Similar to how a 200 psi hydro test doesnt create a problem even though it exceeds 175 psi? Any help would be appreciated.

Reply
Dave Sornsin
3/2/2021 10:42:49 pm

To answer OP: Since Mr. Ercolano and truck are on the other coast, we use the FD's pumper truck and crew. Some FD's charge, others do it for free. We have HM's, calibrated gauges, rent a ton of hose, and have at least 6 people on site for valve spinning and gauge reading.

Reply
JOHN M ERCOLANO
3/3/2021 11:33:49 am

Most of the FD will not perform this test do to liability issues.

Reply
Jordan link
3/9/2021 03:16:56 pm

In my locale for a manual standpipe I have only seen a requirement for a visual requirement on an annual basis. There is also the 5-year requirement for a flow test. For the flow test I will reach out to the AHJ and explain my role as a facility's <a href='https://www.fireprotectionlincoln.com/'>fire protection</a> contractor and ask if they will bring a truck on site while we are there.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT