In an existing building utilizing a “booster pump” or unlisted fire pump for a standpipe or sprinkler system, is there a suggested annual flow test procedure?
I realize there is no manufacturer’s data (0%,100%,150% rated capacity) to compare the results against. Should it be excluded from the annual flow test requirements, and just flowed during the 5 year roof top flow? I would appreciate input as well as, what others in the industry are doing to address this fairly common scenario. Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe
4 Comments
Franck
9/11/2020 10:30:32 am
If there is no historical data, you can at least compare to the pump nominal point.
Reply
Peter
9/11/2020 10:46:24 am
The best I've ever been able to come up with is to have a conversation with the AHJ. I've seen some pretty bizarre "fire pumps" where it is part irrigation pump, part fire pump, etc. In some instances the AHJ asks we put a pitot on it to just capture as much water flowing at as much pressure as it can output. In other instances, the AHJ has looked back at historical records and given the original design data to which we can then test from. In other instances, we've had to calculate the system and then determine if the pump can achieve the demand. In a lot of instances the demand that was needed 50 years ago may be different than what is required per NFPA 13/14/etc. today, so having that conversation with the AHJ is important. From that point forward you can use that data to compare against to determine if performance degrades.
Reply
Brian Gerdwagen FPE
9/14/2020 09:32:40 am
An unlisted booster pump, assuming that you mean a jockey pump, does not require a listing and does not require testing. As said above, you can start flowing the pump and recording data to compare to later tests.
Reply
Peter
9/14/2020 11:22:03 am
I believe the original post was in regards to using an unlisted pump as the main 'fire pump' of the fire protection system. I have personally seen this a number of times on older buildings.
Reply