|
I have an inspection question regarding quarterly checks on low air supervisory devices on dry systems.
Is it okay to simply "jump off" the device when not doing a full or partial trip to simply make sure it hits the panel? I feel like I'm doing a disservice inspecting using this method, but I've seen it a lot. Unfortunately for me, it's been a crapshoot lately on what dry valve is going to go haywire when I drop air via an Inspector's Test Valve or at the riser. I'm thinking of just recommending a bleeder valve to be installed and go the easy route, saving both myself and customers a lot of anxiousness. Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
9 Comments
Mike
5/5/2020 10:14:37 am
I'm sorry. Could you explain jump off?
Reply
I’m assuming that “Jump Off” means placing a jumper on the low air switch contacts to see what the fire alarm panel will do if there’s a low air situation. It doesn’t show if the switch is set correctly, or even if the switch works.
Reply
Justin
5/5/2020 10:32:29 am
I think i understand 'jump off'.
Reply
Jumping (if I understand what you mean by that phrase) equipment during an inspection is not proving the equipment works in "normal" condition.
Reply
Thomas Reinhardt
5/5/2020 11:23:22 am
I might be wrong here,but I would follow NFPA 25. Sound like a liability problem.
Reply
Pete D.
5/5/2020 11:45:44 am
Trip pressure, low air supervisory, compressor on pressure. The thresholds should be set up from low to high in that order. Close the dry system control valve to prevent accidently tripping. Check that control valve supervisory signal comes through at the panel. Before reopening it, bleed air from the compressor tank and verify that the compressor kicks on with no corresponding low air supervisory signal at the FACP. Turn off the compressor and continue to bleed air from the compressor tank verfiying that a low air supervisory signal comes through and that the corresponding pressure is higher than the system trip pressure.Turn the compressor back on and wait until the system is fully pressurized. Open the system control valve and confirm that the system supervisory signal restores. Warm reset panel and take monitoring off of test.
Reply
Wes
5/5/2020 11:57:38 am
Wow, well said Pete!
Reply
Pete D.
5/6/2020 10:26:06 pm
Thanks. It's not outside of the realm of possibility that the poster inspects at one of my 103 buildings, and I'm paying him for the jumper service.
Mike F
5/5/2020 01:07:32 pm
Unless the codes have changed, I believe the QOD/Accelerator is also required to be tested during a quarterly inspection as well.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop Sept '26 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
October 2026
PE PREP SERIES |
RSS Feed
