MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Maintenance for Jockey Without Main Fire Pump?

6/25/2020

9 Comments

 
Does anyone have any pressure maintenance pumps installed on their sprinkler systems without having a fire pump?

In other words, having a pump on the sprinkler system that is only there for the purposes of preventing a false alarm (due to pressure ebbs and spikes in the water supply) instead of boosting the water pressure like a traditional fire and jockey pump combination.

We have some legacy jockey pumps installed like this and it runs into a grey area for maintenance as they don't affect the performance of the sprinkler system they are connected to. Any thoughts?

Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe
9 Comments
Connor Ross
6/25/2020 10:09:31 am

On legacy systems, I've always seen this handled using a retard chamber in between the sensing line and the water gong. In modern systems, a delay can be programmed in for a flow switch to prevent nuisance alarms from pressure fluctuations. If you can put in a new flow switch, wouldn't it be easier than maintaining a jockey pump?

Reply
LC
6/25/2020 10:17:42 am

We have a client with a lot of these (on a campus of multiple buildings). I'm not sure what they are doing for maintenance, but they are working on changing them out to flow switches with a delay as Connor suggested.

Reply
Matt
6/25/2020 10:27:12 am

Are you sure what you've got is a jockey pump and not an excess pressure pump? It's very common for pressure maintenance of wet systems. Most common setup in USA and Canada in my experience is an Albany 1/3HP with a pressure relief valve. They can be set up to run both automatically off a pressure switch and manually.

Reply
VC
6/25/2020 10:34:23 am

The only time I have ever seen them is in a older mall with an 8" lead-in for each building serving pipe scheduled systems. As far as maintenance, as long as the excess pressure pump works how it is supposed to we leave them installed.

This mall is in an area where the water purveyor booster pumps take a while to kick on. So if we walk away from a system with whatever city pressure is available, we may have an alarm hours later after the booster pumps fire up and add the 20psi(rough guess). With that being said, replacing with a time delayed flow switch isn't an option.

Reply
Cliff
6/25/2020 12:34:01 pm

We used to call that a Watchman. It was made by Gamewell and was common 20-30 years ago. Haven't seen too many installs lately though.

http://firealarmresources.com/wp-content/uploads/2013/07/Gamewell-Sprinkler-Watchman.pdf

Reply
Matt
6/25/2020 01:52:21 pm

I swear I'm not a crazy person! I've installed quite a few in the last few years, and replaced a bunch of them too - I didn't do the one in the one photo - but it's the standard automatic setup I mentioned above with a low pressure switch connected to the fire alarm system (Potter PS120) and a pressure switch to control the EPP (Potter PCS300)

Hopefully the photo link works!

https://imgur.com/a/M9XS9D1

Not sure if this is what the OP was referring to but here it is!

Reply
Jonathan Joseph
6/25/2020 05:23:31 pm

I would treat the pumps as a pressure switch and an alarm device and would inspect the pumps quarterly and test annually. If impaired I would replace it with another pump that is rated the same so it is restored to its original design.

Reply
Bruce Verhei link
6/29/2020 07:28:43 pm

Excess pressure pumps are the gold standard for preventing unwanted alarms caused by pressure surges in wet sprinkler systems.

Excess pressure pumps are required for wet systems in Vancouver B.C. (and the rest of B.C?) and New Zealand. They are sometimes used throughout on campus water systems that are based on pumped systems. You don’t want alarms from half a dozen buildings when the first big pump kicks on.

In my city an excess pressure pump was most likely a sign of one of two things.

Even after adjusting the retard out to 90 seconds the system was generating false alarms due to pressure surges.

or

At least one of the sprinkler systems was being used as detection system as part of an alternative method and material solution.

An example: Building operator wants to use more than exempt quantities of a flammable liquid from an intermediate bulk container to support a paint spray operation. Bulk container and spare is located in an H room. Before piped product leaves room it passes through an excess flow valve, sometimes called a liquid fuse and a normally closed valve held open by solenoid during operation. The sprinkler heads and flow switch are the fire detection system for the solenoid. The flow switch is set to 0 or 5 seconds. Solenoid is depowered and valve closes quickly on head operation. Jockey pump is needed to prevent unwanted alarms with this near instantaneous activation, while ensuring only the flammable liquid in the pipe is available to spread fire.

Purchase of a new 1-gpm pump is likely cheaper for the business operator than shutting down their normal operations, even once, because the alarms went off. What is shop fee for all their employees for a quarter of an hour compared to pump cost?

Best.

Bruce Verhei

Reply
Julie
11/7/2023 04:36:57 pm

Hey everyone, this thread is a few years old but still helpful. I just wanted to add this YouTube video onto this post because I am researching these excess pressure pumps and found it extremely helpful.

https://youtu.be/9urpPzmsxHo?feature=shared

This guy does a fantastic job of explaining how it works with an alarm valve.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT