Elevator Lobby, Draft-Curtains Req'd in NFPA 101?

3/6/2023

5 Comments

 
I have a new construction 5-story residential (dormitory) being constructed under UFC.

The architect inquired if lobbies need to be provided for the elevators, and, if not, do smoke protection (draft-curtains) need to be provided?

My immediate thought was of course, something needs to be provided. However, when I follow the code track of NFPA 101, it is not exactly clear in comparison to IBC.

The IBC is very clear, Section 3006 regarding the protection of hoistway openings.

Without going through the entire NFPA 101 code-track here, we end up back at NFPA 101 Chapter 8. Section 8.5.3 states a fire barrier can be used as a smoke barrier, provided it meets the requirements of Section 8.5. Hoistway openings, specifically elevator doors are not specifically mentioned in NFPA 101 Section 8.5. The only thing I can point to is Section 8.5.2 Continuity and Section 8.3.5.2 Joint Systems for Fire Barriers.

Other items: The hoistway is to be protected with a 2-hour fire rating, which requires the elevator door to be 1.5 hour rated (Section 8.6.5), and the building is protected throughout with automatic fire sprinklers, including the elevator shaft.

By definition, the building is not considered a high-rise. The hoistway height is ~57 feet.

​What are everyone's thoughts on this?

Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments
Todd E Wyatt
3/6/2023 09:10:50 am

I recommend clarifying with the Design Professional what the adopted Code(s) (IBC? NFPA 1? NFPA 101?) the project is required to meet ... “UHC” is no longer maintained :

“When referring to the Uniform Fire Codes (UFC), it needs to be clarified (with the Authority Having Jurisdiction AHJ) which fire code release needs to be applied to achieve compliance: Some states and municipalities adopted the Uniform Fire Code from NFPA, also known as NFPA 1, while others adopted the Uniform Fire Code released by ICBO. Since the creation of the International Code Council (ICC) in 1994, the uniform fire code is no longer maintained (last release in 1997) and superseded by the subsequent releases of the International Fire Code (IFC) published by ICC.”

The (scoping) Code will determine the IF the hoistways are required to be protected and HOW they are to be protected.

The 5-story dormitory protected by an automatic sprinkler system (ASPS) would be classified as a Residential Group R-2.

Per 2021 IBC 3006.2, this hoistway is required to be protected since it “connects more than (3) stories.” The hoistway protection would consist of either ...
1) An enclosed elevator lobby at each story separated from adjacent spaces with 0-Hour Smoke Partitions (0SP) since the building is protected by an ASPS, or
2) Smoke and Draft Door Assemblies (meeting 716.2.2.1.1) at each elevator door opening, or
3) Pressurized elevator hoistway.

Chapter 10 Means of Egress includes additional elevator lobby requirements (e.g. Identification Signs) if this option is used.

“Draft Curtains” and closely spaced sprinklers are prescriptive requirements for certain “floor openings” (IBC 1019.3(4)) and escalators (712.1.3.1) but are not used for the protection of the hoistways, as per 2021 IBC.

REFERENCES
2021 IBC
Chapter 30 Elevators and Conveying Systems

2021 NFPA 1 : No prescriptive requirements for “hoistway protection”.
“Hoistway” = (10) references
Chapter 12 Features of Fire Protection
12.4 Fire Doors and Other Opening Protectives.
A.12.4.1.3
For requirements on the installation of hoistway doors for elevators and dumbwaiters, see the applicable sections of ASME A17.1/CSA B44-2016, Safety Code for Existing Elevators and Escalators, or ASME A17.3/CSA B44-2015, Safety Code for Existing Elevators and Escalators. [80:A.1.1.3]
12.4.2 Care and Maintenance of Fire Doors and Other Opening Protectives.
12.4.2.8* Inspection and Testing.
12.4.2.8.2.4
A record of all inspections and testing shall be provided that includes, but is not limited to, the following information:
A.12.4.2.8.2.4(9)
To aid the AHJ during the review of the inspections and testing reports, the records should include a description of the type of fire door assembly as follows:
Type 14: Hoistway doors for elevators and dumbwaiter
“Draft Curtain” = (0) References

2021 NFPA 101 : No prescriptive requirements for “hoistway protection”.
“Hoistway” = (25) references ... Chapters 7, 8, & 9.
Table 8.3.3.2.2 Minimum Fire Ratings for Opening Protectives in Fire-Resistance-Rated Assemblies and Fire-Rated Glazing Markings : Elevator hoistways ... 2, 1, or 0.5 Hours
“Draft Curtain” = (0) References

Reply
Dwight H Havens
3/6/2023 09:43:15 am

I'm thinking that the UFC being referred to is the Unified Facility Criteria developed by the Department of Defense, which for construction specifies the use of the International Codes for construction, except that NFPA 101 be used for egress requirements.

Reply
Question Submitter
3/6/2023 09:55:28 am

Dwight - You are correct.

Todd - My apologies. I should have clarified. This project is being constructed under Department of Defense UFC (Unified Facilities Criteria)

In accordance with UFC 3-600-01 Section 3-3.1.1 NFPA 101 must be utilized to determine the occupancy classification as it relates to fire/smoke resistance rating of interior non-load bearing partitions (other than occupancy separation), means of egress, interior finish, features of fire protection (including vertical openings) and associated requirements.

Reply
Todd E Wyatt
3/7/2023 08:19:58 am

Since the 2021 NFPA 101 does not include prescriptive requirements for “hoistway protection” as the IBC does, the fire-resistance rating (FRR) of the shaft enclosure would need to meet 2021 NFPA Chapter 8 Features of Fire Protection and Chapter 28 New Hotels and Dormitories ...

8.6 Vertical Openings.
8.6.5* Required Fire Resistance Rating.

28.3 Protection.
28.3.1 Protection of Vertical Openings.

... but the "hoistway protection" is not required.

Reply
Question Submitter
3/7/2023 09:13:40 am

Todd - Correct. We arrived at a similar conclusion. We will be providing a 2 hour rated elevator hoistway based on the requirements of 8.6.5 and 8.3.3.2.2.

The FPE in me finds it odd that a 2 hour fire-rated shaft is required. However, smoke protection regarding the hoistway door opening is not specifically identified. Appears the emphasis is placed more on the fire-resistance and less on the smoke-resistance.

The only code sections I can identify that would possibly address this are previously mentioned: Section 8.5.2 Continuity, Section 8.3.5.2 Joint Systems for Fire Barriers, and Section 8.3.3 Opening Protectives.




Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Oct '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 88A
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    November 2026
    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT