MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Exterior Access for Sprinkler Riser Ever Required?

9/1/2022

11 Comments

 
Is there a situation, other than a fire pump room, where a sprinkler riser room would be required to have direct access to the exterior?

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments
Dan Wilder
9/1/2022 08:00:07 am

When the AHJ requires it.

I guess I need more clarification on the question like are you trying to argue or justify a location?

Many time this is written into the adopted building/fire codes and is subject to what they feel is considered "Ready Access" or "Readily accessible"

IBC Section 902.1.1 "Automatic sprinkler system risers, fire pump and controllers, shall be provided with ready access"

Reply
Christopher Nichols
9/1/2022 08:13:51 am

The local jurisdictions usually will require an exterior door to the riser room if the building is going to be multi-tenant occupied like a retail strip center.

Reply
Franck
9/1/2022 08:17:01 am

There is no such requirement in NFPA 13.
But it is a good practice to have a direct access to the riser so that in case of fire within the building the control valve remains accessible.
Best practice is even to have a Post Indicative Valve located away from the building (40 ft), so that even if the building collapse you can still access the valve.
Worst practice is to have the valve in the basement or at an elevated level as it might be difficult to access it in case of fire inside the building.

At the end, as indicated by Dan, this is mostly a decision from the AHJ. Or it may be governed by internal rules for an Industrial group, or the insurance company (FM Global, for example, is quite restrictive for the location of such valves).

Reply
Alex
9/1/2022 08:38:13 am

As far as I know, there is no such requirement within NFPA 13. As others stated above, its good practice.

Reply
Wayne Ammons
9/1/2022 08:41:37 am

I find this extremely ironic because a fellow designer asked me this exact question yesterday and did not make this post himself. In his situation, the riser is being proposed to be installed inside an interior janitor's closet.

Reply
schulman
9/1/2022 08:41:42 am

i tell my architect clients its required.
shhh. dont spoil it for me.
its right for so many reasons.

Reply
Casey Milhorn
9/1/2022 08:43:06 am

Great question. This is one of those that you find a designer that's been on the job 1 day asking about, but also someone that may have been designing for 30 years not really understanding. They just know what certain AHJs want and/or follow the design intent and civil drawings. It also is one of those items that doesn't get coordinated very well between civil engineer and mechanical engineers sometimes.

Below is from NFPA 24, 2013 edition (check your applicable edition, but I don't think this has changed recently).

I believe in earlier editions, it said something about this list of valve locations being in a preferred order... but I don't know if that's my imagination or maybe something I read in some other text or handbook. BUT, this is the order that I go by, and it makes the most sense for the safety of the fire fighter (at least to me).

See option #6 as one of the acceptable methods for access to the control valve.

6.2.11 All connections to private fire service mains for fire
protection systems shall be arranged in accordance with one
of the following so that they can be isolated:
(1)*A post indicator valve installed not less than 40 ft (12 m)
from the building
(a) For buildings less than 40 ft (12 m) in height, a post
indicator valve shall be permitted to be installed
closer than 40 ft (12 m) but at least as far from the
building as the height of the wall facing the post indicator
valve.
(2) A wall post indicator valve
(3) An indicating valve in a pit, installed in accordance with
Section 6.4
(4)*A backflow preventer with at least one indicating valve not
less than 40 ft (12 m) from the building
(a) For buildings less than 40 ft (12 m) in height, a backflow
preventer with at least one indicating valve shall
be permitted to be installed closer than 40 ft (12 m)
but at least as far from the building as the height of
the wall facing the backflow preventer.
(5)*A nonindicating valve, such as an underground gate valve
with an approved roadway box, complete with T-wrench,
located not less than 40 ft (12 m) from the building
(a) For buildings less than 40 ft (12 m) in height, a nonindicating
valve, such as an underground gate valve with an
approved roadway box, complete with T-wrench, shall
be permitted to be installed closer than 40 ft (12 m) but
at least as far from the building as the height of the wall
facing the backflow preventer.
(6) Control valves installed in a fire-rated room accessible
from the exterior
(7) Control valves in a fire-rated stair enclosure accessible
from the exterior as permitted by the authority having
jurisdiction

But to answer your question, it depends on the AHJ. What we see most often is they would like to have a yard PIV first, wall PIV second, and exterior access to the riser room third (all increasing in risk to the responding fire fighters). A lot of AHJs will not allow the other options. I can say I've never seen an UG gate valve provided with a T handle wrench just sitting there for fire department use.... that always seemed like a weird option to have in the list.

Reply
Jesse
9/1/2022 08:47:37 am

Every situation for every AHJ in the Austin, Texas metro area. Every riser room must have direct exterior access.

Reply
Dave
9/1/2022 10:50:59 am

In my area it is as others have said, it depends on he AHJ. As I assist the architect in design development, it is one thing I have to know or confirm. Whether it is written in the city or county ordinance or not, many of my local AHJ's require outside access or an outside PIV (sometimes a minimum distance from the structure). Some require both. Some require neither. One large local city is even okay if the riser located in the basement. I also make sure the architect keeps my riser room at an exterior wall so as not to exceed the 10-ft. maximum of underground, and to allow discharge of main drains if they are to be directed to the exterior..

Reply
Manny Rios
9/1/2022 11:58:36 am

In our jurisdiction, most if not all of the buildings are schools. All of the fire risers rooms are designed/built with direct access to the exterior of the buildings per contract documents.

Reply
Donnie Brewer
9/6/2022 01:57:17 pm

You can use the International Fire Code 2018 Edition section 504.1 required access exterior doors and section 509.2 Equipment access to get an approved exterior door for the sprinkler riser room.

Donnie

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT