MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Hydraulic Calculations Required for Each Zone?

7/24/2020

13 Comments

 
I need an answer for a simple question. I am working on a large airport project expansion. I have a structure of 4 levels with 70+ sprinkler zones.

Is there an NFPA standard requirement stating that each area requires a hydraulic calculation on each system?

Each system is not prototypical.

​​​​​​​Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe
13 Comments
Glenn Berger
7/24/2020 10:13:14 am

Since each system is not identical, separate calculations would be required.

Are you trying to size piping identically? Are the spaces the same hazard categories?

Reply
Jessica L.
7/24/2020 10:42:00 am

An experienced sprinkler plan reviewer should be ok with you submitting one calc per hazard/sprinkler k-factor/system type/pipe size arrangement. ****Be sure you have the knowledge and experienced to make this judgement, and defend it!

Also, check with the airports' submittal requirements...some airports are managed by various parties, with unique requirements specific to each airport...they could possibly required a calc for each zone, or have other special requirements that go beyond NFPA 13.

Reply
Ivonn
7/24/2020 11:06:19 am

I dont have a simple answer maybe no, are there 70 zones or 70 systems?, all zones have the same hazard? What are the most critical pipe configuration?, What is the critical path? What is the most remote or high vs the supply? You need to consider that questions and make a decision

For example in the 4th floor have 3 zones but the farest from supply its a light hazard and the nearest its an extra hazard, the two in a tree pipe configuration, personaly I will calculate the extra hazard or if the farest part is a grid system and the nearest is a tree, tree its more "critical" but I want to choose the lower diameter possible so I will calculated both.

If you have multiple ocupancies (LH,OH,EH) and multiple pipe configurations (Grid, tree, loop), maybe you need to do several hydraulic calculations, but maybe no 70+

Also you need to consider what the AHJ required, NFPA 13 Ed. 2019 do not required one hydraulic calculation per "zone" or per "level" as far as I know.

Reply
CJ Bonczyk
7/24/2020 11:42:42 am

If the systems are not entirely identical in layout I strongly recommend doing the calculations to indicate the hydraulic capability of each zone. For instance if a remodel happens within an area on a specific floor there is no way in determining the hydraulic capability of the system installed. Occupancy changes, building remodels or MIC issues, can alter system capability within a year or two. If something happens from a legal standpoint you have documentation to fall back on on how the system area was protected and why. These placards are usually required on each by the fire marshal anyway. NFPA 13 2019 Handbook Section 28.5 gives a clearer reason why these should be placed on each system.

The only time in which I have used the same hydraulic placard for corresponding floors is if I had an exact layout for multiple floors and I calculated the highest floor and used the same hydraulic plate for the lower floors and denoted on the lower floor placards that the information was based on the hydraulic capability/demand of the highest floor.


Also as Jessica stated earlier confirm with the airport that there is no insurance carrier that will require calculations for all systems.

Reply
Jesse
7/24/2020 12:43:40 pm

If by zone you mean system, then yep, each system needs to be proven. Its most acceptable proving the end-head back to the residual hydrant as opposed just to base of riser so even if each system were identical, the distance from BOR to residual hydrant would be different. If its a single system with multiple zones, the most hydraulically remote would be all that's needed but be prepared to defend your logic. And totally agree with a previous comment about proving multiple areas in case of a future remodel. I rarely sign a drawing with only one area calc'd unless it's very small for that very reason.

Reply
Franck
7/24/2020 03:20:22 pm

Working for an insurance company, I can confirm what has been said.
As a minimum, one hydraulic calculation per different system (as all results might be slightly different, and we are looking for « actual design ».
In addition, if different hazards/configuration on one system, we may ask several calculations to be sure that all configurations are adequately covered.
This is particularly true for EH occupancies or for different storage commodities/arrangement

Reply
Jimmy Landmesser, Jr.
7/24/2020 04:44:17 pm

So, first what you mean by "zone" would need to be understood.
As stated above, there are two main reasons that a single building requires multiple design calculations- 1) multiple systems serving said building or 2) when you there are different design bases (also called occupancy hazards) present. As others have said, only a single design calculation is required for the most remote area of a single system or design basis, even if multiple floors are fed from a single system. Each floor will normally have a zone control valve. On the other, there are sometimes different "zones" on a single floor that each have a different design basis. For example, a building that has offices that are light hazard, an automotive garage of ordinary hazard and high rack storage that is an extra hazard occupancy. Though a single system of a one-story building, each of these areas will require an independent design calculation.

As for reference, per NFPA 13 (2019)- 19.2.3, "the total system supply requirements for each design basis shall be determined in accordance with the procedures of Section 27.2 unless modified by a section of Chapter 19 or Chapter 20.".

Reply
Max
7/24/2020 05:07:39 pm

I would ask for one remote area calculation per riser at a minimum.

Reply
Mike
7/24/2020 07:52:03 pm

Considering the simplicity of today's CAD systems, it's relatively easy to calc many areas in a short amount of time. I'd do a detailed analysis of your different systems. If you use area reduction in some areas but not others, I wouldn't expect those designs to be used in areas where area reduction isn't a factor.

Reply
SK
7/25/2020 03:47:24 am

The basic of all calculations are there to demonstrate your decision against Code/AHJ and justify your design, in this case is NFPA 13. There is no hard and fast rule for this. This is just subjective. So i would suggest performs as much as cals to covers as below;

-Demonstrate you get water with adequate pressure at FARTHEST location
-LARGEST DEMAND Area (Consider Occupancies w.r.t. levels/zones)
-WORST Case, which will decide your system sizes at the end.

So based on my limited knowledge about Airport structure, probably 12-15 calculation for difference Occupancies/Area should serve the purpose but certainly not 70+....

Reply
koray uluc link
7/26/2020 05:18:54 am

According to NFPA 13 if you design systems with hydraulic calculation method then you should run a calculation for all of them according to NFPA13 27.2.4.1
Sometimes AHJ may ask (in my point of view, should ask) for additional calculations to be sure that designer did choose actual "most demanding area"(NFPA13 A.27.2.4.7).
Don't forget that sloped ceilings and grid type piping makes hard to find the most demanding area at first attempt.

Reply
Hassan
10/23/2020 05:06:43 am

I have Grid Network of piping with extra hazard. The area is covered by 1800 Sprinklers, normally distributed through out the space with the 9 sqm/sprinkler. in order to select the size of the pump what is the criteria to decide the number of sprinklers that will be operating together in order to verify the water flow rate.

Reply
Hassan
10/26/2020 09:28:19 am

Thanks for your valuable feedback really appreciated.
I truly have four ZCVs each of them cover separate zone with 450 Sprinklers
in order to run my hydraulic test how many Sprinkles in the critical path will be included in my calculations our of 450 connected to the ZCV this figure will lead me to decide the GPM for the pump and accordingly to decide head.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Oct '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 88A
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    November 2026
    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT