MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Sprinkler Main Larger than Underground Size OK?

7/14/2020

15 Comments

 
Have a situation I've never crossed before: we have a very small building that's getting expanded. Originally the sprinkler contractor gave two options for the general contractor to price their underground fire sprinkler service - (1) is to provide a 2-1/2" main, the other (2) is to provide fire barriers in certain areas with automatic door closers to allow the room design method be used, and bring in a 2" underground.

I completely recognize that small underground pipe is not good practice and limits the future potential of the building. We recommended a 4-inch underground, but the increased cost for tap fees and underground pricing added $10-15,000 to the job which the owner adamantly refused.

We were given notice to proceed with 2-1/2" underground and thus provided a 2-1/2" riser and 2-1/2" mains. 

The GC gave a different direction for the underground and pulled 2" underground and is providing fire barriers and automatic door closers.

We've recalculated using the room design method and everything still works with the 2" underground, but the 2-1/2" riser and 2-1/2" main is already ordered and on the way to the jobsite.

Does NFPA 13 have any restriction against having a larger riser or main size than the underground?

Because of the change in building construction, we only need a 2" riser and 2" main but will instead already have prefabricated 2-1/2" in both. My thought is to have a permanent placard clearly affixed to the riser showing the situation and clearly identify on as-builts the methodology used.

​​​​Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe
15 Comments
Jesse
7/14/2020 10:09:50 am

You have a problem.

The lead-in can not be smaller than the riser. Typically, underground can not be smaller than 6-in, but 13 makes a provision for smaller if A) no hydrants are attached to it, and B) it is no smaller than the riser.

I wouldn't stamp that drawing. Sorry, I know that's not what you hoped to read

Reply
Dustin
7/14/2020 10:22:34 am

Please provide code reference.

Reply
Jonathan Sullivan
7/14/2020 10:28:34 am

Regarding provision "B)",13-16 24.1.3.2 (2) only adds the not smaller than the riser provision if the system is not hydraulically calculated.

Reply
TC Lambert
7/14/2020 10:32:06 am

Being curious, as I have come up against situations like this here and there, I looked at NFPA 13. This limitation on the UG pipe size being at least as large as the riser is only for pipe schedule systems. If it can be proved by hydraulic calcs that the system demands can be satisfied you should be fine. That being said, I don't like the small UG size either. Since the GC has stacked the deck against you, I would push for an ample safety factor to be included in those calcs.

Reply
SUBMITTER
7/14/2020 10:34:23 am

Section 24.1.3.2 (2) is saying that the underground is at least as large as the system riser. That's only for pipe schedule systems - this system is hydraulically calculated.

Also, there are no hydrants connected to it and it is a dedicated sprinkler feed (no domestic).

SUBMITTER
7/14/2020 10:41:10 am

I wouldn't sign/seal the drawing either - if it wasn't code allowed.

The question (at least in my mind) isn't whether it's good practice to have an underground that's smaller than a main. It's not good practice and it doesn't lend itself to future building changes.

The question to me is whether it's allowed by code, and if hydraulically it can suppress a fire under the NFPA 13 standard.

As far as I can tell, despite the pickle the GC has us in, is that it would be allowed by code and does work hydraulically.

Ironically, if the main and riser is all 2-inch instead of 2-1/2-inch, then this discussion kind of goes away and the whole thing starts to look more traditional. That CAN actually work in this situation hydraulically - it's just that we already have the pipe cut at the larger 2-1/2 inch size. It's a goofy arrangement, no doubt, but being unconventional here really is only helping the situation hydraulically.

With the Room Design Method, 2-inch underground, and 2-1/2 inch main, we're sitting at a 12 psi (19.6%) safety factor.

Reply
Rusty Scott
7/14/2020 10:15:49 am

I've seen this before with warehouse risers where 6" underground is provided but in order to make the calc's work, a 8" riser is used and then sometimes transitions back to 6" on the horizontal. This would be the difference in bumping up the branch lines over the gridded system which is $$$. So I believe it is allowed due to code not explicitly stating against it (at least I haven't seen a code against it, doesn't mean it's not there), I believe it's more or less just not considered best practice.

Sounds like you have a fun G.C.

Reply
Jesse
7/14/2020 10:23:43 am

Your situation would be allowed, because of the 6" main. That's the minimum size allowed.

In the OP situation, the underground size is 2". This is only permissible if the system riser is 2" also and there are no hydrants on that lead in

Reply
SUBMITTER
7/14/2020 10:35:02 am

Correct - no hydrants on the lead-in, hydraulically calculated, no domestic flow either.

Colin
7/14/2020 01:03:51 pm

Jesse, this is a hydraulically calculated system with no hydrants. Please provide the code reference where it states that the riser must be the same size as the underground. I believe that's only for pipe schedule systems. While its not "best practice", I'm not aware of a code prohibiting what the OP is asking.

Nic
7/14/2020 10:27:15 am

NFPA 13 2019ed 5.1.3.2 says the incoming fire main can be less than 6" if the incoming main is at least as large as the system riser. So currently you have a problem if your riser is 2-1/2" and incoming main is 2"

But I could technically see a loop hole if you made your system riser 2" and overhead feed main 2-1/2". Not sure if your calcs would work with that.

Reply
SUBMITTER
7/14/2020 10:36:33 am

Even the 2019 section you've referenced, though, is only fir pipe schedule systems.

5.1.3.2(2) "Systems that are not hydraulically calculated shall have a main at least as large as the system riser."

This project is hydraulically calculated, and with the room design method in NFPA 13 it works with the 2-inch underground and 2-1/2" mains.

Reply
Nic
7/14/2020 10:50:23 am

Ah good point. Not sure how I missed that. I don't see where you it says you can't do what you have planned then.

KN
7/14/2020 10:46:49 am

It's common around here to tap the city main with one size, and then to upsize the pipe after the water meter. For example, you could tap the city main with a 2" pipe and then after the meter, upsize the underground to 2½" pipe or 3" pipe (depending your system demand). This obviously has an effect on your hydraulics, but if you can figure out a way to make the calcs work, there technicially isnt any problem with this.

Reply
SUBMITTER
7/16/2020 07:34:29 am

KN - just out of curiosity - do the hydraulic calculations typically accurately reflect the loss through the water meter and smaller tap?

I rarely see water meter losses accounted for, then again around here its uncommon to have fire flow through the meter.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT