Why Does a Hydrant Need a Control Valve?

7/10/2020

9 Comments

 
NFPA 24, Section 7.1.1.2 (2016 Edition), states that control valve shall be installed in each hydrant connection.

What is the purpose of this control valve, other than facilitating maintenance?

Would this be considered a "control valve" per NFPA 24 3.3.3, and does this have to be a post-indicating type valve?
Picture
​Common hydrant arrangement for illustration purposes.
Based on my limited understanding, this control valve is just a post-indicator valve/isolation valve which is for shutoff when there is an impairment downstream. I'm trying to get a better understanding of its purpose. Thanks in advance.

​​​Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe
9 Comments
Jesse
7/10/2020 10:08:19 am

Its primarily for maintenance. And it doesn't necessarily need to be a PIV. I use NRS (non-rising stem) valves most often

Reply
Brian Gerdwagen
7/10/2020 10:38:17 am

This is also to turn off the hydrant after being hit by a vehicle. Some jurisdictions, like Los Angeles County, require that the control valve be a decent distance, like 15 feet, away from the hydrant for this purpose.

If the hydrant were to leak, need to be replaced, et cetera. So yes, impairment downstream. And a PIV would just add one more thing that could be damaged.

Reply
Sue
7/10/2020 11:11:27 am

We do not require a PIV at this control valve because the hydrant is so close. If the hydrant is not live, a street key can be used to open the valve.

We do require a PIV if there is more than one hydrant controlled on the same line, then each hydrant would also have their own street valve so the hydrant can be worked on without closing down all of the others.

Reply
Jimmy Landmesser, Jr.
7/10/2020 11:22:25 am

As stated previously, yes maintenance is a key component and the other being repairs. The intent is to avoid impairing more than that single hydrant when repairs or maintenance are needed. No, a PIV is not required.

I support a Dept. of Energy national lab and we utilize PIVs for the hydrants, but it is because our local FD conducts IT&M for the fire suppression systems on site. Our FD likes to be able to see the site glass and ease of a PIV over curb valve. Most of our hydrants and PIVs are away from streets in the "yard" near the facility It is not an issue since aesthetics are less a priority and vehicular damage are not common with light traffic to begin with but no traffic in the grass.

Reply
SK
7/10/2020 12:17:31 pm

Thanks for all responses.

Yes, I agree it's required for maintenances but adding another ordinary isolation valve (not PIV) for each hydrant connection specially where number of PIVs are already provided on it's mains to segments the Looped FW mains strategically (as conventional FW system design) what value can add other than increasing the cost.

Utilizing PIV located on mains, can still serve the same maintenance purpose even if don't provide individual hydrant isolation valve or am i missing something here against NFPA 24?

Reply
Sue
7/10/2020 12:34:43 pm

I sometimes agree with what you are saying SK. I worry about the end users costs.

I work for a fire department and we utilize the water supply for emergency purposes. Having said that we would like as many devices to be available at any given time.

So for us, the valve allows for repair, maintenance, and control of the device during an emergency leaving us with the access to as many devices as possible.

Better to have 1 hydrant out of service than half of a loop of hydrants because the only valve to isolate it the sectional and main control valve for the full undergrounds.

We also have valves on risers and at each floor for the same reason.

Keeping as much as possible in service at all times.

Ken Thackery
7/10/2020 12:40:02 pm

HI, It's called a repair gate (NRS) and not required in every jurisdiction just depends on the site and water/fire loop configuration.

Reply
Bruce Verhei
7/10/2020 07:42:53 pm

1. Need for maintenance is sufficient cause to require a foot valve.

2. If your fire engine is connected to hydrant via large soft suction, and the break away cotter pin in safety coupling breaks with hydrant open, you’re in trouble. The engine is out of service, unable to respond to further incidents.

It’s handy to be able to grab the wrench off the rig, turn off the foot valve, and effectively take back possession of your vehicle.

3. PIV.

A. I’ll use the word never here. By now your public water service has the foot valve in their GIS system. They know where the valve is with more accuracy than you know where you left a pen on your desk. You don’t need PIV’s for public water system footvalves.

B. Private. Is the valve off in the lawn, in a campus situation, vs in the driveway of a distribution center? There may be some cases where a signed PIV is needed so you can find valve in ten years. A cheaper solution that might be sufficient is a concrete marker post.

Your water department likely already has a detail you can reference. One example:

https://www.kentwa.gov/Home/ShowDocument?id=3680

Best.

Bruce Verhei

Reply
knowledge Sourcing link
10/5/2020 06:41:37 am

Thank you for this valuable information. It is most appreciated.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Oct '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 88A
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    November 2026
    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT