|
Many sprinkler systems in our area (I'm a fire marshal) have aboveground pipe installed by a fire sprinkler installer and the underground installed by an underground pipe contractor. NFPA 24 requires a minimum flow rate from underground pipe in order to remove rock and debris from the underground pipe.
Many of the underground contractors simply open up the pipe and wait until there's consistent clear water and/or stop hearing the rocks ping around. There's no measurements taken for the underground flushing and when I ask for them to verify the flow rate I get blank stares. Is there a way to tell just by static pressure in the area if opening up the pipe flange is enough flow to satisfy the underground flushing? Or is there a measurement I should be seeing to verify the flow rate? Thanks in advance. Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe
9 Comments
Brian Gerdwagen FPE
7/31/2020 10:06:49 am
Just put a handheld pitot on the flow after it is clear, like you would when flow testing a hydrant.
Reply
FIREPE25
7/31/2020 10:08:00 am
We generally use hosemonsters that we make ourselves with friction clamps welded to them to hold play pipes. Once the water is clean we then pitot the playpipes to ensure we flowed enough.
Reply
James
7/31/2020 10:34:38 am
NFPA 13 seems to indicate that flowing the maximum available may be acceptable. But using a pitot tube should be able to measure the flow.
Reply
Bruce Verhei
7/31/2020 10:34:16 pm
You can calculate the flow required.
Reply
Franck
8/3/2020 05:05:21 am
Just a question (maybe stupid) from Europe.
Reply
Bruce Verhei
8/4/2020 02:43:09 am
I talked with survey bureau and local FM contact a little more than a decade ago. I had to teach them what pigging was in terms of water system. Back then the fire protection engineers I talked with weren’t aware just how widely the public water systems were cleaned using pigging.
Franck
8/3/2020 05:16:16 am
Another possible solution to guess the flow without a pitot tube or hosemonster, is to use the water supply flow curve at the area of the flushing.
Reply
ELSA LOPEZ
8/4/2020 04:11:07 pm
For me the flowrate measurement for a 4" or 6" pipe is not an Easy solution to be done at Site with an open pipe flowing huge quantity of water, for small risers it could be a good solution. For me the most accurate way is to measure the flow with the pumps discharge pumps Curve. Measuring pressure at pumps discharge will give you the flowrate you are using if any other system is being used at the same time.
Reply
HJ
8/6/2020 10:12:10 am
The requirement is found in NFPA 24:Table 10.10.2.1.3 (2013). The contractor should be using a pitot gauge to verify the minimum required gpm is reached during the flush test.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop Oct '26 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
November 2026
PE PREP SERIES |
RSS Feed
