MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Allowed to Use Hydrant Across 2-Lane Highway?

3/9/2023

12 Comments

 
When a building is 84-feet from an existing public fire hydrant located across a 2-lane 45mph roadway, can we assume it is standard practice to use it in an event of a fire?

Or would the owner be required to add a personal-use fire hydrant or water storage device on their side of the road?

In the latter case, how far would the fire hydrant have to be placed from the building?​
Picture
Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
12 Comments
Glenn Berger
3/9/2023 08:06:47 am

Unless the AHJ says anything to the contrary, I see no reason why the hydrant across the street cannot be used in case of a fire emergency.

Reply
Scott McBride
3/9/2023 08:17:46 am

The code and standards require that the hydrant has to be no more than 100' from the location of the FDC not the building. Unless the AHJ has added an amendment to change that distance.

Reply
sean
5/8/2023 08:40:57 pm

only for standpipe systems does 100 ft apply

Dale
3/9/2023 08:26:01 am

NFPA 24 is your resource for Fire Hydrants. In the 2016 edition (which is what is in use in my area), hyrdrants are supposed to be located within 40 feet from a building (7.2.3). If they can't be located within 40 feet, then hydrants are permitted to be used where approved the AHJ. I had a project many years ago, where the nearest hydrant was more than 40 feet away. The Fire Chief made the client add a Hydrant to the project (we were doing some renovation in an existing space, along with a new addition to the existing building). "Too much hose" is what he told me. Hope they are OK with the one you got.

Reply
JH
3/9/2023 08:47:18 am

40 ft. is the minimum distance, not the maximum distance per NFPA 24:7.2.3. The "intent" of the code is for the clearance to be at least greater than the height of the building facing wall, known as the "collapse zone". (I believe the IFC establishes this distance as 1.5 times the building height.)
NFPA 1:18.5 is the chapter and section for hydrant spacing from buildings and other hydrants, if your JD is an "NFPA state". Also reference NFPA 1141 chapters 8 and 9 for additional requirements not found in NFPA 1, where applicable.

Reply
JH
3/9/2023 08:36:24 am

I tried posting this from my email, so I apologize if it shows up twice. I can't see it.

The answer has to do with traffic management, and how many trips per day that road section has. Check with your jurisdiction's P&Z requirements, as well as your adopted fire code and ordinances.
Here is the minimum requirement in NFPA 1:18.5.1.5:
"Where fire department access roads are provided with
median dividers incapable of being crossed by fire apparatus, or
where fire department access roads have traffic counts of more
than 30,000 vehicles per day, hydrants shall be placed on both
sides of the fire department access road on an alternating basis, and the distances specified by Section 18.5 shall be measured independently of the hydrants on the opposite side of the fire department access road."

Reply
Brian Cockburn
3/9/2023 09:47:30 am

This should be fine unless the AHJ says otherwise. The Fire Department (along with police) would block the road while the fire is dealt with.

Reply
Anthony
3/14/2023 09:02:30 am

This.

Reply
Mike M link
3/9/2023 10:10:17 am

JH beat me to it and has it exactly correct.
Not sure if I understand if the ahj is requiring an additional hydrant for existing building or the existing building is going through a major renovation.
Also you cannot always depend on the availability of police to stop traffic or pull firefighter resources to direct traffic.

Reply
JH
3/9/2023 12:25:35 pm

Very true. We recently had a project that, even though there was an existing hydrant within the specified distances, using it under normal circumstances would have paralyzed fireground operations and impeded occupant evacuation as well as blocked ingress/egress from neighboring business. A new hydrant was ultimately installed to serve the new project.

Reply
Alex
3/16/2023 06:15:39 am

This is one of the situations where it’s allowed, but if possible, I would avoid it.

Being a fire fighter myself, I would not want to be the first (or second typically) arriving engine on scene in charge of tapping a hydrant across a few lanes of traffic. Police may still be setting up their detail and there may still be cars driving past an already chaotic scene.

Depending on number of hose lines flowing and or a deck gun, getting to an available water supply quickly is extremely important. Of course, after the police detail is set up, this concern is mitigated. If you due only keep the single hydrant, I would work on ensuring the AHJ sets up a pre incident plan with police.

Reply
James Art, FPE
4/4/2023 12:03:59 pm

30,000 vehicles per day- per NFPA 1. THANKS!

Q.IS there something similar in the IFC, or CaFC?

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT