MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Must Water Storage Tank Include Site Fire Flow?

2/4/2019

11 Comments

 
A remote project site does not have any water utility available. 

Under the latest edition of NFPA 22 (2018 Edition of Water Tanks for Private Fire Protection, Section 4.1.1), the "size... of tanks shall be determined by the required fire flow and duration for the attached fire protection system(s) and the pressures required."

Is this implying that the site fire flow for firefighting operation should be included as part of the storage volume for the water storage tank?

For this project the sprinkler system's required water supply would be about 40,000 gallons, while water storage for site fire flow would be well over 240,000 gallons under IFC fire flow or 140,000 gallons under NFPA 1142. Prior versions of NFPA 22 required "the size... of the tank shall be determined by conditions at each individual property after due consideration of all factors involved."

Posted anonymously by a member for discussion. Discuss this  | Subscribe ​
11 Comments
RJ
2/4/2019 12:54:13 pm

I have used the following to figure tank size. System Demand plus Hose Demand times Duration = Gallons (Tank Size).
NFPA13-2016 page 143

Reply
James Phifer
2/4/2019 01:08:08 pm

The outside hose demand can be ignored unless the hoses come directly off the tank piping. see appendix below from NFPA 13.

A.11.1.5.2 Where tanks serve sprinklers only, they can be
sized to provide the duration required for the sprinkler system,
ignoring any hose stream demands. Where tanks serve
some combination of sprinklers, inside hose stations, outside
hose stations, or domestic/process use, the tank needs to be
capable of providing the duration for the equipment that is
fed from the tank, but the demands of equipment not connected
to the tank can be ignored.

Reply
David C
2/4/2019 04:51:11 pm

RJ & James are correct, one other point is it depends on what the tank is for.

If the tank is only supplying the Fire flow for sprinklers then that's how you would size it.

If the tank is required to accommodate the required fire flow for fire fighting operations then you would need to add that value and duration.

I have in the past had to add both of those together and ended up providing 1.8 Million gallon water tank for site fire flow and sprinkler water demand (Airport)

Reply
JW
2/5/2019 09:25:02 am

If your tank serves fire hydrants then you need to consider site fire flow demand for tank capacity. I would explore NFPA 1142 Standard On Water Supplies For Suburban And Rural Fire Fighting. Depending on your site you may be able to propose a reduced site fire flow per NFPA 1142, if approved by the AHJ.

Reply
PETE
2/5/2019 12:13:43 pm

IFC and NFPA 1 both allow for up to a 75% reduced fire flow requirement for "fully sprinklered" buildings, as approved by the AHJ. Also, NFPA 1 §18.4.3.1 allows for decreases by the AHJ for rural areas where the development of full fire flow requirements is impractical. This provision is also in the IFC §B103.1. Also, In NPFA 1 (2012)§18.4.5.3 For a building with an approved fire sprinkler system, the fire flow demand and the fire sprinkler system demand shall not be required to be added together. The water supply shall be capable of delivering the larger of the individual demands. * On a personal note * The terms "fire flow" and "sprinkler demand" should not be confused or used interchangeably. Everything I've read in the codes makes distinctions between the two.

Reply
Ahmed
12/20/2023 01:59:44 pm

Thank you

Reply
Franck Orset
2/20/2019 11:20:38 am

Water demand for hydrant should be added to the water flow for the largest sprinkler system demand if the water supply is used for both the sprinkler systems and the hydrants.
All insurance companies will recommend that as a minimum.
It is the same for sizing the fire pump (which should be able to supply the hydrants + the sprinkler flows).

In case of fire, the sprinkler system "control the fire" but you will need manual firefighting (i.e. hoses and hydrants) to extinguish it. Even if it is true that many fires are not just controlled, but extinguished by the sprinkler system only.
This is the reason why, with ESFR (for storage occupancies) the outside water demand is lower (250 gpm instead of 500 gpm) and the duration is lower (1 h instead of 1.5-2 hours for storage occupancies).

If, as indicated by James, the hydrant are fed from an independent supply, then the water tank + fire pump should be designed for the sprinkler demand only.

Note that in some cases, the water supply is not sufficient to supply the full demand for manual firefighting (hydrants). The complement can be asked from the private water supply (tank + pump) with some additional private hydrants located on this system.

Reply
Chris Pederson link
4/15/2021 05:31:39 pm

I agree that the required fire flow should determine the size of the tank. Too small and you run into a problem. Too big and you'll pay too much money to fill it up.

Reply
Tom Kennedy
10/8/2021 08:10:45 am

If the underground tank is the only supply for the sprinkler system and there is a dry hydrant connected to the tank, would a hose demand need to be included in the sprinkler calculation?

Reply
James Phifer
10/11/2021 09:04:28 am

yes, I believe so per Annex A from the 2016 edition.

A.11.1.5.2 Where tanks serve sprinklers only, they can be
sized to provide the duration required for the sprinkler system,
ignoring any hose stream demands. Where tanks serve
some combination of sprinklers, inside hose stations, outside
hose stations, or domestic/process use, the tank needs to be
capable of providing the duration for the equipment that is
fed from the tank, but the demands of equipment not connected
to the tank can be ignored

Reply
Tom Kennedy
10/11/2021 10:31:34 am

Thank you, James. A.11.1.5.2 is referring to sizing the tank (volume). My question is referring more to the sprinkler system hydraulic calculation, wondering if a 250gpm outside hose flow would need to be added to an ord. hazard sprinkler system hydraulic calculation.




Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT