Provide Fire Access for Narrow Mechanical Yard?

7/18/2022

2 Comments

 
Hoping to gain some insight from industry here:

Working on preliminary layouts for a large industrial facility that is comprised of tilt-up precast single-story building (~40' tall) and flanked on one side by an equipment yard (think generators, switchgears, mechanical equipment) configured in two levels (think mezzanine).

Question is on fire access to the main building: The mechanical yard runs the entire length of the main building and we are considering fire access as the depth of the equipment yard is ~100ft with a limited service corridor separating the two (~12ft) for maintenance and building egress. There will be periodic gaps (~6ft wide) between equipment located at grade, however the access will require passing through the yard on foot (underneath the second level of equipment on the mezzanine) to gain access to the main building.

Per IFC 503.1.1 our fire access roads must provide continuous access to the exterior within 150ft of the building.

Would passing "through" the mechanical yard at grade meet this requirement?

Would placing "driveways" through the yard to allow a truck to pull closer to the building (but being parked underneath the second level) be kosher?

A similar question exists regarding having hydrants located directly under the second level near the extents of the yard, is this OK?

Have been unsuccessful at locating any code references regarding fire access through a "tunnel" if you would. An AHJ perspective would be much appreciated, along with any other thoughts/feedback.

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
2 Comments
Greg
7/18/2022 08:25:00 am

One of the first items to consider about fire department access is "why does a fire department want access". Generally, access is for ease of entry into a building or as a defensive posture. The mention of "tip up" wall construction immediately brings to mind limited openings and therefore limited opportunities for entry or defense. In consideration for entry, one must also consider the defensive action of retreat and the ability to move from the building. If I recall correctly, some highly protective risk insurers and government agencies require PIV valves to be located at least 40 ft from exterior walls. Why, you ask? When defensive fire fighting prevails, wall collapse is a distinct possibility. Having the ability to isolate a system, post collapse, will preserve water for large hose streams (when the sprinkler system has failed).

So in describing offense and considerations for defensive firefighting, is there any advantage to accessing the lane described in the question? Looking at the question from a 50/50 chance perspective, yes or no, if there is not a benefit gained for access (offensive and defensive) then the decision should be No.

In deciding that access is not available on one side of the structure, how can the remaining sides be improved upon. Signage, wayfinding and pre-planning are the least expensive, low cost capital items. Roadway improvement, fire zones painting, and additional fire hydrants are higher capital items.

In concluding, consider AHJ input and local fire agency practice. Explain the complexities of 100 percent exterior access and discuss the value of 75 percent (three sides) or alternative means to improve the accessible areas. Discuss and ask questions about primary entry points, personnel doors, roll-up doors (dock doors), secondary entry points, and combustible loading expectations. Improvements could include fire alarm, smoke detection addition, or smoke evacuation system. This may or may not be needed as alternative means but thinking through all of the low to high cost capital solutions is important ahead of your first conversation with the AHJ, or fire response agency.

Reply
Todd E Wyatt
7/18/2022 08:51:38 am

The adopted Code for this project (e.g. 2021 IBC?) will define what this "yard" as one of the following :

COURT. An open, uncovered space, unobstructed to the sky, bounded on three or more sides by exterior building walls or other enclosing devices.

YARD. An open space, other than a court, unobstructed from the ground to the sky, except where specifically provided by this code, on the lot on which a building is situated.

EGRESS COURT. A court or yard which provides access to a public way for one or more exits.

I recommend review of the building's Means of Egress (MOE) as access through this "COURT" may be required. IBC Ch 10 Section 1029 Egress Courts includes additional requirements.

For the "second level of equipment", you may want to define these as "EQUIPMENT PLATFORMS" (see IBC Ch 5 Section 505) :

EQUIPMENT PLATFORM. An unoccupied, elevated platform used exclusively for mechanical systems or industrial process equipment, including the associated elevated walkways, stairways, alternating tread devices and ladders necessary to access the platform (see Section 505.3).

Once you have defined this "open, unenclosed space" and the associated "equipment platforms", you can direct your MOE and Fire Protection questions to the AHJs.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Aug '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT