I have two questions on projects in areas that are seismic regions D or more restrictive and flood prone/high water table:
NFPA 13 (2016) Section 9.3.4.3 where clearance is provided by a pipe sleeve, 4 in. pipe & larger require 4 in. larger pipe sleeve. So if we are providing a below grade wall or floor penetration, that experiences high water tables and flooding. What are the most common practices to prevent ground water intrusion through the pipe sleeve? NFPA 13 Section 9.3.4.8 states - where required, the clearance shall be filled with flexible material that is compatible with the piping material. Is this most likely a water proofing or rated caulk? My original thoughts lead me to something like a Metraflex Sliding MetraSeal or any pipe sleeve seal on the market, but think that would go against the internal pipe sleeve clearance requirements. Any suggestions on best practices? Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
10 Comments
Jeremy
12/9/2020 10:12:59 am
A common practice when penetrating through an exterior wall is to use a "Link seal".
Reply
Dave
12/9/2020 10:43:46 am
I agree with Jeremy, for decades I have designed utilizing LinkSeal products. Currently working on one where I'm scratching my head on the best way to do the restraint, can't really run the rods through the link seal.
Reply
Colin Lusher
12/9/2020 01:28:37 pm
Can you just use an MJ Sleeve or Elbow with restraining glands and eliminate the rods altogether?
Dave
12/9/2020 01:53:32 pm
I think you are right, Colin, I like to see two types of restraint but I guess that is still doable. I welcome more discussion on the topic.
Glenn Berger
12/9/2020 10:44:35 am
https://www.gptindustries.com/en/products/link-seal - Adding a link (pun intended) to Jeremy's response. These typically cost more, but less problems over time.
Reply
12/9/2020 10:46:14 am
Agree with Jeremy; I've used "Link seal" when penetrating a basement wall with a low water table. But the best solution, if at all possible, would be to avoid the penetration altogether and enter the building above grade. I understand that it's not always possible however.
Reply
Jonathan Joseph
12/9/2020 01:55:50 pm
If your in a high flood zone but also in a moderate siesmic zones. The linkseal or metroflex options will work for a great deal of water head and psi however, flexible couplings should still be installed for your seismic protection due to the clearance issue.
Reply
Jonathan Sullivan
12/11/2020 09:25:25 am
By this you are referring to the requirement where if there is no clearance is provided flex connectors are required on both sides of the penetration? What do you use on the underground side?
Reply
Will Parrish
12/9/2020 06:12:59 pm
Straight up Oakum
Reply
Alex H
7/6/2026 03:12:33 pm
Weighing in 6 years later because I'm looking at this situation right now. My current thought is that a flexible coupling on the building side of the penetration should suffice to meet the intent of NFPA 13. NFPA 13 does require a flexible coupling on both sides of a penetration to omit the clearance, but when one side of the penetration buried in in soil, I don't think we're dealing with the kind of differential motion that the clearance/flex fittings intend to mitigate. Therefore, the link-seal could be installed for weatherproofing the sleeve and the "free end" of the pipe inside the building receives a flex coupling.
Reply